Why Mesa 5i20 does not start?
02 Aug 2016 00:33 #78269 by pkasy
Replied by pkasy on topic Why Mesa 5i20 does not start?
I already changed the cables. nothing changed.
Now I will change two boards 5i20.
02 Aug 2016 00:35 #78270 by pkasy
Here are configs.
LinuxCNC is 2.7.5
02 Aug 2016 01:12 #78271 by PCW
Replied by PCW on topic Why Mesa 5i20 does not start?
The outputs are close to what is expected with those configs
Based on the HAL file, I certainly I would expect GPIO 65 and 67 to be stuck on as you found
( Because 7I37 outputs are active low, if you enable FPGA GPIO outputs without setting the invert attribute,
the 7I37 output will be enabled as soon as LinuxCNC starts up)
If any 7I37 outputs are on when LinuxCNC is _not_ running, that suggests a FPGA fault
02 Aug 2016 01:52 #78272 by pkasy
Why?
And setp ...065.out 1 or 0 does not make anything. These keys are just in open state.
02 Aug 2016 02:52 - 02 Aug 2016 03:00 #78274 by PCW
Why?
the FPGA output will be low so the 7I37 output will be enabled as soon as LinuxCNC starts up
are any GPIO pins low when LinuxCNC is not running?
Last edit: 02 Aug 2016 03:00 by PCW.
02 Aug 2016 04:53 #78275 by pkasy
No, only then LinuxCNC starts.
Anyway, I can't change output at 64-71 or 40-47 pins.
I tried open_drain too.
No luck.
On the other machine, I have not been able to obtain from the mesa 7i37 any outputs. Instead, I set card for LPT port. And it worked.
02 Aug 2016 04:55 #78276 by pkasy
Why 65 and 67? Where did you get information?
02 Aug 2016 05:15 #78277 by PCW
This strongly suggests that the problem is configuration, bitfile or OS/PC related, not a bad 5I20
What PC hardware, linuxCNC version, OS , and md5sum of svst8_4.bit do you have?
02 Aug 2016 05:18 #78279 by PCW
They are not set in hal file, therefore will start up at a 0 level, turning the 7I37 outputs on as soon
as they are set to is_output
02 Aug 2016 05:51 #78280 by pkasy
Why 69 and 71 are OFF?
Moderators: PCWjmelson