a colleague and I are currently repairing a milling machine ("Heller CNC PFH 10-1000"). We are using LinuxCNC 2.7.7 and the engines are controled by MESA Cards (5i20, 7i37 TA, 7i48) with a svst6_6_7i48 firmware.
The problem we are facing is, that LinuxCNC tries to compensate the drifting of the x- and y-axis with lots of short peaks of voltage in the output, so the machine starts to cog while holding its position or moving against the drifting direction. Moving the axis in drifting direction in not a problem. You can see the voltage output signal in the attached picture.

Attachment not found



We have been trying to figure out the correct PID values to fix this, but couldn't really. So we would appreciate your help. If you have problems understanding or need further information, please ask.

Thanks in advance!

Please Log in to join the conversation.

More
9 years 11 months ago #82372 by andypugh
How much I-Gain do you have relative to P-Gain?

Please Log in to join the conversation.

More
9 years 11 months ago #82375 by PCW
Replied by PCW on topic PID Setting for drifting axis
Also do you have the PWM gens output mode set to 2?

( This is required by the 7I48 and you will have bizarre behaviour if they are not set to mode 2 )

Please Log in to join the conversation.

More
9 years 11 months ago #82531 by Chre9
Replied by Chre9 on topic PID Setting for drifting axis
Hey guys, thanks for your reply!

Yes, we are already using output mode 2. Before that it was a huge mess.
The best results we could get were including P=1,5 and I=0,75.
This way the cogging is not so hard, but it still doesn't prevent it.

Please Log in to join the conversation.

More
9 years 11 months ago #82545 by PCW
Replied by PCW on topic PID Setting for drifting axis
Do the axis move smoothly both ways open loop? say with 100 mV/-100 mV of analog signal
(that is, is this possibly a drive issue?)

Can you send any output voltage open loop (via setp) (try +5 and -5)
(that is is this a hardware interface problem)

Does the encoder read accurately?

A 10V output with a P gain of 1.5 means an error of 6.66 mm (assuming mm)
is this much error really present?
(In addition I should almost always be 0 when doing initial tuning )

Halscope plots of the PID output value, commanded and feedback position would be helpful

Also posting the HAL and INI files may help

Please Log in to join the conversation.

More
9 years 11 months ago #82587 by Chre9
Replied by Chre9 on topic PID Setting for drifting axis
We just recorded the PID output value, commanded and feedback position of the x-axis with halscope while moving in each direction and staying in the same position. First with P=1,5 and I=0,75:

Attachment not found

Attachment not found

Attachment not found



And with P=1 and I=0:

Attachment not found

Attachment not found

Attachment not found



The y and z axes show the same behaviour.

Please Log in to join the conversation.

More
9 years 11 months ago #82588 by Chre9
Replied by Chre9 on topic PID Setting for drifting axis
Here you can find the .ini and .hal document:

Attachment not found

Attachment not found



We already fixed one of the encoders and they all work properly. Furthermore we have been testing the axis with an external power supply and they move smoothly this way.

Please Log in to join the conversation.

More
9 years 11 months ago #82589 by PCW
Replied by PCW on topic PID Setting for drifting axis

setp hm2_5i20.0.pwmgen.04.output-type 1


Wrong PWM output type

So what's happening is this:

The 7I48 is designed for UP/DOWN PWM mode (output type 2)
where positive outputs are generated by a PWM signals on the UP pin
and negative outputs are generated by PWM signals on the DOWN pin
the absolute analog voltage in either case is proportional to the PWM duty cycle

If you instead run the 7I48 with the PWM generator in PWM / DIR mode (output mode 1)
it works fine in the direction that the direction pin is 0, but you get a immediate full scale
output (10V) when the PID output sign changes making the direction pin high

Please Log in to join the conversation.

More
9 years 11 months ago #82684 by Chre9
Replied by Chre9 on topic PID Setting for drifting axis
Thanks for the explanation.
We changed output mode to 2.
Now, when we start the machine the axis starts to accellerate to a high velocity until a joint following error appears.

Attachment not found



Is it possible, that it tries to home the axis?

Please Log in to join the conversation.

More
9 years 11 months ago #82685 by PCW
Replied by PCW on topic PID Setting for drifting axis
That's expected (it means the loop feedback is positive instead of negative)

The fix is to reverse the PWM output scale, that is change:

OUTPUT_SCALE = 10.0

to:

OUTPUT_SCALE = -10.0

in the per AXIS sections of the .ini file