- Posts: 37
- Thank you received: 0
Timeout Communication Error
- pmcstoneinc
- Topic Author
- Offline
- Junior Member
-
Less
More
9 years 9 months ago #86383
by pmcstoneinc
Timeout Communication Error was created by pmcstoneinc
Hello Peter hopefully you can lead me in the right direction to troubleshoot this.
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (3) Timeout
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (3) Timeout
hm2/hm2_7i92.0: Smart Serial Error: port 0 channel 0. You may see this error if the FPGA card read thread is not running. This error message will not repeat.
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (3) Timeout
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (3) Timeout
hm2/hm2_7i92.0: Smart Serial Error: port 0 channel 0. You may see this error if the FPGA card read thread is not running. This error message will not repeat.
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (3) Timeout
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (3) Timeout
hm2/hm2_7i92.0: Smart Serial Error: port 0 channel 0. You may see this error if the FPGA card read thread is not running. This error message will not repeat.
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (3) Timeout
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (3) Timeout
hm2/hm2_7i92.0: Smart Serial Error: port 0 channel 0. You may see this error if the FPGA card read thread is not running. This error message will not repeat.
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (3) Timeout
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (3) Timeout
hm2/hm2_7i92.0: Smart Serial Error: port 0 channel 0. You may see this error if the FPGA card read thread is not running. This error message will not repeat.
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (3) Timeout
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (3) Timeout
hm2/hm2_7i92.0: Smart Serial Error: port 0 channel 0. You may see this error if the FPGA card read thread is not running. This error message will not repeat.
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (3) Timeout
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (3) Timeout
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
Sorry for the all the text, lots of repeat......Anyways the machine was stationary when the error occurred. Let me know what other info you will need from me. Thanks.
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (3) Timeout
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (3) Timeout
hm2/hm2_7i92.0: Smart Serial Error: port 0 channel 0. You may see this error if the FPGA card read thread is not running. This error message will not repeat.
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (3) Timeout
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (3) Timeout
hm2/hm2_7i92.0: Smart Serial Error: port 0 channel 0. You may see this error if the FPGA card read thread is not running. This error message will not repeat.
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (3) Timeout
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (3) Timeout
hm2/hm2_7i92.0: Smart Serial Error: port 0 channel 0. You may see this error if the FPGA card read thread is not running. This error message will not repeat.
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (3) Timeout
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (3) Timeout
hm2/hm2_7i92.0: Smart Serial Error: port 0 channel 0. You may see this error if the FPGA card read thread is not running. This error message will not repeat.
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (3) Timeout
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (3) Timeout
hm2/hm2_7i92.0: Smart Serial Error: port 0 channel 0. You may see this error if the FPGA card read thread is not running. This error message will not repeat.
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (3) Timeout
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (3) Timeout
hm2/hm2_7i92.0: Smart Serial Error: port 0 channel 0. You may see this error if the FPGA card read thread is not running. This error message will not repeat.
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (3) Timeout
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (3) Timeout
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
Sorry for the all the text, lots of repeat......Anyways the machine was stationary when the error occurred. Let me know what other info you will need from me. Thanks.
Please Log in to join the conversation.
9 years 9 months ago #86384
by PCW
Replied by PCW on topic Timeout Communication Error
Usually this means total loss of communication between the 7I92 and 7I77
Most common causes are
1. 5V power issue on 7I77 (low 5V or total loss of 5V)
2. Watchdog bite due to real time issues
Most common causes are
1. 5V power issue on 7I77 (low 5V or total loss of 5V)
2. Watchdog bite due to real time issues
Please Log in to join the conversation.
- pmcstoneinc
- Topic Author
- Offline
- Junior Member
-
Less
More
- Posts: 37
- Thank you received: 0
9 years 8 months ago #87306
by pmcstoneinc
Replied by pmcstoneinc on topic Timeout Communication Error
Hello Peter
I added a 5v power supply to exclude the possibility of a power issue to the 7i77, what do I need to check for real time issues. I have checked this system for latency issues in the past and never saw any alarming values from the test. What would I need to check while the system is running. I do have have a USB to RS485 running on a different thread speed. Let me know. Thanks.
I added a 5v power supply to exclude the possibility of a power issue to the 7i77, what do I need to check for real time issues. I have checked this system for latency issues in the past and never saw any alarming values from the test. What would I need to check while the system is running. I do have have a USB to RS485 running on a different thread speed. Let me know. Thanks.
Please Log in to join the conversation.
9 years 8 months ago #87314
by PCW
Replied by PCW on topic Timeout Communication Error
Do you still have an issue with the external 5V power?
Also if you run LinuxcCNC from a terminal you can get the entire error log
which may catch a watchdog bite message
Also if you run LinuxcCNC from a terminal you can get the entire error log
which may catch a watchdog bite message
Please Log in to join the conversation.
- pmcstoneinc
- Topic Author
- Offline
- Junior Member
-
Less
More
- Posts: 37
- Thank you received: 0
9 years 8 months ago #87327
by pmcstoneinc
Replied by pmcstoneinc on topic Timeout Communication Error
Yes. Still present present with an external 5v supply. I seem to be getting error (4) and (14)
Please Log in to join the conversation.
9 years 8 months ago #87328
by PCW
Replied by PCW on topic Timeout Communication Error
OK well 4 and 14 are different than what you got before (which looked more like a power supply issue)
Can you start linuxcnc in a terminal and capture the actual errors?
How long (and what type) is the cable from the 7I92 to the 7I77?
Did you make sure the 7I77 and 7I92 are jumpered for external power (7I77 W5 right 7I92 W3,W4 down)
Also what LinuxCNC version are you running?
Can you start linuxcnc in a terminal and capture the actual errors?
How long (and what type) is the cable from the 7I92 to the 7I77?
Did you make sure the 7I77 and 7I92 are jumpered for external power (7I77 W5 right 7I92 W3,W4 down)
Also what LinuxCNC version are you running?
Please Log in to join the conversation.
- pmcstoneinc
- Topic Author
- Offline
- Junior Member
-
Less
More
- Posts: 37
- Thank you received: 0
9 years 8 months ago #87329
by pmcstoneinc
Replied by pmcstoneinc on topic Timeout Communication Error
The cable was purchased from you. The length I wanna say is 3ft (1m). I can get you the exact errors on Monday. I want to say the jumpers are what you stated because I was using USB power from the PC as an external source. As far as LinuxCNC version I am using the most updated version of Machinekit.
Please Log in to join the conversation.
9 years 8 months ago #87344
by PCW
Replied by PCW on topic Timeout Communication Error
I would try LinuxCNC 2.7.8 (or master), Machinkit is not as up-to-date as
LinuxCNC WRT Hostmot2/sserial driver bug fixes
LinuxCNC WRT Hostmot2/sserial driver bug fixes
Please Log in to join the conversation.
- pmcstoneinc
- Topic Author
- Offline
- Junior Member
-
Less
More
- Posts: 37
- Thank you received: 0
9 years 8 months ago #87350
by pmcstoneinc
Replied by pmcstoneinc on topic Timeout Communication Error
Hello Peter see below
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (4) Extra character
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (4) Extra character
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (4) Extra character
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (4) Extra character
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (4) Extra character
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (4) Extra character
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (4) Extra character
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (4) Extra character
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (4) Extra character
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (4) Extra character
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (4) Extra character
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (4) Extra character
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (4) Extra character
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (4) Extra character
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (4) Extra character
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (4) Extra character
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (4) Extra character
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (4) Extra character
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (4) Extra character
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (4) Extra character
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (4) Extra character
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (4) Extra character
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.1 error = (4) Extra character
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (4) Extra character
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
hm2/hm2_7i92.0: Smart serial card hm2_7i92.0.7i77.0.0 error = (13) Communication error
Please Log in to join the conversation.
- tommylight
-
- Away
- Administrator
-
Less
More
- Posts: 22012
- Thank you received: 4
9 years 8 months ago #87353
by tommylight
Replied by tommylight on topic Timeout Communication Error
Just a stab in the dark, but are you sure you have the 7i77 connected to the right port on the 7i92 ?
It sure looks like it is not.
Also did you flash the 7i92 with the firware for 7i77?
What do you get if you type "sudo mesaflash --device 7i92 your_7i92_ip_address_here --readhmid ?
It sure looks like it is not.
Also did you flash the 7i92 with the firware for 7i77?
What do you get if you type "sudo mesaflash --device 7i92 your_7i92_ip_address_here --readhmid ?
Please Log in to join the conversation.