7i76e step dir signal missing for stepgen type 0

More
2 years 1 month ago #309404 by Traken
Hello everyone, I'm trying to configure linuxcnc 2.10 and mese 7i76e and I don't have a step/dir signal at all, but when I switch stepgen to type 2, there is a signal, but it's probably not correct because the machine loses steps.

Please Log in to join the conversation.

More
2 years 1 month ago #309411 by PCW
It probably means that you have the step time too short for
the drive to recognize the step pulses (type 2 is quadrature
so has square wave signals that are quite wide at slow speeds)

Please Log in to join the conversation.

More
2 years 1 month ago #309414 by Traken
ok, but why don't I have a signal on Stepgen Type 0, the oscilloscope doesn't show anything

Please Log in to join the conversation.

More
2 years 1 month ago #309416 by PCW
Do you see a signal with type 2?

What is the step length set to?

Please Log in to join the conversation.

More
2 years 1 month ago #309417 by Traken
Yes i see signal type 2 step length 5us

Please Log in to join the conversation.

More
2 years 1 month ago #309419 by PCW
Maybe you have the step length too short for the scope to catch

Please Log in to join the conversation.

More
2 years 1 month ago #309420 by Traken
Is this correct for it to work on stepgen type 2?

Please Log in to join the conversation.

More
2 years 1 month ago #309421 by PCW
All modes work (0,1,2), but the steplength setting
only  affects the step length in modes 0 and 1.

Please Log in to join the conversation.

More
2 years 1 month ago #309422 by Traken
How can I diagnose why it's not type 0? Maybe it's the Ethernet cable's fault?

Please Log in to join the conversation.

More
2 years 1 month ago #309423 by PCW
Its most likely a hal file setting thats wrong: The step length

Please Log in to join the conversation.