Help in problem "unexpected switch limit"
13 Dec 2010 12:44 #6003
by ArcEye
Replied by ArcEye on topic Re Debounce component
Hi
If it helps, the below are extracts from my lathe .hal file which had problems with a home switch that required debounce.
Works perfectly now, 100 may seem big, but I have a fast base thread and trial and error resulted in that figure.
ArcEye
loadrt debounce cfg=2
addf debounce.0 base-thread
#If necessary, you can
#to change the amount of debounce; the default is apparently 5, which
#means the switch input to emc has to be stable for 5 servo periods
#before the debounce output changes.
setp debounce.0.delay 100
# Needed debounce on X home switch. Has quite
# a long travel and did not give a clean on/off
net xhome-raw <= parport.0.pin-13-in-not => debounce.0.0.in
net xhome-filtered debounce.0.0.out => axis.0.home-sw-in
ArcEye
14 Dec 2010 03:06 #6017
by aike
Replied by aike on topic Re:Re Debounce component
Thank you for answer.
I'll try debounce, if grounded all elements (computer, power supply etc) not solved the problem.
17 Dec 2010 15:08 #6097
by aike
Hi!
My servo-tread is 1000000 nS or 1000 mkS or 1 mS, I set debounce delay as 20. It is mean, that all noise less then 20 mS (50Hz) will be ignored.
Yes!
The masseage "jointX limit switch error" disappead.
But the message "jointX following error" appears. So as this error is obtained due encoder feedback, I checked this chain.
Also the broken 3 phase lube motor was found with short connect to ground. I replaced lube motor and the message "follow error" disapperd.
I'm continue the investigation, will report it further.
Yes!
Moderators: piasdom
Time to create page: 0.205 seconds