Mesa 7i96 Inputs coupled together?
  • Moosey
  • Topic Author
  • New Member
  • New Member
4 years 10 months ago #229347 by Moosey
Mesa 7i96 Inputs coupled together? was created by Moosey
I'm setting up my limit switches (NPN proximity sensors) and am seeing some unexpected behavior at the inputs on my Mesa 7i96. I have the Input Common pulled to +24V, Brown wires to +24V, Blue wires to GND, and Black to the input terminals. Whenever a sensor is triggered it pulls all the voltages lower triggering all the inputs I have connected. I already tried adding a series resistor and a pull up resistor without any meaningful changes. Any suggestions? I'm probably missing something simple. Also, I need to provide a 5V signal to an SSR driving an AC load. Using the isolated outputs isn't turning out to be straight forward since the voltage drop across the transistor brings the output to ~500mV if I hook up 5V to +out and the signal to -out. I'm sure these are solved problems but haven't been able to find the right information. Any suggestions?
4 years 10 months ago #229349 by BigJohnT
Replied by BigJohnT on topic Mesa 7i96 Inputs coupled together?
The inputs are sinking so they are looking for 24vdc and the common should be 0vdc, not sure if you can run NPN inputs or not.
JT
4 years 10 months ago - 4 years 10 months ago #229351 by PCW
Replied by PCW on topic Mesa 7i96 Inputs coupled together?
On the inputs it sounds like the input common is not connected.
If the input common (TB3, pin 12) is at a fixed 24V, there should be
no interference from input to input at all.
On the outputs, an "on" 7I96 output is less than 0.1 Ohm so a connection
like +5V -->OUTN+ -->OUTN- --> SSRIN+ --> SSRIN- -->5VGND
should put 5V across SSRIN+ to SSRIN-  (when on) within a fraction
of a mV of the 5V source voltage
Last edit: 4 years 10 months ago by PCW.
The following user(s) said Thank You: Moosey
4 years 10 months ago #229352 by PCW
JT
The 7I96 inputs can be sinking (for PNP sensors) or sourcing (for NPN sensors) depending on how you connect the input common pin
For sourcing inputs (NPN sensors or switches with common of 0V) you connect the input common to +5 to +24V
For sinking inputs ( and  PNP sensors or switches with a common of +5 to +24V) you connect the input common to 0V
  • Moosey
  • Topic Author
  • New Member
  • New Member
4 years 10 months ago #229353 by Moosey
Replied by Moosey on topic Mesa 7i96 Inputs coupled together?
Wow thanks for the quick reply guys. Turns out I had an off by one error between my ears. The headers were plugged in to the wrong spot. It's all working now!
Moderators: PCW, jmelson