7I76e volt readings
06 Jun 2022 08:53 #244659
by Yannis
7I76e volt readings was created by Yannis
Hello
try to configure a 5 axis machine
the machine X Y Z A B is working in all directions exept B-
When i mesure the volt in the TB2 0-3 step and dir i have values from 0 to 5 volts
When i mesure the fault axis TB3 4 step and dir i have values from 1.45 to 5 volts(not 0 as the 4 previus axis)
Is this normal?
What coold cause that?
Is this normal?
06 Jun 2022 14:44 #244673
Replied by PCW on topic 7I76e volt readings
Sounds like the driver chip for STEP4/DIR 4 has been damaged
(U24 74ACT04)
Probably from accidental connection to a voltage outside of the 0 to +5V range
(U24 74ACT04)
The following user(s) said Thank You: Yannis