soft limits different after power cycle
29 Oct 2017 17:47 #100977
by RayJr
"No problem can be solved from the same level of consciousness that created it"
Albert Einstein
Replied by RayJr on topic Sanity Check (was soft limits different after power cycle)
Hi Petr.
Commenting that out seems to have aggravated the resonance like problem. I am back to having the motor freeze up when it gets near the commanded speed.
Going back to open loop by commenting out:
net y-pos-fb <= hm2_5i25.0.encoder.01.position
net y-vel-fb <= hm2_5i25.0.encoder.01.velocity
net y-index-enable axis.1.index-enable <=> hm2_5i25.0.encoder.01.index-enable
and un-commenting:
net y-pos-fb <= hm2_5i25.0.stepgen.01.position-fb
net y-pos-fb => axis.1.motor-pos-fb
seems to eliminate the problem.
I am wondering if my choice of encoder per is grossly too high and causing the stepper module in the 5i25 to be jittery and screwing up the Gecko G202. Encoders are 2000ppr, so with quad counts, it is 4x the steps per unit.
Is there a place I can find documentation of all the pins for the 5i25 presented to HAL, including options for each?
A man page?
and un-commenting:
A man page?
Albert Einstein
29 Oct 2017 18:27 #100978
Replied by PCW on topic Sanity Check (was soft limits different after power cycle)
You very likely have to reduce the P term after removing the PID error limit for closed loop via encoder mode
too much P term is what will cause jiiteryness in the stepgen
I'm not sure I understand what you mean by "having the motor freeze up when it gets near the commanded speed"
The motor should always be running at the commanded speed, do you mean maximum speed?
As far as encoder resolution goes, the higher the better
The hostmot2 manual page has most of the firmware pin names:
man hostmot2
If you change the hal file in that manner you are using open loop mode (so P can go back to being 1000)
man hostmot2
29 Oct 2017 22:26 #100995
by RayJr
Albert Einstein
Could I be screwing up the PID by feeding it both vel-fb and pos-fb?
Ray
Ray
Albert Einstein
29 Oct 2017 22:48 #100996
vel-fb is a no-op if you have a 0 D term ( and you probably should leave D at 0 )
30 Oct 2017 02:59 - 30 Oct 2017 03:56 #100999
by RayJr
Albert Einstein
This afternoon, I isolated the step motor from the machine, set lcnc up for open loop, and tested.
I have a very bad resonance problem!
Now I need to figure out the cause.
the Chineese step motor, or the Gecko G202.
Albert Einstein
Last edit: 30 Oct 2017 03:56 by RayJr.
31 Oct 2017 13:22 #101056
The manpage (man hostmot2) is also available here: linuxcnc.org/docs/2.7/html/man/man9/hostmot2.9.html
All the manpages are here: linuxcnc.org/docs/2.7/html/
Replied by andypugh on topic Sanity Check (was soft limits different after power cycle)
Time to create page: 0.095 seconds