Step or velocity control for servo gantry

More
12 years 3 weeks ago #51754 by andypugh

alan_3301 wrote:

setp pid.x.Pgain [AXIS_0]P


shouldnt this be pid.0.Pgain?

in the docs <loopnum> is a number, don't know if a letter works?


if you use
Code:
loadrt pid count=3
then you get pid.0.Pgain, pid.1.Pgain, pid.3.Pgain etc
If you instead use
Code:
loadrt pid count=3 names=pid.x,pid.y,pid.z
then you get pid.x.Pgain etc.
It is up to you to choose sensible names, you could use
Code:
loadrt pid count=3 names=encoder.0,and2.3,bladerunner
if you wanted to make your HAL file utterly impenetrable :-)

Please Log in to join the conversation.

More
12 years 3 weeks ago #51779 by crisiacuf@yahoo.com
I am now using a 7i77+7i85s setup with encoder feedback from my MR-J2S40A virtual encoder and things start to get crazy.
My servo is getting Al 20 wich is an encoder communication error or excessive acceleration according to the manual.
Funny thing is this happens at linuxCNC startup with either of the two bus connections to the servo(encoder abz signals OR speed command with voltage and enable). So as long as I don't feed +/-10V to the servo this can't be accelearation error which lefts me with encoder communication error.
This only happens at Linux CNC startup.

What's even funnier, I somehow got past the startup.In pncconf I got to the axis test but I get AL20 after I move the axis a couple of mm with only around 0,5V(from 10V max speed) speed command.
Even if it's offline because of this bellowed AL-20, the amplifier still sends the virtual encoder signal and Linux CNC correctly displays my axis movement. So the position is correctly read by the amplifier and correctly sent to the 7i77.
I'll check every wire and shield connection and get back.

Please Log in to join the conversation.

More
12 years 3 weeks ago #51784 by PCW
If you get errors with no commands (analog input disconnected)
it sounds like a noise/ground loop issue

I would check that the drives and the PC running the 7I77 are grounded to the same point,
that the motors are mounted and have secure ground returns to the drive
(large HF currents flow in the motor ground return to the drive due to the HV
square wave PWM signal driving the stator winding to ground capacitance)

Please Log in to join the conversation.

More
12 years 3 weeks ago #51894 by crisiacuf@yahoo.com
Yes, that's what I suspect also. I am now rewiring everything to make sure there is no ground loop and everything is nice and tidy.

Please Log in to join the conversation.

More
12 years 2 weeks ago #52056 by crisiacuf@yahoo.com
Ok, I separated the logic ground used by mesa and PC from the amplifiers, motors and main box ground shield.
I am now experimenting on the Z axis instead of X. Z has a belt 1:2 multiplication X is direct drive.
I am now using feedback from the amplifiers virtual encoders @ 25000 pulses/rev so 10000 pulses/mm and things are working much better.
I got a max Ferror of around 0.01mm @ < 6000mm/s speed. Around 6000 something happens and Ferror rises to 1mm instantly. I dont know why,yet, but It,s not my main problem for the moment.
I am now changing the X direct drive to belt drive and trying to setup the gantry mode(2 joint Y axis).

Could someone guide me to the git link for the 2.7 pre version with improved TP of LinuxCNC please?

Please Log in to join the conversation.

More
12 years 2 weeks ago #52058 by andypugh

crisiacuf@yahoo.com wrote: Around 6000 something happens and Ferror rises to 1mm instantly.

That is possibly as fast as the motor is able to go. How many RPM is that?
Alternatively you might be running into encoder count-rate limits. How many counts per second is that?

Could someone guide me to the git link for the 2.7 pre version with improved TP of LinuxCNC please?

buildbot.linuxcnc.org is the easy way.

Please Log in to join the conversation.

More
12 years 2 weeks ago #52059 by PCW
Master has the improved TP so
git checkout master
should be enough

on your speed issue, you may be running into the encoder max count rate
(you can try turning off the filter bit in the encoders if its currently set)

Please Log in to join the conversation.

More
11 years 11 months ago #53026 by crisiacuf
I have been configuring my gantry in the past few weeks. I took the hal file and edit it by hand.
I now have movement in all axis using both rotary and linear encoder.
The dual joint Y axis works ok. I am using one as a master and the other as slave but I have an awkward problem in inverting the axis direction.

My working .ini file looks like this:

TYPE = LINEAR
MAX_VELOCITY = 125.0
MAX_ACCELERATION = 300.0
BACKLASH = 0.000
FERROR = 5
MIN_FERROR = 1
INPUT_SCALE = 10000
INPUT_SCALE_LINEAR = 200
OUTPUT_SCALE = 125
OUTPUT_SCALE_NEG = -125
OUTPUT_OFFSET = 0.0
MAX_OUTPUT = 125
MIN_LIMIT = 0
MAX_LIMIT = 1100.0
HOME = 0.0
HOME_OFFSET = 0.0
HOME_SEARCH_VEL = 2.0
HOME_LATCH_VEL = -2.0
HOME_USE_INDEX = NO
HOME_IGNORE_LIMITS = YES
HOME_SEQUENCE = 2
DEADBAND = 0.001
P = 450
I = 12
D = 0.2
FF0 = 0
FF1 = 1
FF2 = 0
BIAS = 0
SCALE_P = 0
SCALE_I = 100
SCALE_DEADBAND = 0.006
SCALE_MAXCORR = 0.2
With this config axis works ok, no feed error.

To change axis direction I modified:

INPUT_SCALE = -10000
INPUT_SCALE_LINEAR = -200
OUTPUT_SCALE = -125

Now I get Feed error.

Any idea why?

Please Log in to join the conversation.

More
11 years 11 months ago #53030 by DaBit
Keep these the same:

OUTPUT_SCALE = 125
OUTPUT_SCALE_NEG = -125
MAX_OUTPUT = 125

Please Log in to join the conversation.

More
11 years 11 months ago #53040 by crisiacuf@yahoo.com
Using PNCconf I made 2 configurations, one with motor and encoder inverted and one with motor and encoder non inverted.
The ONLY difference between the 2 .ini and .hal files are changed signs for ENCODER_SCALE and OUTPUT_SCALE.
"+" for non-inverted and "-" for inverted.

Keeping
OUTPUT_SCALE
OUTPUT_SCALE_NEG
MAX_OUTPUT

and

changing signs for
INPUT_SCALE
INPUT_SCALE_LINEAR

returns following error.
Any other ideas? The last resort would be to inverse the command signal for the servos.

PS
I used the SNS-mill configuration mostly and added linear scales for Y and servo for Z.
Thank you DaBit :)

Please Log in to join the conversation.

Time to create page: 0.474 seconds
Powered by Kunena Forum