Wiring Unidrive M100 VFD to MESA 7i76e
7 years 7 months ago #128695
by Immutef
Wiring Unidrive M100 VFD to MESA 7i76e was created by Immutef
Hello,
I am trying to connect the original VFD that came with my milling machine to my 7i76e. Previously I borrowed my Huanyang VFD from my other mill to get things going, but the M100 has a somewhat different wiring requirement ( here's a link to the quick start / wiring ).
M100 Wiring Mode
7i76e Wiring Mode
If i connect ENA+ to PIN9, ENA- to PIN11 and short PIN9 & PIN12 or PIN9 & PIN13 it starts spinning forward/reverse.
I can't figure out how get a proper DIR+/DIR- connection to PIN12 & PIN13.
My last thought was using a relais, and wire NC=PIN12 (FOR), NO=PIN13 (REV) and use ENA- as COM.
I just don't know how to trigger the relais for either FOR or REV with DIR+ or DIR- then [it's late, i'm tired and i'm not an electronics expert
]
Anybody has a general idea for me on how to continue?
Thanks & best regards,
Pierre
I am trying to connect the original VFD that came with my milling machine to my 7i76e. Previously I borrowed my Huanyang VFD from my other mill to get things going, but the M100 has a somewhat different wiring requirement ( here's a link to the quick start / wiring ).
M100 Wiring Mode
Attachment not found
7i76e Wiring Mode
Attachment not found
If i connect ENA+ to PIN9, ENA- to PIN11 and short PIN9 & PIN12 or PIN9 & PIN13 it starts spinning forward/reverse.
I can't figure out how get a proper DIR+/DIR- connection to PIN12 & PIN13.
My last thought was using a relais, and wire NC=PIN12 (FOR), NO=PIN13 (REV) and use ENA- as COM.
I just don't know how to trigger the relais for either FOR or REV with DIR+ or DIR- then [it's late, i'm tired and i'm not an electronics expert
]Anybody has a general idea for me on how to continue?
Thanks & best regards,
Pierre
Please Log in to join the conversation.
7 years 7 months ago #128698
by PCW
Replied by PCW on topic Wiring Unidrive M100 VFD to MESA 7i76e
Looks like PR11 set to 2 will set the drive to ENABLE/DIRECTION mode
Please Log in to join the conversation.
7 years 7 months ago #128720
by Immutef
Replied by Immutef on topic Wiring Unidrive M100 VFD to MESA 7i76e
Good find! I'll check that out later today. Also found this helpful wiring diagram today, so I may be able to figure it out,
Attachment not found
Please Log in to join the conversation.
7 years 7 months ago #128722
by andypugh
Replied by andypugh on topic Wiring Unidrive M100 VFD to MESA 7i76e
The parameter that PCW suggests probably means that you don't need any relays.
The other diagram does not, necessarily, require the enable relay, one relay is enough in your case, that diagram is for a VFD with separate FWD and REV inputs but no enable.
The other diagram does not, necessarily, require the enable relay, one relay is enough in your case, that diagram is for a VFD with separate FWD and REV inputs but no enable.
Please Log in to join the conversation.
7 years 7 months ago #128724
by Immutef
Replied by Immutef on topic Wiring Unidrive M100 VFD to MESA 7i76e
Thanks to both you, I think i figured it out mentally. I also figured it out as it is, with two relais.
Will change the Parameter to 2 later, I guess I'll have to wire it like:
- SPIN ENA+ & SPIN DIR+ to T9
- SPIN ENA- to T11 & T12
- SPIN DIR- to T13
This way SPIN ENA closes enable & run when running and SPIN DIR closed is forward, open is reverse?
I'll later route the T9 to T11 separately through my security relais, so the spindle stops when i hit the ESTOP.
Will change the Parameter to 2 later, I guess I'll have to wire it like:
- SPIN ENA+ & SPIN DIR+ to T9
- SPIN ENA- to T11 & T12
- SPIN DIR- to T13
This way SPIN ENA closes enable & run when running and SPIN DIR closed is forward, open is reverse?
I'll later route the T9 to T11 separately through my security relais, so the spindle stops when i hit the ESTOP.
Please Log in to join the conversation.
7 years 7 months ago #128726
by andypugh
Replied by andypugh on topic Wiring Unidrive M100 VFD to MESA 7i76e
I think that should work. You could consider simply jumpering "enable" so the VFD is "live" any time the machine is on.
Please Log in to join the conversation.