6 years 3 weeks ago #185382
by COlger81
Locking indexer issues was created by COlger81
Are there any known issues with the "locking indexer" function? While rotary is locked with air brake, and servo is on hold (no command input to servo), encoder walks out of position until estop is caused by following errors. The servo shaft is not turning and rotary is not moving so this is a tough one to solve.
Please Log in to join the conversation.
- Todd Zuercher
- Offline
- Platinum Member
-
Less
More
- Posts: 4739
- Thank you received: 2
6 years 3 weeks ago #185394
by Todd Zuercher
Replied by Todd Zuercher on topic Locking indexer issues
So you are saying that even though everything is mechanically locked your encoder is counting up or down?
If that is the case you need to check for an electrical problem in your encoder system. Either it is picking up electrical interference causing false counts, or there is a short or bad connection somewhere causing false counts.
Check your grounds, are you using shielded cables, are the shields properly grounded (at only one end).
If that is the case you need to check for an electrical problem in your encoder system. Either it is picking up electrical interference causing false counts, or there is a short or bad connection somewhere causing false counts.
Check your grounds, are you using shielded cables, are the shields properly grounded (at only one end).
Please Log in to join the conversation.
6 years 3 weeks ago #185461
by COlger81
Replied by COlger81 on topic Locking indexer issues
Yes, mechanically locked and encoder freaks out as soon as a milling load is applied to part. When tool contacts part, it initially might fluctuate 1 or 2 encoder counts, then over a few seconds, with no mechanical movement. Encoder counts freak out and following errors trip estop.
Yes, shielded CAT6 cable with proper shielding on one end. I'm suspecting a faulty drive if there's no known bugs with locking indexer function.
Is there a way to ignore position of A axis while brake is locked? It would at least help me with diagnosing.
Yes, shielded CAT6 cable with proper shielding on one end. I'm suspecting a faulty drive if there's no known bugs with locking indexer function.
Is there a way to ignore position of A axis while brake is locked? It would at least help me with diagnosing.
Please Log in to join the conversation.
- Todd Zuercher
- Offline
- Platinum Member
-
Less
More
- Posts: 4739
- Thank you received: 2
6 years 3 weeks ago #185470
by Todd Zuercher
Replied by Todd Zuercher on topic Locking indexer issues
Have you tried plotting the encoder A and B signals with Halscope when the problem is occurring and when it isn't for comparison. Also, looking at those signals with a real scope might be enlightening.
Please Log in to join the conversation.
6 years 3 weeks ago #185472
by COlger81
Replied by COlger81 on topic Locking indexer issues
It's showing over and under shoot but nothing is mechanically moving. This is a DMM DYN4 which simulates encoder counts to feed 7i77. It does not actually directly pass through raw encoder signals.
Please Log in to join the conversation.
- Todd Zuercher
- Offline
- Platinum Member
-
Less
More
- Posts: 4739
- Thank you received: 2
6 years 3 weeks ago #185474
by Todd Zuercher
Replied by Todd Zuercher on topic Locking indexer issues
All bets might be off then. Is the drive being disabled when in "locked" mode?
You might need to contact DMM and ask their opinion what might be going on with their goofy encoder.
You might need to contact DMM and ask their opinion what might be going on with their goofy encoder.
Please Log in to join the conversation.
6 years 3 weeks ago #185480
by COlger81
Replied by COlger81 on topic Locking indexer issues
Yes, drive is "disabled". DMM has a "SHOLD" input that is verified functioning. They call it a servo hold which is goofy. Faulty encoder or drive most likely.
Please Log in to join the conversation.
- Mike_Eitel
- Offline
- Platinum Member
-
Less
More
- Posts: 1018
- Thank you received: 0
6 years 3 weeks ago #185487
by Mike_Eitel
Replied by Mike_Eitel on topic Locking indexer issues
You sometimes can improve the shilding against high frequencies when you connect the free shield end via a low inductive capacitor. Fx. a ceramic one.
Mike