- Posts: 90
- Thank you received: 0
Mesa 7i76e + VFD Omron 3g3mv
- MarcoGaspar
- Topic Author
- Offline
- Premium Member
-
Less
More
4 years 10 months ago #228484
by MarcoGaspar
Mesa 7i76e + VFD Omron 3g3mv was created by MarcoGaspar
Hello,
Can some one help me to wiring Mesa 7i76e to VFD Omron 3g3mv?
Best Regards,
Marco Gaspar
Can some one help me to wiring Mesa 7i76e to VFD Omron 3g3mv?
Best Regards,
Marco Gaspar
Please Log in to join the conversation.
4 years 10 months ago #228488
by PCW
Replied by PCW on topic Mesa 7i76e + VFD Omron 3g3mv
This would be my guess: (with S1 set for NPN mode)
TB4 PIN SIGNAL
1 SPINDLE- --> FC
2 SPINDLE OUT --> FR
3 SPINDLE+ --> FS
4 NC
5 SPINDLE ENA- --> SC
6 SPINDLE ENA+ --> S1, S2 Note driving RUN AND STOP inputs in parallel
7 SPINDLE DIR- --> SC
8 SPINDLE DIR+ --> S3
Drive set for 3 wire mode (n052=0) and analog 0 to 10V input (n004=2)
TB4 PIN SIGNAL
1 SPINDLE- --> FC
2 SPINDLE OUT --> FR
3 SPINDLE+ --> FS
4 NC
5 SPINDLE ENA- --> SC
6 SPINDLE ENA+ --> S1, S2 Note driving RUN AND STOP inputs in parallel
7 SPINDLE DIR- --> SC
8 SPINDLE DIR+ --> S3
Drive set for 3 wire mode (n052=0) and analog 0 to 10V input (n004=2)
Please Log in to join the conversation.
- MarcoGaspar
- Topic Author
- Offline
- Premium Member
-
Less
More
- Posts: 90
- Thank you received: 0
4 years 10 months ago #228508
by MarcoGaspar
Replied by MarcoGaspar on topic Mesa 7i76e + VFD Omron 3g3mv
Hello,
Thanks for the answer I'll test it tomorrow.
Thanks for the answer I'll test it tomorrow.
Please Log in to join the conversation.
- MarcoGaspar
- Topic Author
- Offline
- Premium Member
-
Less
More
- Posts: 90
- Thank you received: 0
4 years 10 months ago #228768
by MarcoGaspar
Replied by MarcoGaspar on topic Mesa 7i76e + VFD Omron 3g3mv
Hello,
The frequency change but the spindle don't start.
The frequency change but the spindle don't start.
Please Log in to join the conversation.
4 years 10 months ago #228782
by PCW
Replied by PCW on topic Mesa 7i76e + VFD Omron 3g3mv
Did you set parameter n052 to 0?
Is S1 set for NPN mode?
Are the other motor specific parameters set properly?
Is S1 set for NPN mode?
Are the other motor specific parameters set properly?
Please Log in to join the conversation.
- MarcoGaspar
- Topic Author
- Offline
- Premium Member
-
Less
More
- Posts: 90
- Thank you received: 0
4 years 10 months ago #228795
by MarcoGaspar
Replied by MarcoGaspar on topic Mesa 7i76e + VFD Omron 3g3mv
Hello,
Yes NPN mode and n052 to 0.
The run led blink but don't start.
Before changing the parameters and connect to mesa card when starting manually the led stay on.
Yes NPN mode and n052 to 0.
The run led blink but don't start.
Before changing the parameters and connect to mesa card when starting manually the led stay on.
Please Log in to join the conversation.
4 years 10 months ago #228822
by PCW
Replied by PCW on topic Mesa 7i76e + VFD Omron 3g3mv
Yeah, its not really clear from the manual what the
RUN and /STOP inputs do when changed simultaneously
You might try wiring /STOP (S2) to ground so its always enabled
(leaving the 7I76E ENA to drive S1 = RUN only)
If this does not work, I would probably reprogram N50,N51,N52 to the default
1,2,3 (FWD/REV on S1 and S2) set Switch 1 to PNP mode and drive S1 and S2
with 7I76E field outputs
RUN and /STOP inputs do when changed simultaneously
You might try wiring /STOP (S2) to ground so its always enabled
(leaving the 7I76E ENA to drive S1 = RUN only)
If this does not work, I would probably reprogram N50,N51,N52 to the default
1,2,3 (FWD/REV on S1 and S2) set Switch 1 to PNP mode and drive S1 and S2
with 7I76E field outputs
Please Log in to join the conversation.