Retrofitting knee mill
is more susceptible to ground loop issues
Please Log in to join the conversation.
OT-CNC wrote: Nice clean box JT. I wish mine was roomy. The old ones were smaller and I had to hang the 7i77 off the end in a separate enclosure. I assume your drives don't emit that annoying high pitch whine? Where did you mount the vfd?
The VFD is in the other cabinet on other side, there were 3 cabinets total and I removed the back one, completely gutted the left one and removed all but the drives and DC power supply from the right cabinet. Wine not that I can hear lol oh you said whine.
JT
Please Log in to join the conversation.
PCW wrote: No problem with 7I92 in any setup , but 5I25/6I25 + 7I77 in separate cabinets
is more susceptible to ground loop issues
And I can verify that is a fact!
JT
Please Log in to join the conversation.
bevins wrote:
PCW wrote: A 7I77 + 7I92M is a good choice if the PC is in a separate cabinet than the control/power electronics
Whats the problem with the 7i92M and 7i77 in same control cabinet as the PC?
Nothing. Just that Ethernet is good for 100 metres and you don't need that in your situation. PCI/PCIe may have been a cheaper choice.
Please Log in to join the conversation.
JT
Please Log in to join the conversation.
- tommylight
-
- Away
- Administrator
-
- Posts: 22012
- Thank you received: 3
That is what I use I several retrofits.
Please Log in to join the conversation.
Please Log in to join the conversation.
+24V --> 7I77 field power+ --> 7I77 output --> load --> field power -
Sinking current path (7I77D)
+24V --> load --> 7I77D output --> 7I77 field power common --> field power -
Notice that for sourcing drives the load common is negative and for sinking drives,
the load common is positive. Polarity is important because the relay will have flyback
diodes installed. This means that if you are driving existing relay arrays
is best the get the 7I77 type that matches the original wiring, unless you want to rewire
every relay.
Please Log in to join the conversation.
I’m assuming that sinking would be standard right?