I have three RS485 devices (each operating at 115200 baud) and one BNO08x IMU, which supports UART at 3,000,000 baud, as well as I2C and SPI.Currently, I am using three USB-to-RS485 adapters and one USB-to-UART adapter to connect these devices. This setup is bulky and inconvenient.I am looking for a more integrated solution, such as a single controller or I/O board, that can communicate with all these devices independently and reduce cabling and USB usage.Any recommendations?
Please Log in to join the conversation.
10 months 4 days ago #340569
by NWE
Replied by NWE on topic Recommend hardware solution for multi rs485 channel?
Depends partly on how much data each device needs to transmit/receive, and how often. Theoretically, rs485 can multi-drop a large number of devices. I have used rs485 almost strictly via modbus protocol, but I see you do not mention modbus.
Using modbus rtu (rs485) with the mb2hal component, I was able to operate 1 VFD per converter/adapter. I was reading/writing approximately 16 parameters per VFD several times per second. I could not reliably run 2 VFDs on one converter. It seemed I was pushing the limits on bandwidth. But I had it running a lot slower - I think it was 9600, I needed that for better interference tolerance.
I used the ebyte NA111 ethernet bridge. They seem ok. Maybe a bit sensitive to interference. (I was using them in a large cabinet with one 30hp, one 10hp, two 5hp, and one 3hp 480VAC VFD, so there was plenty interference available and they've been running relatively reliably since about 4 month ago when they started using it.)
I also tried using the ebyte NE2-D11 but was very disappointed with it. It was so sensitive to interference it did not work with the Allen Bradley VFD I tried to interface. Well, it worked, but froze every time, the instant the VFD was started. I want to try it sometime on a sensor, or maybe even multiple sensors, I expect it might be fine for that.
I also have on another LinuxCNC installation a cheap USB to rs232 converter reading a position sensor about 50x per second nearly continuously since about 2016.
Using modbus rtu (rs485) with the mb2hal component, I was able to operate 1 VFD per converter/adapter. I was reading/writing approximately 16 parameters per VFD several times per second. I could not reliably run 2 VFDs on one converter. It seemed I was pushing the limits on bandwidth. But I had it running a lot slower - I think it was 9600, I needed that for better interference tolerance.
I used the ebyte NA111 ethernet bridge. They seem ok. Maybe a bit sensitive to interference. (I was using them in a large cabinet with one 30hp, one 10hp, two 5hp, and one 3hp 480VAC VFD, so there was plenty interference available and they've been running relatively reliably since about 4 month ago when they started using it.)
I also tried using the ebyte NE2-D11 but was very disappointed with it. It was so sensitive to interference it did not work with the Allen Bradley VFD I tried to interface. Well, it worked, but froze every time, the instant the VFD was started. I want to try it sometime on a sensor, or maybe even multiple sensors, I expect it might be fine for that.
I also have on another LinuxCNC installation a cheap USB to rs232 converter reading a position sensor about 50x per second nearly continuously since about 2016.
Please Log in to join the conversation.
10 months 2 days ago #340640
by heaven
Replied by heaven on topic Recommend hardware solution for multi rs485 channel?
The system utilizes three RS485 devices configured in Auto-send mode rather than the standard Query/Response mode to achieve high-speed data transmission. Each device autonomously broadcasts data packets at a 1ms interval. To ensure simultaneous data acquisition and prevent bus contention, right now the solution employs three independent USB-to-RS485 adapters.
I'm looking to move away from USB interfaces due to noise sensitivity and latency concerns at high speeds. I need a more industrial-grade solution that can handle three simultaneous 1ms RS485 streams without data corruption.
I'm looking to move away from USB interfaces due to noise sensitivity and latency concerns at high speeds. I need a more industrial-grade solution that can handle three simultaneous 1ms RS485 streams without data corruption.
Please Log in to join the conversation.
10 months 2 days ago #340642
by rodw
Replied by rodw on topic Recommend hardware solution for multi rs485 channel?
Please Log in to join the conversation.