Weird intermittent bug involving proximity sensors and homing

More
7 years 6 months ago #132030 by Mike@CNCproCuts.com
What is weird is that I didn't change anything ...

Please Log in to join the conversation.

More
7 years 6 months ago #132301 by Mike@CNCproCuts.com

PCW wrote: Can you measure the 7i77 input 07 with a voltmeter relative to field power common
in both switch states and both drive enable states?

That is measure from TB8 pin 8 to TB2 (orange) pin 8 in all states

If you had a noise issue with serial communications I would expect to see
error pop-ups in axis


Here are the voltage values ... now the relays are not changing values ... getting worse

Drives disabled, port 7 opened = 24,2V
Drives disabled, port 7 closed = 0V

Drives enabled, port 7 opened = 24,2V
Drives enabled, port 7 closed = 24,2V ... the relay is now not working on all of them ...

How do I find a ground loop ?

Please Log in to join the conversation.

More
7 years 6 months ago #132302 by PCW
Sounds a bit more like a missing/unconnected field common/ground so as soon as you enable the drives or turn on a relay, field common is pulled up to +24V

Please Log in to join the conversation.

More
7 years 6 months ago #132305 by Mike@CNCproCuts.com

PCW wrote: Sounds a bit more like a missing/unconnected field common/ground so as soon as you enable the drives or turn on a relay, field common is pulled up to +24V


Thanks ! Found an unconnected wire ... now everything works fine ... still don't know how it could have happened but ... that was the problem so thanks a lot for the insights ;)

Please Log in to join the conversation.

More
7 years 6 months ago #132307 by Mike@CNCproCuts.com

andypugh wrote:

Mike@CNCproCuts.com wrote: the 7i84 inputs will have names like "hm2_5i25.0.7i84.0.0.input-00"
You should be able to find them in Halshow


I had not connected the VIN yet ... now I see it so thanks ;)

Please Log in to join the conversation.

More
7 years 5 months ago #132437 by Mike@CNCproCuts.com
Thougt it was solved ... worked fine for 24hrs ... now the problem is back ... very strange ... could a ground loop take time to accumulate voltage ?

Please Log in to join the conversation.

More
7 years 5 months ago #132442 by Mike@CNCproCuts.com
Closing it for 30 minutes ... now it works ... intermittent ... back to square one ...

Please Log in to join the conversation.

More
7 years 5 months ago #132443 by Todd Zuercher
Sounds like a wiring problem somewhere. Check all your connections, plugs, etc. You said you found one loose connection, there could be others.

Please Log in to join the conversation.

More
7 years 5 months ago #132449 by Mike@CNCproCuts.com

Todd Zuercher wrote: Sounds like a wiring problem somewhere. Check all your connections, plugs, etc. You said you found one loose connection, there could be others.


Been checking ... didn't find anything ... must be a design error on my part for the grounding ...

Please Log in to join the conversation.

More
7 years 5 months ago #132749 by andypugh
be aware that cage clamp screw terminals can be 100% tight but that is no good if the wire is below the cage. So you need to pull each wire as well as check the screws.

Please Log in to join the conversation.