Compiling Altivar VFD Modbus comp
When i run the altivar comp i get nothing, its not touching the serialport at all.
i have ran it with -v no difference.
The VFD does have modbus activated since i can read registers with mb2hal component.
That in my world means that serial coms and settings to read the VFD is correct.
Since the VFD comp is changed and compiled against newer linuxcnc software my guess is that something in the modbus lib is wrong and its not able to communicate correctly.
Please Log in to join the conversation.
Swapper wrote: The port sniffing i have tried, maight not have been exactly like that but i tried with mb2hal and got data in the "sniffer"
When i run the altivar comp i get nothing, its not touching the serialport at all.
i have ran it with -v no difference.
The VFD does have modbus activated since i can read registers with mb2hal component.
That in my world means that serial coms and settings to read the VFD is correct.
Since the VFD comp is changed and compiled against newer linuxcnc software my guess is that something in the modbus lib is wrong and its not able to communicate correctly.
Can you describe sniff method?
I compiled altivar comp on 2.7.0 pre not on 2.8. But I can try it.
Please Log in to join the conversation.
i tried the sniffer you provided
socat -d -d PTY: PTY
halrun:
loadusr -W atv_vfd -g -r 19200 -s 1 -t 1 -v -d /dev/pts/5
setp atv_vfd.spindle-on 1
cat /dev/pts/6
No results at all from cat
if you can try the same on 2.8 it would be very appreciated!
Please Log in to join the conversation.
here is the source-code
Please Log in to join the conversation.
Oh now where getting some errors at least
halcmd: setp atv_vfd.enable 1
halcmd: read_data: reading setup parameters:
ERROR invalid crc received 208 - crc_calc 5846
main: read_data retval=-16
ERROR Communication time out
main: write_data retval=-16
read_data: reading setup parameters:
ERROR Communication time out
main: read_data retval=-12
ERROR Communication time out
main: write_data retval=-12
read_data: reading setup parameters:
Please Log in to join the conversation.
Please Log in to join the conversation.
and its works
Don't forget to set the parameters in ATV 310
- 401 : Reference Channel 1 = 164 (for modbus)
- 406 : Channel Configuration = 02 (for separate mode)
- 407 : Command Channel 1 = 10 (for modbus)
- 701 : Modbus Address = 01
- 302 : Rated Motor Power = Nominal motor power given on the nameplate, in kW
- 304 : Rated Motor Voltage = Nominal motor voltage is given on the nameplate, in V.
- 305 : Rated Motor Current = Nominal motor current is given on the nameplate, in A.
- 306 : Rated Motor Frequency = Nominal motor frequency is given on the nameplate, in Hz.
- 307 : Rated Motor Speed = Nominal motor speed is given on the nameplate, in RPM.