- Posts: 1683
- Thank you received: 0
Hal help for home to index with stepgen firmware update
3 years 8 months ago #264372
by Lcvette
Hal help for home to index with stepgen firmware update was created by Lcvette
Hello all,
I am hoping this can be solved here and used as future reference for those connecting index pulse on a step direction system with motor encoders, but not using the encoders for feedback to close the loop.
My system: 7i92+7i76+7i77
- I control the servos drives with the 7i76 in step and direction
- I feed the motor encoders to the 7i77
- I do not run in feedback control mode due to rough operation that could not be resolved.
- Goal: utilize motor encoder index pulse to more accurately/ repeatability home the machine.
- I have new firmware for utilizing this feature from @PCW at Mesa Electronics
- I have attached the new firmware below as well.
Notes from PCW: There are now 2 index-enable hal pins per encoder: the encoder index enable and the stepgen index enable.
Below is the X axis portion from my existing non index pulse home configuration. There are some commented out lines from when we were testing feedback mode.
My hope is to create a hal example for an axis for future searchable reference regarding this scenario as I could not find anything specifically related to this method with updated firmware and linuxcnc 2.9, and did not see an option to select in the config builder softwares like mesact, pncconfig, etc.
Any help is greatly appreciated!
Chris
I am hoping this can be solved here and used as future reference for those connecting index pulse on a step direction system with motor encoders, but not using the encoders for feedback to close the loop.
My system: 7i92+7i76+7i77
- I control the servos drives with the 7i76 in step and direction
- I feed the motor encoders to the 7i77
- I do not run in feedback control mode due to rough operation that could not be resolved.
- Goal: utilize motor encoder index pulse to more accurately/ repeatability home the machine.
- I have new firmware for utilizing this feature from @PCW at Mesa Electronics
- I have attached the new firmware below as well.
Attachment not found
Notes from PCW: There are now 2 index-enable hal pins per encoder: the encoder index enable and the stepgen index enable.
Below is the X axis portion from my existing non index pulse home configuration. There are some commented out lines from when we were testing feedback mode.
Code:
#*******************
# AXIS X JOINT 0
#*******************
setp pid.x.Pgain [JOINT_0]P
setp pid.x.Igain [JOINT_0]I
setp pid.x.Dgain [JOINT_0]D
setp pid.x.bias [JOINT_0]BIAS
setp pid.x.FF0 [JOINT_0]FF0
setp pid.x.FF1 [JOINT_0]FF1
setp pid.x.FF2 [JOINT_0]FF2
setp pid.x.deadband [JOINT_0]DEADBAND
setp pid.x.maxoutput [JOINT_0]MAX_OUTPUT
setp pid.x.error-previous-target true
setp pid.x.maxerror 0
net x-index-enable <=> pid.x.index-enable
net x-enable => pid.x.enable
net x-pos-cmd => pid.x.command
##net x-vel-cmd => pid.x.command-deriv
net x-pos-fb => pid.x.feedback
net x-output => pid.x.output
# Step Gen signals/setup
setp hm2_7i92.0.stepgen.00.dirsetup [JOINT_0]DIRSETUP
setp hm2_7i92.0.stepgen.00.dirhold [JOINT_0]DIRHOLD
setp hm2_7i92.0.stepgen.00.steplen [JOINT_0]STEPLEN
setp hm2_7i92.0.stepgen.00.stepspace [JOINT_0]STEPSPACE
setp hm2_7i92.0.stepgen.00.position-scale [JOINT_0]STEP_SCALE
setp hm2_7i92.0.stepgen.00.step_type 0
setp hm2_7i92.0.stepgen.00.control-type 1
setp hm2_7i92.0.stepgen.00.maxaccel [JOINT_0]STEPGEN_MAXACCEL
setp hm2_7i92.0.stepgen.00.maxvel [JOINT_0]STEPGEN_MAXVEL
# ---closedloop stepper signals---
net x-pos-cmd <= joint.0.motor-pos-cmd
net x-vel-cmd <= joint.0.vel-cmd
net x-output <= hm2_7i92.0.stepgen.00.velocity-cmd
net x-pos-fb <= hm2_7i92.0.stepgen.00.position-fb
##net x-pos-fb <= hm2_7i92.0.encoder.00.position
net x-pos-fb => joint.0.motor-pos-fb
##net x-encpos-fb => joint.0.motor-pos-fb
net x-enable <= joint.0.amp-enable-out
net x-enable => hm2_7i92.0.stepgen.00.enable
# ---Encoder feedback signals/setup---
setp hm2_7i92.0.encoder.00.counter-mode 0
setp hm2_7i92.0.encoder.00.filter 1
setp hm2_7i92.0.encoder.00.index-invert 0
setp hm2_7i92.0.encoder.00.index-mask 0
setp hm2_7i92.0.encoder.00.index-mask-invert 0
setp hm2_7i92.0.encoder.00.scale [JOINT_0]ENCODER_SCALE
# ****the following line is for drive tuning purposes only****
net x-encpos-fb <= hm2_7i92.0.encoder.00.position
net x-vel-fb <= hm2_7i92.0.encoder.00.velocity
net x-pos-fb => joint.0.motor-pos-fb
net x-index-enable joint.0.index-enable <=> hm2_7i92.0.encoder.00.index-enable
net x-pos-rawcounts <= hm2_7i92.0.encoder.00.rawcounts
# ---setup home / limit switch signals---
net home-x => joint.0.home-sw-in
net limit-x => joint.0.neg-lim-sw-in
My hope is to create a hal example for an axis for future searchable reference regarding this scenario as I could not find anything specifically related to this method with updated firmware and linuxcnc 2.9, and did not see an option to select in the config builder softwares like mesact, pncconfig, etc.
Any help is greatly appreciated!
Chris
Please Log in to join the conversation.
3 years 8 months ago #264600
by Lcvette
Replied by Lcvette on topic Hal help for home to index with stepgen firmware update
I am updating this thread as I have gotten my machine running with home to index using step direction in open loop mode but with the use of encoders being connected to one of my mesa boards. below is the current working hardware configuration.
7i92+7i76+7i77
This configuration requires the use of an updated firmware from Mesa to utilize a second stepgen encoder enable signal. once the new firmware is obtained, the following x axis Hal excerpt can be used as a guide template for what will be needed in Hal.
I started with a config built using PNCCONFIG to create the Hal files. the following are the selections required to make the config correct for editing:
- FEEDBACK = ACTUAL (this creates the encoder halpins which we need, but we will edit some Hal lines to disable feedback control.)
- Set the joint STEPGENS and ENCODERs on the same designation, For Example: X Axis, joint, would be configured on STEPGEN.00 and ENCODER.00 They need to match for setting the stepgen index enable signal.
- The rest must be configured such that you are using the correct cards and in the correct order as the firmware you have. these instructions may come with your firmware notes.
For the Hal edits, there are really only two needed once you have a feedback type config built from PNCCONFIG. This is to remove the feedback loop to the PID, This is shown below in Bold BLUE, we are simply renaming the net so that it isn't the source of feedback the PID uses for motion.
net x-pos-fb <= hm2_7i92.0.encoder.00.position
will be changed to:
net x-encpos-fb <= hm2_7i92.0.encoder.00.position
The next change is where we define the index enable pin.
net x-index-enable joint.0.index-enable <=> hm2_7i92.0.encoder.00.index-enable
will be changed to:
net x-index-enable joint.0.index-enable <=> hm2_7i92.0.stepgen.00.index-enable
This should b the extent of what will be required to change in Hal. You will need to update the INI file joint homing sections and change the following highlighted items to enable home to index. The other settings will be per your own machine requirements. HOME_USE_INDEX = YES.
From the INI file of the configuration output change the line as show below:
MIN_LIMIT = 0
MAX_LIMIT = 26.5
HOME_OFFSET = .170
HOME_SEARCH_VEL = -2.00
HOME_LATCH_VEL = .100
HOME_FINAL_VEL = .400
HOME_USE_INDEX = YES
HOME_SEQUENCE = 1
Note these edits will of course need to be done for ALL of your used JOINTS (X, Y, Z, A, B etc...)
Hopefully this helps someone out, It was new and as of yet undocumented and the information was rather spread out and hidden in various threads. thanks to the help of PCW and Tom_L I was able to get my machine homing to index! and it is Glorious!
Edit the above Hal Lines from the Hal File, their location is shown below for clarity:
#*******************
# AXIS X JOINT 0
#*******************
setp pid.x.Pgain [JOINT_0]P
setp pid.x.Igain [JOINT_0]I
setp pid.x.Dgain [JOINT_0]D
setp pid.x.bias [JOINT_0]BIAS
setp pid.x.FF0 [JOINT_0]FF0
setp pid.x.FF1 [JOINT_0]FF1
setp pid.x.FF2 [JOINT_0]FF2
setp pid.x.deadband [JOINT_0]DEADBAND
setp pid.x.maxoutput [JOINT_0]MAX_OUTPUT
setp pid.x.error-previous-target true
setp pid.x.maxerror 0
net x-index-enable <=> pid.x.index-enable
net x-enable => pid.x.enable
net x-pos-cmd => pid.x.command
net x-pos-fb => pid.x.feedback
net x-output => pid.x.output
# Step Gen signals/setup
setp hm2_7i92.0.stepgen.00.dirsetup [JOINT_0]DIRSETUP
setp hm2_7i92.0.stepgen.00.dirhold [JOINT_0]DIRHOLD
setp hm2_7i92.0.stepgen.00.steplen [JOINT_0]STEPLEN
setp hm2_7i92.0.stepgen.00.stepspace [JOINT_0]STEPSPACE
setp hm2_7i92.0.stepgen.00.position-scale [JOINT_0]STEP_SCALE
setp hm2_7i92.0.stepgen.00.step_type 0
setp hm2_7i92.0.stepgen.00.control-type 1
setp hm2_7i92.0.stepgen.00.maxaccel [JOINT_0]STEPGEN_MAXACCEL
setp hm2_7i92.0.stepgen.00.maxvel [JOINT_0]STEPGEN_MAXVEL
# ---closedloop stepper signals---
net x-pos-cmd <= joint.0.motor-pos-cmd
net x-vel-cmd <= joint.0.vel-cmd
net x-output <= hm2_7i92.0.stepgen.00.velocity-cmd
net x-pos-fb <= hm2_7i92.0.stepgen.00.position-fb
net x-pos-fb => joint.0.motor-pos-fb
net x-enable <= joint.0.amp-enable-out
net x-enable => hm2_7i92.0.stepgen.00.enable
# ---Encoder feedback signals/setup---
setp hm2_7i92.0.encoder.00.counter-mode 0
setp hm2_7i92.0.encoder.00.filter 1
setp hm2_7i92.0.encoder.00.index-invert 0
setp hm2_7i92.0.encoder.00.index-mask 0
setp hm2_7i92.0.encoder.00.index-mask-invert 0
setp hm2_7i92.0.encoder.00.scale [JOINT_0]ENCODER_SCALE
net x-encpos-fb <= hm2_7i92.0.encoder.00.position
net x-vel-fb <= hm2_7i92.0.encoder.00.velocity
net x-pos-fb => joint.0.motor-pos-fb
net x-index-enable joint.0.index-enable <=> hm2_7i92.0.stepgen.00.index-enable
net x-pos-rawcounts <= hm2_7i92.0.encoder.00.rawcounts
7i92+7i76+7i77
This configuration requires the use of an updated firmware from Mesa to utilize a second stepgen encoder enable signal. once the new firmware is obtained, the following x axis Hal excerpt can be used as a guide template for what will be needed in Hal.
I started with a config built using PNCCONFIG to create the Hal files. the following are the selections required to make the config correct for editing:
- FEEDBACK = ACTUAL (this creates the encoder halpins which we need, but we will edit some Hal lines to disable feedback control.)
- Set the joint STEPGENS and ENCODERs on the same designation, For Example: X Axis, joint, would be configured on STEPGEN.00 and ENCODER.00 They need to match for setting the stepgen index enable signal.
- The rest must be configured such that you are using the correct cards and in the correct order as the firmware you have. these instructions may come with your firmware notes.
For the Hal edits, there are really only two needed once you have a feedback type config built from PNCCONFIG. This is to remove the feedback loop to the PID, This is shown below in Bold BLUE, we are simply renaming the net so that it isn't the source of feedback the PID uses for motion.
net x-pos-fb <= hm2_7i92.0.encoder.00.position
will be changed to:
net x-encpos-fb <= hm2_7i92.0.encoder.00.position
The next change is where we define the index enable pin.
net x-index-enable joint.0.index-enable <=> hm2_7i92.0.encoder.00.index-enable
will be changed to:
net x-index-enable joint.0.index-enable <=> hm2_7i92.0.stepgen.00.index-enable
This should b the extent of what will be required to change in Hal. You will need to update the INI file joint homing sections and change the following highlighted items to enable home to index. The other settings will be per your own machine requirements. HOME_USE_INDEX = YES.
From the INI file of the configuration output change the line as show below:
MIN_LIMIT = 0
MAX_LIMIT = 26.5
HOME_OFFSET = .170
HOME_SEARCH_VEL = -2.00
HOME_LATCH_VEL = .100
HOME_FINAL_VEL = .400
HOME_USE_INDEX = YES
HOME_SEQUENCE = 1
Note these edits will of course need to be done for ALL of your used JOINTS (X, Y, Z, A, B etc...)
Hopefully this helps someone out, It was new and as of yet undocumented and the information was rather spread out and hidden in various threads. thanks to the help of PCW and Tom_L I was able to get my machine homing to index! and it is Glorious!
Edit the above Hal Lines from the Hal File, their location is shown below for clarity:
#*******************
# AXIS X JOINT 0
#*******************
setp pid.x.Pgain [JOINT_0]P
setp pid.x.Igain [JOINT_0]I
setp pid.x.Dgain [JOINT_0]D
setp pid.x.bias [JOINT_0]BIAS
setp pid.x.FF0 [JOINT_0]FF0
setp pid.x.FF1 [JOINT_0]FF1
setp pid.x.FF2 [JOINT_0]FF2
setp pid.x.deadband [JOINT_0]DEADBAND
setp pid.x.maxoutput [JOINT_0]MAX_OUTPUT
setp pid.x.error-previous-target true
setp pid.x.maxerror 0
net x-index-enable <=> pid.x.index-enable
net x-enable => pid.x.enable
net x-pos-cmd => pid.x.command
net x-pos-fb => pid.x.feedback
net x-output => pid.x.output
# Step Gen signals/setup
setp hm2_7i92.0.stepgen.00.dirsetup [JOINT_0]DIRSETUP
setp hm2_7i92.0.stepgen.00.dirhold [JOINT_0]DIRHOLD
setp hm2_7i92.0.stepgen.00.steplen [JOINT_0]STEPLEN
setp hm2_7i92.0.stepgen.00.stepspace [JOINT_0]STEPSPACE
setp hm2_7i92.0.stepgen.00.position-scale [JOINT_0]STEP_SCALE
setp hm2_7i92.0.stepgen.00.step_type 0
setp hm2_7i92.0.stepgen.00.control-type 1
setp hm2_7i92.0.stepgen.00.maxaccel [JOINT_0]STEPGEN_MAXACCEL
setp hm2_7i92.0.stepgen.00.maxvel [JOINT_0]STEPGEN_MAXVEL
# ---closedloop stepper signals---
net x-pos-cmd <= joint.0.motor-pos-cmd
net x-vel-cmd <= joint.0.vel-cmd
net x-output <= hm2_7i92.0.stepgen.00.velocity-cmd
net x-pos-fb <= hm2_7i92.0.stepgen.00.position-fb
net x-pos-fb => joint.0.motor-pos-fb
net x-enable <= joint.0.amp-enable-out
net x-enable => hm2_7i92.0.stepgen.00.enable
# ---Encoder feedback signals/setup---
setp hm2_7i92.0.encoder.00.counter-mode 0
setp hm2_7i92.0.encoder.00.filter 1
setp hm2_7i92.0.encoder.00.index-invert 0
setp hm2_7i92.0.encoder.00.index-mask 0
setp hm2_7i92.0.encoder.00.index-mask-invert 0
setp hm2_7i92.0.encoder.00.scale [JOINT_0]ENCODER_SCALE
net x-encpos-fb <= hm2_7i92.0.encoder.00.position
net x-vel-fb <= hm2_7i92.0.encoder.00.velocity
net x-pos-fb => joint.0.motor-pos-fb
net x-index-enable joint.0.index-enable <=> hm2_7i92.0.stepgen.00.index-enable
net x-pos-rawcounts <= hm2_7i92.0.encoder.00.rawcounts
Please Log in to join the conversation.
3 years 5 months ago #272381
by jhandel
Replied by jhandel on topic Hal help for home to index with stepgen firmware update
I should read the whole thread (especially the first part)... you are running 2.9... thanks and sorry for the noise.. I would delete the previous post if it was allowed.
Please Log in to join the conversation.
- tommylight
-
- Away
- Administrator
-
Less
More
- Posts: 22012
- Thank you received: 3
3 years 5 months ago #272420
by tommylight
Replied by tommylight on topic Hal help for home to index with stepgen firmware update
Deleted.
Pretty sure you should be able to delete your own posts, but can not recall for sure.
Pretty sure you should be able to delete your own posts, but can not recall for sure.
Please Log in to join the conversation.
3 years 5 months ago #272462
by rodw
Replied by rodw on topic Hal help for home to index with stepgen firmware update
No, its not possible. Best solution is to delete the content and put a note inDeleted.
Pretty sure you should be able to delete your own posts, but can not recall for sure.
Please Log in to join the conversation.
- besriworld
- Offline
- Platinum Member
-
Less
More
- Posts: 327
- Thank you received: 0
2 years 4 months ago #301985
by besriworld
Replied by besriworld on topic Hal help for home to index with stepgen firmware update
Hello, I'm trying to set up a home with an index. When HOME_IGNORE_INDEX = NO I have repeatability 13-20uM. For more accurate I want to use the index pulse from the servo driver. I have the special firmware. Each time it is zeroed in a different place. I can't find a logical reason. I use low speed but no change. I am attaching the files. I work on the X axis.
In Halshow I test the index signal comes.
In Halshow I test the index signal comes.
Attachment not found
Attachment not found
Please Log in to join the conversation.
2 years 4 months ago #301994
by PCW
Replied by PCW on topic Hal help for home to index with stepgen firmware update
Unless LinuxCNC is using encoder feedback
(and your hal file is not), you cannot use homing
to encoder index.
It is possible to home open loop step/dir systems
to index with firmware that has support for step/dir index
(and your hal file is not), you cannot use homing
to encoder index.
It is possible to home open loop step/dir systems
to index with firmware that has support for step/dir index
Please Log in to join the conversation.
- besriworld
- Offline
- Platinum Member
-
Less
More
- Posts: 327
- Thank you received: 0
2 years 4 months ago #302002
by besriworld
Replied by besriworld on topic Hal help for home to index with stepgen firmware update
Yes, that is the case. On the other topic, I have firmware supports the stepgen index.
In another thread you explained how to modify my firmware.
"To support stepgen index, you need
1. Recent LinuxCNC 2.9 or master
2 To change the stepgen revision from 0x02 to 0xC2
3. If you want shared encoder/stepgen index pins, replace
QCountIDXPin with SharedSDQCIdxPin
(the module number must match on shared pins
so stepgen index 00 == encoderindex 00)
like:
IOPortTag & x"NN" & QCountTag &SharedSDQCIdxPin,
4.If you want just a stepgen index, use :
IOPortTag & x"NN" & StepGenTag & StepGenIndexPin, "
I made a mistake in the previous comment. The signal is:HOME_USE_INDEX
In another thread you explained how to modify my firmware.
"To support stepgen index, you need
1. Recent LinuxCNC 2.9 or master
2 To change the stepgen revision from 0x02 to 0xC2
3. If you want shared encoder/stepgen index pins, replace
QCountIDXPin with SharedSDQCIdxPin
(the module number must match on shared pins
so stepgen index 00 == encoderindex 00)
like:
IOPortTag & x"NN" & QCountTag &SharedSDQCIdxPin,
4.If you want just a stepgen index, use :
IOPortTag & x"NN" & StepGenTag & StepGenIndexPin, "
I made a mistake in the previous comment. The signal is:HOME_USE_INDEX
Please Log in to join the conversation.
2 years 4 months ago #302011
by PCW
Replied by PCW on topic Hal help for home to index with stepgen firmware update
If you successfully built software that incorporates stepgen index
you should have a stepgen index enable pin for each stepgen.
This is the pin you must use (rather than the encoder index enable pin)
if you are homing to index on a step/dir system without encoder
feedback to LinuxCNC.
you should have a stepgen index enable pin for each stepgen.
This is the pin you must use (rather than the encoder index enable pin)
if you are homing to index on a step/dir system without encoder
feedback to LinuxCNC.
Please Log in to join the conversation.
- besriworld
- Offline
- Platinum Member
-
Less
More
- Posts: 327
- Thank you received: 0
2 years 4 months ago #302030
by besriworld
Replied by besriworld on topic Hal help for home to index with stepgen firmware update
All day I tried different options. I'm pretty sure I made this change before I left the shop...it was connected to the correct pin.
Please Log in to join the conversation.
Time to create page: 0.202 seconds