7i77-Analog Output TB5 does not appear in HalShow and is not found

More
2 years 4 months ago #301978 by programador
Hello everyone, please, I need to configure the analog outputs of the 7i77d board that is connected to the 7i96s board. The digital outputs and inputs already appear in the HalShow figure attached below. But unfortunately nothing appears regarding analog inputs and outputs.
The 7i96s board has already been updated with 7i96s_7i77d.bin, the green LED lights up when the 7i96s board is connected and run by linuxCNC, the 7i77 digital inputs and outputs are appearing and being activated in LinuxCNC. But the analog part doesn't appear at all.
I tried to use the Pncconf Wizard to have a graphic example of how to configure the analog part of the 7i96s with the 7i77d, but unfortunately this newer version of the board is not available. So, following previous recommendations, I used 7i92 with 7i77 as examples to generate the necessary Hal files as an example, I edited the name 7i92 to 7i96s, but I did not get the satisfactory result, the error that was not found appeared: . /7i96s_7i77analogico1.hal:64: parameter or pin 'hm2_7i96s.0.7i77.0.1.analogout0-scalemax' not found

How do I do the basic configuration in HAL so that hm2_7i96s.0.7i77.0.1.analogout0... appears?


# Generated by PNCconf at Fri May 31 13:19:30 2024
# Using LinuxCNC version:  Master (2.9)
# If you make changes to this file, they will be
# overwritten when you run PNCconf again

loadrt [KINS]KINEMATICS
loadrt [EMCMOT]EMCMOT servo_period_nsec=[EMCMOT]SERVO_PERIOD num_joints=[KINS]JOINTS
loadrt hostmot2
#loadrt hm2_eth board_ip="10.10.10.10" config="num_encoders=6 num_pwmgens=0 num_stepgens=0 sserial_port_0=000xxxxx" 
loadrt hm2_eth board_ip="10.10.10.10" config="num_encoders=1 num_pwmgens=1 num_stepgens=5 sserial_port_0=0xxxxxxx"

#setp    hm2_7i92.0.watchdog.timeout_ns 5000000

setp    hm2_7i96s.0.pwmgen.pwm_frequency 20000
setp    hm2_7i96s.0.pwmgen.pdm_frequency 6000000
setp    hm2_7i96s.0.watchdog.timeout_ns 5000000

loadrt pid names=pid.x,pid.y,pid.z,pid.a,pid.s

#addf hm2_7i92.0.read          servo-thread
addf hm2_7i96s.0.read          servo-thread

addf motion-command-handler   servo-thread
addf motion-controller        servo-thread
addf pid.x.do-pid-calcs       servo-thread
addf pid.y.do-pid-calcs       servo-thread
addf pid.z.do-pid-calcs       servo-thread
addf pid.a.do-pid-calcs       servo-thread
addf pid.s.do-pid-calcs       servo-thread
#addf hm2_7i92.0.write         servo-thread
addf hm2_7i96s.0.write         servo-thread
setp hm2_7i96s.0.dpll.01.timer-us -50
setp hm2_7i96s.0.stepgen.timer-number 1

# external output signals


# external input signals


#*******************
#  AXIS X JOINT 0
#*******************

setp   pid.x.Pgain     [JOINT_0]P
setp   pid.x.Igain     [JOINT_0]I
setp   pid.x.Dgain     [JOINT_0]D
setp   pid.x.bias      [JOINT_0]BIAS
setp   pid.x.FF0       [JOINT_0]FF0
setp   pid.x.FF1       [JOINT_0]FF1
setp   pid.x.FF2       [JOINT_0]FF2
setp   pid.x.deadband  [JOINT_0]DEADBAND
setp   pid.x.maxoutput [JOINT_0]MAX_OUTPUT
setp   pid.x.error-previous-target true

net x-index-enable  =>  pid.x.index-enable
net x-enable        =>  pid.x.enable
net x-pos-cmd       =>  pid.x.command
net x-pos-fb        =>  pid.x.feedback
net x-output        <=  pid.x.output

# ---PWM Generator signals/setup---

setp      [JOINT_0]OUTPUT_SCALE
setp   hm2_7i96s.0.7i77.0.1.analogout0-minlim    [JOINT_0]OUTPUT_MIN_LIMIT
setp   hm2_7i96s.0.7i77.0.1.analogout0-maxlim    [JOINT_0]OUTPUT_MAX_LIMIT

net x-output     => hm2_7i96s.0.7i77.0.1.analogout0
net x-pos-cmd    <= joint.0.motor-pos-cmd
net x-enable     <= joint.0.amp-enable-out
# enable _all_ sserial pwmgens
net x-enable   => hm2_7i96s.0.7i77.0.1.analogena

# ---Encoder feedback signals/setup---

setp    hm2_7i96s.0.encoder.00.counter-mode 0
setp    hm2_7i96s.0.encoder.00.filter 1
setp    hm2_7i96s.0.encoder.00.index-invert 0
setp    hm2_7i96s.0.encoder.00.index-mask 0
setp    hm2_7i96s.0.encoder.00.index-mask-invert 0
setp    hm2_7i96s.0.encoder.00.scale  [JOINT_0]ENCODER_SCALE

net x-pos-fb               <=  hm2_7i96s.0.encoder.00.position
net x-vel-fb               <=  hm2_7i96s.0.encoder.00.velocity
net x-pos-fb               =>  joint.0.motor-pos-fb
net x-index-enable    joint.0.index-enable  <=>  hm2_7i96s.0.encoder.00.index-enable
net x-pos-rawcounts        <=  hm2_7i96s.0.encoder.00.rawcounts

# ---setup home / limit switch signals---

net x-home-sw     =>  joint.0.home-sw-in
net x-neg-limit     =>  joint.0.neg-lim-sw-in
net x-pos-limit     =>  joint.0.pos-lim-sw-in

#*******************
#  AXIS Y JOINT 1
#*******************

setp   pid.y.Pgain     [JOINT_1]P
setp   pid.y.Igain     [JOINT_1]I
setp   pid.y.Dgain     [JOINT_1]D
setp   pid.y.bias      [JOINT_1]BIAS
setp   pid.y.FF0       [JOINT_1]FF0
setp   pid.y.FF1       [JOINT_1]FF1
setp   pid.y.FF2       [JOINT_1]FF2
setp   pid.y.deadband  [JOINT_1]DEADBAND
setp   pid.y.maxoutput [JOINT_1]MAX_OUTPUT
setp   pid.y.error-previous-target true

net y-index-enable  =>  pid.y.index-enable
net y-enable        =>  pid.y.enable
net y-pos-cmd       =>  pid.y.command
net y-pos-fb        =>  pid.y.feedback
net y-output        <=  pid.y.output

# ---PWM Generator signals/setup---

setp   hm2_7i96s.0.7i77.0.1.analogout1-scalemax  [JOINT_1]OUTPUT_SCALE
setp   hm2_7i96s.0.7i77.0.1.analogout1-minlim    [JOINT_1]OUTPUT_MIN_LIMIT
setp   hm2_7i96s.0.7i77.0.1.analogout1-maxlim    [JOINT_1]OUTPUT_MAX_LIMIT

net y-output     => hm2_7i96s.0.7i77.0.1.analogout1
net y-pos-cmd    <= joint.1.motor-pos-cmd
net y-enable     <= joint.1.amp-enable-out

# ---Encoder feedback signals/setup---

setp    hm2_7i96s.0.encoder.01.counter-mode 0
setp    hm2_7i96s.0.encoder.01.filter 1
setp    hm2_7i96s.0.encoder.01.index-invert 0
setp    hm2_7i96s.0.encoder.01.index-mask 0
setp    hm2_7i96s.0.encoder.01.index-mask-invert 0
setp    hm2_7i96s.0.encoder.01.scale  [JOINT_1]ENCODER_SCALE

net y-pos-fb               <=  hm2_7i96s.0.encoder.01.position
net y-vel-fb               <=  hm2_7i96s.0.encoder.01.velocity
net y-pos-fb               =>  joint.1.motor-pos-fb
net y-index-enable    joint.1.index-enable  <=>  hm2_7i96s.0.encoder.01.index-enable
net y-pos-rawcounts        <=  hm2_7i96s.0.encoder.01.rawcounts

# ---setup home / limit switch signals---

net y-home-sw     =>  joint.1.home-sw-in
net y-neg-limit     =>  joint.1.neg-lim-sw-in
net y-pos-limit     =>  joint.1.pos-lim-sw-in

#*******************
#  AXIS Z JOINT 2
#*******************

setp   pid.z.Pgain     [JOINT_2]P
setp   pid.z.Igain     [JOINT_2]I
setp   pid.z.Dgain     [JOINT_2]D
setp   pid.z.bias      [JOINT_2]BIAS
setp   pid.z.FF0       [JOINT_2]FF0
setp   pid.z.FF1       [JOINT_2]FF1
setp   pid.z.FF2       [JOINT_2]FF2
setp   pid.z.deadband  [JOINT_2]DEADBAND
setp   pid.z.maxoutput [JOINT_2]MAX_OUTPUT
setp   pid.z.error-previous-target true

net z-index-enable  =>  pid.z.index-enable
net z-enable        =>  pid.z.enable
net z-pos-cmd       =>  pid.z.command
net z-pos-fb        =>  pid.z.feedback
net z-output        <=  pid.z.output

# ---PWM Generator signals/setup---

setp   hm2_7i96s.0.7i77.0.1.analogout2-scalemax  [JOINT_2]OUTPUT_SCALE
setp   hm2_7i96s.0.7i77.0.1.analogout2-minlim    [JOINT_2]OUTPUT_MIN_LIMIT
setp   hm2_7i96s.0.7i77.0.1.analogout2-maxlim    [JOINT_2]OUTPUT_MAX_LIMIT

net z-output     => hm2_7i96s.0.7i77.0.1.analogout2
net z-pos-cmd    <= joint.2.motor-pos-cmd
net z-enable     <= joint.2.amp-enable-out

# ---Encoder feedback signals/setup---

setp    hm2_7i96s.0.encoder.02.counter-mode 0
setp    hm2_7i96s.0.encoder.02.filter 1
setp    hm2_7i96s.0.encoder.02.index-invert 0
setp    hm2_7i96s.0.encoder.02.index-mask 0
setp    hm2_7i96s.0.encoder.02.index-mask-invert 0
setp    hm2_7i96s.0.encoder.02.scale  [JOINT_2]ENCODER_SCALE

net z-pos-fb               <=  hm2_7i96s.0.encoder.02.position
net z-vel-fb               <=  hm2_7i96s.0.encoder.02.velocity
net z-pos-fb               =>  joint.2.motor-pos-fb
net z-index-enable    joint.2.index-enable  <=>  hm2_7i96s.0.encoder.02.index-enable
net z-pos-rawcounts        <=  hm2_7i96s.0.encoder.02.rawcounts

# ---setup home / limit switch signals---

net z-home-sw     =>  joint.2.home-sw-in
net z-neg-limit     =>  joint.2.neg-lim-sw-in
net z-pos-limit     =>  joint.2.pos-lim-sw-in

#*******************
#  AXIS A JOINT 3
#*******************

setp   pid.a.Pgain     [JOINT_3]P
setp   pid.a.Igain     [JOINT_3]I
setp   pid.a.Dgain     [JOINT_3]D
setp   pid.a.bias      [JOINT_3]BIAS
setp   pid.a.FF0       [JOINT_3]FF0
setp   pid.a.FF1       [JOINT_3]FF1
setp   pid.a.FF2       [JOINT_3]FF2
setp   pid.a.deadband  [JOINT_3]DEADBAND
setp   pid.a.maxoutput [JOINT_3]MAX_OUTPUT
setp   pid.a.error-previous-target true

net a-index-enable  =>  pid.a.index-enable
net a-enable        =>  pid.a.enable
net a-pos-cmd       =>  pid.a.command
net a-pos-fb        =>  pid.a.feedback
net a-output        <=  pid.a.output

# ---PWM Generator signals/setup---

setp   hm2_7i96s.0.7i77.0.1.analogout3-scalemax  [JOINT_3]OUTPUT_SCALE
setp   hm2_7i96s.0.7i77.0.1.analogout3-minlim    [JOINT_3]OUTPUT_MIN_LIMIT
setp   hm2_7i96s.0.7i77.0.1.analogout3-maxlim    [JOINT_3]OUTPUT_MAX_LIMIT

net a-output     => hm2_7i96s.0.7i77.0.1.analogout3
net a-pos-cmd    <= joint.3.motor-pos-cmd
net a-enable     <= joint.3.amp-enable-out

# ---Encoder feedback signals/setup---

setp    hm2_7i96s.0.encoder.03.counter-mode 0
setp    hm2_7i96s.0.encoder.03.filter 1
setp    hm2_7i96s.0.encoder.03.index-invert 0
setp    hm2_7i96s.0.encoder.03.index-mask 0
setp    hm2_7i96s.0.encoder.03.index-mask-invert 0
setp    hm2_7i96s.0.encoder.03.scale  [JOINT_3]ENCODER_SCALE

net a-pos-fb               <=  hm2_7i96s.0.encoder.03.position
net a-vel-fb               <=  hm2_7i96s.0.encoder.03.velocity
net a-pos-fb               =>  joint.3.motor-pos-fb
net a-index-enable    joint.3.index-enable  <=>  hm2_7i96s.0.encoder.03.index-enable
net a-pos-rawcounts        <=  hm2_7i96s.0.encoder.03.rawcounts

# ---setup home / limit switch signals---

net a-home-sw     =>  joint.3.home-sw-in
net a-neg-limit     =>  joint.3.neg-lim-sw-in
net a-pos-limit     =>  joint.3.pos-lim-sw-in

#*******************
#  SPINDLE
#*******************

setp   pid.s.Pgain     [SPINDLE_0]P
setp   pid.s.Igain     [SPINDLE_0]I
setp   pid.s.Dgain     [SPINDLE_0]D
setp   pid.s.bias      [SPINDLE_0]BIAS
setp   pid.s.FF0       [SPINDLE_0]FF0
setp   pid.s.FF1       [SPINDLE_0]FF1
setp   pid.s.FF2       [SPINDLE_0]FF2
setp   pid.s.deadband  [SPINDLE_0]DEADBAND
setp   pid.s.maxoutput [SPINDLE_0]MAX_OUTPUT
setp   pid.s.error-previous-target true

net spindle-index-enable  =>  pid.s.index-enable
net spindle-enable        =>  pid.s.enable
net spindle-vel-cmd-rpm     => pid.s.command
net spindle-vel-fb-rpm      => pid.s.feedback
net spindle-output        <=  pid.s.output

# ---setup spindle control signals---

net spindle-vel-cmd-rps        <=  spindle.0.speed-out-rps
net spindle-vel-cmd-rps-abs    <=  spindle.0.speed-out-rps-abs
net spindle-vel-cmd-rpm        <=  spindle.0.speed-out
net spindle-vel-cmd-rpm-abs    <=  spindle.0.speed-out-abs
net spindle-enable             <=  spindle.0.on
net spindle-cw                 <=  spindle.0.forward
net spindle-ccw                <=  spindle.0.reverse
net spindle-brake              <=  spindle.0.brake
net spindle-revs               =>  spindle.0.revs
net spindle-at-speed           =>  spindle.0.at-speed
net spindle-vel-fb-rps         =>  spindle.0.speed-in
net spindle-index-enable      <=>  spindle.0.index-enable

# ---Setup spindle at speed signals---

sets spindle-at-speed true


#******************************
# connect miscellaneous signals
#******************************

#  ---HALUI signals---

net axis-select-x  halui.axis.x.select
net jog-x-pos      halui.axis.x.plus
net jog-x-neg      halui.axis.x.minus
net jog-x-analog   halui.axis.x.analog
net x-is-homed     halui.joint.0.is-homed
net axis-select-y  halui.axis.y.select
net jog-y-pos      halui.axis.y.plus
net jog-y-neg      halui.axis.y.minus
net jog-y-analog   halui.axis.y.analog
net y-is-homed     halui.joint.1.is-homed
net axis-select-z  halui.axis.z.select
net jog-z-pos      halui.axis.z.plus
net jog-z-neg      halui.axis.z.minus
net jog-z-analog   halui.axis.z.analog
net z-is-homed     halui.joint.2.is-homed
net axis-select-a  halui.axis.a.select
net jog-a-pos      halui.axis.a.plus
net jog-a-neg      halui.axis.a.minus
net jog-a-analog   halui.axis.a.analog
net a-is-homed     halui.joint.3.is-homed
net jog-selected-pos      halui.axis.selected.plus
net jog-selected-neg      halui.axis.selected.minus
net spindle-manual-cw     halui.spindle.0.forward
net spindle-manual-ccw    halui.spindle.0.reverse
net spindle-manual-stop   halui.spindle.0.stop
net machine-is-on         halui.machine.is-on
net jog-speed             halui.axis.jog-speed
net MDI-mode              halui.mode.is-mdi

#  ---coolant signals---

net coolant-mist      <=  iocontrol.0.coolant-mist
net coolant-flood     <=  iocontrol.0.coolant-flood

#  ---probe signal---

net probe-in     =>  motion.probe-input

#  ---motion control signals---

net in-position               <=  motion.in-position
net machine-is-enabled        <=  motion.motion-enabled

#  ---digital in / out signals---

#  ---estop signals---

net estop-out     <=  iocontrol.0.user-enable-out
net estop-out     =>  iocontrol.0.emc-enable-in

#  ---manual tool change signals---

net tool-change-request    <= iocontrol.0.tool-change
net tool-change-confirmed  => iocontrol.0.tool-changed
net tool-number            <= iocontrol.0.tool-prep-number

#  ---Use external manual tool change dialog---

loadusr -W hal_manualtoolchange
net tool-change-request    =>  hal_manualtoolchange.change
net tool-change-confirmed  <=  hal_manualtoolchange.changed
net tool-number            =>  hal_manualtoolchange.number

#  ---ignore tool prepare requests---
net tool-prepare-loopback   iocontrol.0.tool-prepare      =>  iocontrol.0.tool-prepared

 

Please Log in to join the conversation.

More
2 years 4 months ago #301979 by PCW
change:

sserial_port_0=0xxxxxxx

to:

sserial_port_0=000

sserial_port_0=0xxxxxxx  only enables one sserial channel
(the digital I/O section of the 7I77)

sserial_port_0=000 enables 3 channels: 0,1,2 = 7I77 digital, 7I77 analog,
and the 7I96S's sserial expansion channel. 
 

Please Log in to join the conversation.

More
2 years 4 months ago #301980 by programador
Thank you very much, now the analog variables have appeared!

Please Log in to join the conversation.

More
2 years 4 months ago #302861 by Hastrh2o
Hi,

I have the a similar issue but with one 5i25 and two 7i77. With Halshow, I see Parameters / hm2_5i25 / 0 / 7i77 / 0 / {0, 3, 4} (7i77 digital on P3, 7i77 digital on P2 and 7i77 analog on P2). I think I should have 0, 1, 3 and 4.

I work with a fresh install, linuxcnc 2.9.2
I used mseflash with 5i25_7i77x2.bit
The 5V is powered by the 5i25 and the leds are on (but I measure 4,7V  and 4,8V ) . Field power is 24V.
In the firmware tab of MesaCT, I see the Smart Serial channels 4, 5, 6 on P2, 1, 2, 3 on P3.
The config line generated by MesaCT (because I don't succeed in finding my two 7i77 I/O with PncConf, this may be related) is :
loadrt [HM2](DRIVER) config="num_encoders=12 sserial_port_0=00000000"
If I switch the cables, that's the same board wich remain without analog (so instead to be on P3 it's on P2)
If I disconnect the board on P2, I still don't see the 7i77 analog on P3.
If I disconnect all I/O cables on the 7i77 it's still the same.


Any idea to look at ?

Thanks

Please Log in to join the conversation.

More
2 years 4 months ago #302873 by PCW
Are you saying that one 7I77 never has analog
or that the 7I77 connected to  P3 connector 
never has analog?

Please Log in to join the conversation.

More
2 years 4 months ago #302875 by Hastrh2o
I say that one 7I77 never has analog

Please Log in to join the conversation.

More
2 years 4 months ago #302878 by PCW
So sounds like a bad 7I77
Does it have all 4 yellow LEDs illuminated?

Please Log in to join the conversation.

More
2 years 4 months ago #302879 by Hastrh2o

Please Log in to join the conversation.

More
2 years 4 months ago #302888 by PCW
So if both 7I77s are jumpered identically I would say the 7I77
with the analog section that does not work may have a bad  or
damaged pin on the FPGA interface that interferes with serial
communications.

Please Log in to join the conversation.

More
2 years 4 months ago #302933 by Hastrh2o
I swaped the two cards and I can now read Parameters / hm2_5i25 / 0 / 7i77 / 0 / {0, 1, 3} as expected.

I will order a new one.

Please Log in to join the conversation.