Hello

I am converting my Spindle to RS485 modbus to get one servo axis more.
My idea is to use HW COM port: ttyS0 and rs232 to 485 converter.

I have tested that RS485 converter works with VFD setup software.
Also I verified that baud rate is correct and it is in correct mode 19200, RTU and 8-N-1.

Attachment not found



Attachment not found



I Tested Linuxcnc with this USB to RS232 to verify that there is no HW problem.

ttyUSB0 is found:

Attachment not found



Here is Config for modbus:

Attachment not found



Attachment not found



It was trying to send something (indicated by TX led in usb to rs232 conveter), but no modbus connection was made.
I was using same setup usb to rs232 + rs232 to rs485 converter to test connection with VFd softaware and it works.

Any Idea what i am missing?
Clearly something in Linux or linuxcnc..

Please Log in to join the conversation.

More
6 years 9 months ago #155233 by Mike_Eitel
Have you tried RTS on?
RS485 needs switching of direction

Please Log in to join the conversation.

More
6 years 9 months ago #155234 by cmorley
Replied by cmorley on topic Modbus communication error
It's been awhile since I did classicladder modbus but ...

run linuxcnc in a terminal and set classicladder's modbus debug setting high.
that should show the raw commands being sent and received on classicladders's side.

Sometime changing the element offset, timeouts etc. also if you can try at a slower baud rate first might be helpful.

Chris

Please Log in to join the conversation.

More
6 years 9 months ago #155235 by jsskangas
OK

I am not expert in modbus so for me this does not tell much.

It outputs this:

Serial flush all!
INFO CLASSICLADDER- Modbus I/O module to send: Lgt=8 <- Slave address-1 Function code-4 Data-8 35 0 1 23 A4
INFO CLASSICLADDER- MODBUS Length we should receive=4 (+3)
Serial config...
Set RTS=1
Serial writing...
Writing done!
Set RTS=0
select() for serial reading...
Serial reading...
5 chars found
INFO CLASSICLADDER- Modbus I/O module received: Lgt=5 -> (Slave address-1 - Function code-84 ) 1 82 C0
ERROR CLASSICLADDER- MODBUS-EXCEPTION RECEIVED:84 (Excep=1)
ERROR CLASSICLADDER- MODBUS-INCORRECT RESPONSE RECEIVED FROM SLAVE!!!
Serial flush all!
INFO CLASSICLADDER- Modbus I/O module to send: Lgt=8 <- Slave address-1 Function code-4 Data-8 35 0 1 23 A4
INFO CLASSICLADDER- MODBUS Length we should receive=4 (+3)
Serial config...
Set RTS=1
Serial writing...
Writing done!
Set RTS=0
select() for serial reading...
Serial reading...
5 chars found
INFO CLASSICLADDER- Modbus I/O module received: Lgt=5 -> (Slave address-1 - Function code-84 ) 1 82 C0
ERROR CLASSICLADDER- MODBUS-EXCEPTION RECEIVED:84 (Excep=1)
ERROR CLASSICLADDER- MODBUS-INCORRECT RESPONSE RECEIVED FROM SLAVE!!!
Serial flush all!

Please Log in to join the conversation.

More
6 years 9 months ago #155239 by cmorley
Replied by cmorley on topic Modbus communication error
Again been awhile but...

You are getting a response from the VDF.
I believe it's telling you the function (4 - read registers) is not available.
I don't see from to snippet if function 6/16 is working.
Do you have info on the modbus commands the VFD uses ?

Chris

Please Log in to join the conversation.

More
6 years 9 months ago #155240 by jsskangas
Hello

If you look at my first post, second picture.
There is there is two messages i tried trough ModBus.
First one is read register 2100, this went OK.
Then write register 2001, again ok.
and you can see answer from VFD to those requests.


I did look a manual and all requester and written register exists.

Please Log in to join the conversation.

More
6 years 9 months ago #155241 by cmorley
Replied by cmorley on topic Modbus communication error
Looks from your setup software that the function should be 3 (read hold registers)not 4 ....

Please Log in to join the conversation.

More
6 years 9 months ago #155244 by jsskangas
I did try 3 (read hold registers) and it did not make any difference:

Serial reading...
5 chars found
INFO CLASSICLADDER- Modbus I/O module received: Lgt=5 -> (Slave address-1 - Function code-83 ) 2 C0 F1
ERROR CLASSICLADDER- MODBUS-EXCEPTION RECEIVED:83 (Excep=2)
ERROR CLASSICLADDER- MODBUS-INCORRECT RESPONSE RECEIVED FROM SLAVE!!!
Serial flush all!
INFO CLASSICLADDER- Modbus I/O module to send: Lgt=8 <- Slave address-1 Function code-3 Data-8 34 0 1 C7 A4
INFO CLASSICLADDER- MODBUS Length we should receive=4 (+3)
Serial config...
Serial writing...
Writing done!
select() for serial reading...
Serial reading...
5 chars found
INFO CLASSICLADDER- Modbus I/O module received: Lgt=5 -> (Slave address-1 - Function code-83 ) 2 C0 F1
ERROR CLASSICLADDER- MODBUS-EXCEPTION RECEIVED:83 (Excep=2)
ERROR CLASSICLADDER- MODBUS-INCORRECT RESPONSE RECEIVED FROM SLAVE!!!
Serial flush all!
INFO CLASSICLADDER- Modbus I/O module to send: Lgt=8 <- Slave address-1 Function code-3 Data-8 34 0 1 C7 A4
INFO CLASSICLADDER- MODBUS Length we should receive=4 (+3)
Serial config...
Serial writing...
Writing done!
select() for serial reading...
Serial reading...
5 chars found
INFO CLASSICLADDER- Modbus I/O module received: Lgt=5 -> (Slave address-1 - Function code-83 ) 2 C0 F1
ERROR CLASSICLADDER- MODBUS-EXCEPTION RECEIVED:83 (Excep=2)
ERROR CLASSICLADDER- MODBUS-INCORRECT RESPONSE RECEIVED FROM SLAVE!!!
Serial flush all!
INFO CLASSICLADDER- Modbus I/O module to send: Lgt=8 <- Slave address-1 Function code-3 Data-8 34 0 1 C7 A4
INFO CLASSICLADDER- MODBUS Length we should receive=4 (+3)
Serial config...
Serial writing...
Writing done!
select() for serial reading...
Serial reading...
5 chars found
INFO CLASSICLADDER- Modbus I/O module received: Lgt=5 -> (Slave address-1 - Function code-83 ) 2 C0 F1
ERROR CLASSICLADDER- MODBUS-EXCEPTION RECEIVED:83 (Excep=2)
ERROR CLASSICLADDER- MODBUS-INCORRECT RESPONSE RECEIVED FROM SLAVE!!!
Serial flush all!

Please Log in to join the conversation.

More
6 years 9 months ago #155245 by cmorley
Replied by cmorley on topic Modbus communication error
It did make a difference - the exception code is now 2 - illegal data address

So the function (3) is corrected but seems the address is wrong
is address 2101 legal? in your test you used 2100

Please Log in to join the conversation.

More
6 years 9 months ago #155246 by cmorley
Replied by cmorley on topic Modbus communication error
ahh I bet you did set 2100 in classicladder - try setting 'modbus element offset' to 0

Chris