Guys, I have a question about Ladder. I'm using the 7i76 + 7i84 boards, I'm programming and I used all the I/O from the 7i76 and almost all from the 7i84, my question is: do I make two classicladder one for each board? Or do I only do one and how do I make the identification in the HAL file? What is the correct procedure to do this?
Thank you very much
Ingo
Thank you very much
Ingo
Please Log in to join the conversation.
5 years 4 months ago #212634
by cmorley
Replied by cmorley on topic Assembling Classicladder
There can only be one instance of classicladder.
I don't understand the problem you are trying to work around.
Can you describe the problem more?
Chris
I don't understand the problem you are trying to work around.
Can you describe the problem more?
Chris
Please Log in to join the conversation.
5 years 4 months ago #212638
by Ingo
Replied by Ingo on topic Assembling Classicladder
Hi Chris,
I'm still learning about LinuxCNC and it's the first time I've used two boards, sorry if it's so obvious…, but I needed a daughter board because I have a lot of I/O. I want to know how do I point the I/O on the 7i84. Because for example it has the same number “names” inputs and outputs of the two boards, how do I differentiate the same pin on the classicladder? Example an input in-05 on board 7i76 and I have the same input in-05 on 7i84. Will I make the logic in the ladder of the I/O related to the daughter board as I write it in ClassicLadder and in HAL so there is no conflict?
I'm still learning about LinuxCNC and it's the first time I've used two boards, sorry if it's so obvious…, but I needed a daughter board because I have a lot of I/O. I want to know how do I point the I/O on the 7i84. Because for example it has the same number “names” inputs and outputs of the two boards, how do I differentiate the same pin on the classicladder? Example an input in-05 on board 7i76 and I have the same input in-05 on 7i84. Will I make the logic in the ladder of the I/O related to the daughter board as I write it in ClassicLadder and in HAL so there is no conflict?
Please Log in to join the conversation.
- tommylight
-
- Offline
- Administrator
-
Less
More
- Posts: 22010
- Thank you received: 3
5 years 4 months ago #212655
by tommylight
Notice the different addresses after the card numbers, 7i77 has an address of 0.0., 7i71 is at 1.4. and 7i70 is at 1.5. .
The same goes for 7i84, wire it, power it on, open LinuxCNC and use the "Show hal configuration" from the "machine" menu to see the address and pin names.
Replied by tommylight on topic Assembling Classicladder
Code:
# --- MACHINE-IS-ENABLED ---
net machine-is-enabled hm2_7i92.0.7i77.0.0.output-02
Code:
net Carousel-up hm2_7i92.0.7i71.1.4.output-20
Code:
net Carousel-is-up hm2_7i92.0.7i70.1.5.input-00
The same goes for 7i84, wire it, power it on, open LinuxCNC and use the "Show hal configuration" from the "machine" menu to see the address and pin names.
Please Log in to join the conversation.
5 years 4 months ago #212661
by BigJohnT
Replied by BigJohnT on topic Assembling Classicladder
With your configuration running open a terminal and issue the following command.
The > is redirect and will send the output from the command to the text file so you can copy and paste pin names easy. You can also get the signals and parameters in the same way with
JT
Code:
halcmd show pin > pins.txt
The > is redirect and will send the output from the command to the text file so you can copy and paste pin names easy. You can also get the signals and parameters in the same way with
Code:
halcmd show sig > signals.txt
halcmd show param > parameters.txt
JT
Please Log in to join the conversation.
5 years 4 months ago #212666
by bevins
Replied by bevins on topic Assembling Classicladder
Classicladder can be configured from different boards no problem. It distinguishes the difference from the pins.
Something like this:
Check the actual pins like BigJohnT showed you.
Something like this:
Code:
net arm-up classicladder.0.in-00 hm2_7i92.0.7i76.0.0.input-01
net arm-down classicladder.0.in-01 hm2_7i92.0.7i84.1.2.input-01
Check the actual pins like BigJohnT showed you.
Please Log in to join the conversation.
5 years 4 months ago #212702
by Ingo
Replied by Ingo on topic Assembling Classicladder
So, today I was doing Hal according to the tips you gave me, I've attached it for you to see what you think, but I had some problems. First the number of I/O in the classicladder was insufficient, I added I80 and Q48, but I found it very strange when I open the classicladder in symbol it only shows maximum I47 and Q31 why is it? There is also a problem regarding “Torre_CW” and “Torre_CCW” on the 7i84 daughter board, both in Oct-03 and Oct-04, as well as in In-11 and In-12.
Please Log in to join the conversation.
5 years 4 months ago #212705
by BigJohnT
Replied by BigJohnT on topic Assembling Classicladder
You might have exceeded the default number of variables. You need to load more in your hal file loadrt line.
linuxcnc.org/docs/2.8/html/ladder/classi...dder.html#_variables
JT
linuxcnc.org/docs/2.8/html/ladder/classi...dder.html#_variables
JT
Please Log in to join the conversation.
5 years 4 months ago #212764
by Ingo
Replied by Ingo on topic Assembling Classicladder
Hello JT,
I loaded 80 in the inputs (numPhysInputs=80) in the Hal file plus maximum accepted is 50, the problem is that I have more inputs than that (52) and they are insufficient…. I read the link you gave me I went to Pncconf and edited it in the ladder the same thing. Do you have any idea?
I loaded 80 in the inputs (numPhysInputs=80) in the Hal file plus maximum accepted is 50, the problem is that I have more inputs than that (52) and they are insufficient…. I read the link you gave me I went to Pncconf and edited it in the ladder the same thing. Do you have any idea?
Please Log in to join the conversation.
5 years 4 months ago #212765
by Aciera
Replied by Aciera on topic Assembling Classicladder
I also have more than 50 inputs and even more outputs in classic ladder. If I remember correctly it's the graphical variable interface in Classicladder (the one in your screen shot) that somehow doesn't show all the available inputs and outputs. I had to add the %Ixx and the %Qxx in the .clp file directly (ie. the variable names) then you can use those in your ladder schematics. But I think you have to type the names you defined in the .clp manually as they don't show up in the variable browser in the gui.
So the signals do work but you cannot see them in the list in the gui.
So the signals do work but you cannot see them in the list in the gui.
Warning: Spoiler!
_FILES_CLASSICLADDER
_FILE-rung_0.csv
#VER=2.0
#LABEL=drives-en
#COMMENT=Enable stepper drives and fan
#PREVRUNG=0
#NEXTRUNG=2
9-0-70/0 , 2-0-50/45 , 9-0-50/0 , 2-0-50/46 , 9-0-50/0 , 2-0-50/47 , 9-0-50/0 , 2-0-50/43 , 9-0-0/0 , 50-0-60/40
1-0-50/0 , 9-0-50/0 , 2-0-50/76 , 9-0-0/0 , 2-0-50/75 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 50-0-60/41
9-0-50/0 , 1-0-60/40 , 9-0-0/0 , 1-0-50/42 , 9-0-50/0 , 1-0-50/50 , 9-0-50/0 , 99-0-0/0 , 13-0-0/0 , 50-0-60/22
0-0-0/27 , 0-0-0/0 , 0-0-50/3 , 0-0-0/0 , 0-0-50/5 , 0-0-0/5 , 0-1-50/12 , 99-0-0/0 , 99-0-0/0 , 0-0-60/37
0-0-50/12 , 0-0-0/0 , 0-0-50/3 , 0-0-0/0 , 0-0-50/0 , 0-0-0/0 , 9-1-0/0 , 9-0-0/0 , 9-0-0/0 , 50-0-60/43
0-0-50/0 , 0-0-0/27 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 9-1-0/0 , 9-0-0/0 , 9-0-0/0 , 50-0-60/36
_/FILE-rung_0.csv
_FILE-modbusioconf.csv
#VER=1.0
_/FILE-modbusioconf.csv
_FILE-monostables.csv
1,0
1,0
1,0
1,0
1,0
1,0
1,0
1,0
1,0
1,0
_/FILE-monostables.csv
_FILE-rung_4.csv
#VER=2.0
#LABEL=wkw
#COMMENT=Werkzeugwechsler
#PREVRUNG=7
#NEXTRUNG=6
0-0-50/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
2-0-50/44 , 9-0-0/0 , 1-0-50/60 , 9-0-0/0 , 9-0-0/0 , 1-0-50/36 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 50-0-60/31
0-0-0/0 , 0-0-0/0 , 0-0-50/38 , 0-0-0/0 , 9-1-0/0 , 1-0-50/38 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 50-0-60/32
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 9-1-0/0 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 50-0-60/12
0-0-50/44 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 9-1-0/0 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 50-0-60/15
_/FILE-rung_4.csv
_FILE-counters.csv
0
0
0
0
0
0
0
0
0
0
_/FILE-counters.csv
_FILE-rung_7.csv
#VER=2.0
#LABEL=
#COMMENT=Spindle Run Forward
#PREVRUNG=5
#NEXTRUNG=4
1-0-60/35 , 0-0-0/0 , 0-0-50/64 , 0-0-50/0 , 0-0-50/0 , 0-0-0/0 , 9-0-0/0 , 2-0-50/53 , 9-0-0/0 , 50-0-60/53
0-0-0/0 , 9-1-0/0 , 9-0-50/0 , 1-0-50/7 , 9-0-50/0 , 9-0-0/0 , 0-1-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
0-0-0/0 , 0-1-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
0-0-0/0 , 0-1-0/0 , 0-0-50/65 , 0-0-0/0 , 0-0-50/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
0-0-0/0 , 9-1-0/0 , 9-0-0/0 , 1-0-50/5 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 2-0-50/53 , 9-0-0/0 , 50-0-60/54
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
_/FILE-rung_7.csv
_FILE-sequential.csv
#VER=1.0
S1,0,1701669204,114,0,0
S8,0,1701669204,114,0,0
S15,79,1701669204,114,0,0
S50,69,1816535154,97,103,32
S57,69,1816535154,97,103,32
S64,69,1816535154,97,103,32
S71,69,1816535154,97,103,32
S78,69,1816535154,97,103,32
_/FILE-sequential.csv
_FILE-rung_8.csv
#VER=2.0
#LABEL=prg-com
#COMMENT=Programm Run-Pause-Stop
#PREVRUNG=6
#NEXTRUNG=9
1-0-50/53 , 1-0-60/43 , 9-0-50/0 , 1-0-50/12 , 2-0-50/75 , 9-0-0/0 , 9-0-0/0 , 2-0-50/76 , 9-0-0/0 , 50-0-60/73
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 1-1-50/13 , 9-0-50/0 , 99-0-0/0 , 13-0-0/3 , 9-0-50/0 , 1-0-50/76 , 50-0-60/71
0-0-0/0 , 0-0-0/0 , 0-0-50/13 , 0-1-0/0 , 0-0-50/13 , 99-0-0/0 , 99-0-50/3 , 0-1-50/0 , 0-0-0/0 , 0-0-60/71
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-1-0/0 , 0-0-50/13 , 0-0-0/0 , 0-0-0/0 , 9-1-50/0 , 1-0-50/75 , 50-0-60/70
0-0-0/0 , 0-0-0/0 , 0-0-50/14 , 9-1-0/0 , 1-0-50/14 , 9-0-0/0 , 9-0-0/0 , 1-0-50/75 , 9-0-0/0 , 50-0-60/72
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-50/76 , 0-0-0/0 , 9-1-0/0 , 1-0-50/76 , 0-1-0/0 , 0-0-0/0
_/FILE-rung_8.csv
_FILE-rung_5.csv
#VER=2.0
#LABEL=Spdl-En
#COMMENT=Spindle enable
#PREVRUNG=3
#NEXTRUNG=7
1-0-50/62 , 9-0-0/0 , 1-0-50/44 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 9-0-50/0 , 50-0-60/51
1-0-60/40 , 9-0-0/0 , 1-0-50/44 , 1-0-50/50 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 50-0-60/35
0-0-0/0 , 0-1-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-50/7 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-60/53
0-0-0/0 , 1-1-50/50 , 9-0-50/0 , 2-0-50/62 , 9-0-0/0 , 0-0-50/5 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-60/54
0-0-0/0 , 0-0-0/0 , 9-1-50/0 , 2-0-50/44 , 9-0-0/0 , 9-1-50/0 , 2-0-50/53 , 9-0-0/0 , 9-0-0/0 , 50-0-60/55
0-0-0/0 , 0-0-0/0 , 9-1-50/0 , 1-0-50/6 , 9-0-0/0 , 0-1-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
_/FILE-rung_5.csv
_FILE-rung_3.csv
#VER=2.0
#LABEL=ang-jog-s
#COMMENT=Switch to angular jog speed
#PREVRUNG=1
#NEXTRUNG=5
0-0-50/9 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
2-0-50/19 , 2-0-50/17 , 9-0-50/0 , 2-0-50/11 , 2-0-50/22 , 9-0-0/0 , 2-0-50/10 , 2-0-50/21 , 9-0-0/0 , 50-0-0/1
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 1-0-50/9 , 0-0-0/0 , 0-0-0/0
1-0-0/1 , 9-0-0/0 , 1-0-50/51 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 1-1-50/20 , 9-1-0/0 , 50-0-60/47
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
_/FILE-rung_3.csv
_FILE-sections.csv
#VER=1.0
#NAME000=Prog1
000,0,-1,0,11,0
_/FILE-sections.csv
_FILE-rung_2.csv
#VER=2.0
#LABEL=home-btn
#COMMENT=home with panel button
#PREVRUNG=0
#NEXTRUNG=1
1-0-60/43 , 9-0-0/0 , 9-0-0/0 , 1-0-50/54 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 50-0-60/5
0-0-50/51 , 0-0-0/0 , 0-0-50/4 , 0-0-0/0 , 9-1-0/0 , 9-0-0/0 , 9-0-0/0 , 1-0-50/4 , 9-0-0/0 , 50-0-60/45
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
_/FILE-rung_2.csv
_FILE-timers.csv
1,0
1,0
1,0
1,0
1,0
1,0
1,0
1,0
1,0
1,0
_/FILE-timers.csv
_FILE-rung_1.csv
#VER=2.0
#LABEL=a-hme-man
#COMMENT=home A with Ao button
#PREVRUNG=2
#NEXTRUNG=3
1-0-50/54 , 2-0-50/59 , 9-0-0/0 , 1-0-50/58 , 9-0-0/0 , 99-0-0/0 , 13-0-0/6 , 9-0-0/0 , 9-0-0/0 , 50-0-0/0
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 99-0-0/0 , 99-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-50/0 , 0-0-0/0 , 0-0-0/2 , 0-0-0/0 , 0-0-0/0 , 0-0-60/46
2-0-0/0 , 9-0-0/0 , 9-0-0/0 , 99-0-50/0 , 13-0-0/2 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 50-0-60/46
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 99-0-0/0 , 99-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
_/FILE-rung_1.csv
_FILE-arithmetic_expressions.csv
#VER=2.0
_/FILE-arithmetic_expressions.csv
_FILE-symbols.csv
#VER=1.0
%I0,btn-usr1,
%I1,btn-usr2,
%I2,btn-m7,
%I3,btn-m8,
%I4,btn-home, l
%I5,btn-m4,
%I6,btn-m5,
%I7,btn-m3,
%I8,btn-y0,
%I9,btn-a-,
%I10,btn-z+,
%I11,btn-y+,
%I12,btn-prgSt,
%I13,btn-prgPs,
%I14,btn-prgCl,
%I15,btn-x0,
%I16,btn-z0,
%I17,btn-x-,
%I18,btn-4achs,
%I19,btn-x+,
%I20,btn-a+,
%I21,btn-z-,
%I22,btn-y-,
%I23,btn-a0,
%I36,btn-wzOut,
%I37,btn-usr3,
%I38,btn-wzIn,
%I39,btn-g91,
%I40,btn-usr5,
%I41,btn-usr4,
%I42,btn-drsEn,
%I43,drv-fault,
%I44,btn-splEn,
%I45,Err-Varm,
%I46,Err-Hspdl,
%I47,Err-Estp,
%I50,Mach-isOn,
%I51,mode=man,
%I52,mode=mdi,
%I53,mode=auto,
%I54,mode=jnt,
%I57,a-homed,
%I58,a-hmng,
%I59,a-prsnt,
%I60,spl-atRst,
%I62,spl-emcEn,
%I63,spl-emcDr,
%I70,m7-isOn,
%I71,m8-isOn,
%I75,led-prgRn,
%I76,led-prgPs,
%Q0,Q0,
%Q1,Q1,
%Q2,Q2,
%Q3,Q3,
%Q4,Q4,
%Q5,led-home,
%Q6,led-m4,
%Q7,led-m3,
%Q8,led-m8,
%Q9,led-m7,
%Q10,led-usr4,
%Q11,led-usr5,
%Q12,led-wzout,
%Q13,led-usr3,
%Q14,led-g91,
%Q15,led-wzin,
%Q16,led-usr1,
%Q17,led-usr2,
%Q18,Q18,
%Q19,led-prgps,
%Q20,led-prgst,
%Q21,led-4achs,
%Q22,rly-fan,
%Q23,Q23,
%Q24,Q24,
%Q25,Q25,
%Q26,Q26,
%Q27,Q27,
%Q28,Q28,
%Q29,Q29,
%Q30,Q30,
%Q31,rly-wzRls,
%Q32,rly-wzLck,
%Q33,rly-dose,
%Q34,Q34,
%Q35,led-splEn,
%Q36,led-drsEn,
%Q37,Q37,
%Q38,Q38,
%Q39,Q39,
%Q40,emc-en,
%Q41,btn-mach,
%Q43,drvs-en,
%Q45,home-all,
%Q46,home-aMan,
%Q47,jog-aSpd,
%Q51,spl-drv,
%Q53,m3En,
%Q54,m4En,
%Q55,m5En,
%Q60,m7-On,
%Q61,m7-Off,
%Q62,m8-On,
%Q63,m8-Off,
%Q70,prg-ps,
%Q71,prg-rsm,
%Q72,prg-stp,
%Q73,prg-run,
%Q80,zero-x,
%Q81,zero-y,
%Q82,zero-z,
%Q83,zero-a,
%Q85,btn-g91,
%Q87,btn-mode,
%B0,B0,
%B1,B1,
%B2,B2,
%B3,B3,
%B4,B4,
%B5,B5,
%B6,B6,
%B7,B7,
%B8,B8,
%B9,B9,
%B10,B10,
%B11,B11,
%B12,B12,
%B13,B13,
%B14,B14,
%B15,B15,
%B16,B16,
%B17,B17,
%B18,B18,
%B19,B19,
%B20,B20,
%B21,B21,
%B22,B22,
%B23,B23,
%B24,B24,
%B25,B25,
%B26,B26,
%B27,B27,
%B28,B28,
%B29,B29,
%B30,B30,
%B31,B31,
%B32,B32,
%B33,B33,
%B34,B34,
%B35,B35,
%B36,B36,
%B37,B37,
%B38,B38,
%B39,B39,
%W0,%W0,
%W1,%W1,
%W2,%W2,
%W3,%W3,
%W4,%W4,
%W5,%W5,
%W6,%W6,
%W7,%W7,
%W8,%W8,
%W9,%W9,
%W10,%W10,
%W11,%W11,
%W12,%W12,
%W13,%W13,
%W14,%W14,
%W15,%W15,
%W16,%W16,
%W17,%W17,
%W18,%W18,
%W19,%W19,
%IW0,%IW0,
%IW1,%IW1,
%IW2,%IW2,
%IW3,%IW3,
%IW4,%IW4,
%IW5,%IW5,
%IW6,%IW6,
%IW7,%IW7,
%IW8,%IW8,
%IW9,%IW9,
%QW0,%QW0,
%QW1,%QW1,
%QW2,%QW2,
%QW3,%QW3,
%QW4,%QW4,
%QW5,%QW5,
%QW6,%QW6,
%QW7,%QW7,
%QW8,%QW8,
%QW9,%QW9,
%IF0,%IF0,
%IF1,%IF1,
%IF2,%IF2,
_/FILE-symbols.csv
_FILE-rung_11.csv
#VER=2.0
#LABEL=mdi-hnd
#COMMENT=toggle mdi and hand modus
#PREVRUNG=10
#NEXTRUNG=-1
2-0-50/53 , 9-0-0/0 , 1-0-50/37 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 50-0-60/87
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
_/FILE-rung_11.csv
_FILE-rung_9.csv
#VER=2.0
#LABEL=zero-axis
#COMMENT=Zero X,Y,Z,A
#PREVRUNG=8
#NEXTRUNG=10
2-0-50/53 , 9-0-0/0 , 1-0-50/50 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 1-0-50/15 , 9-0-0/0 , 9-0-0/0 , 50-0-60/80
0-0-0/0 , 0-0-0/0 , 0-0-50/8 , 0-1-0/0 , 0-0-0/0 , 9-1-0/0 , 1-0-50/8 , 9-0-0/0 , 9-0-0/0 , 50-0-60/81
0-0-0/0 , 0-0-0/0 , 0-0-50/16 , 0-1-0/0 , 0-0-0/0 , 9-1-0/0 , 1-0-50/16 , 9-0-0/0 , 9-0-0/0 , 50-0-60/82
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-1-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
0-0-0/0 , 0-0-0/0 , 0-0-50/23 , 9-1-0/0 , 1-0-50/57 , 9-0-0/0 , 1-0-50/23 , 9-0-0/0 , 9-0-0/0 , 50-0-60/83
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
_/FILE-rung_9.csv
_FILE-rung_6.csv
#VER=2.0
#LABEL=wkw
#COMMENT=Werkzeugwechsler
#PREVRUNG=4
#NEXTRUNG=8
0-0-60/40 , 0-0-0/0 , 0-0-50/70 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-60/60
1-0-60/40 , 1-0-50/50 , 1-0-50/2 , 9-0-0/0 , 99-0-50/2 , 13-0-50/4 , 9-0-0/0 , 9-0-50/0 , 2-0-50/70 , 50-0-60/60
0-0-0/0 , 0-0-0/0 , 0-1-50/70 , 0-0-0/0 , 99-0-50/70 , 99-0-50/70 , 0-0-0/0 , 9-1-50/0 , 1-0-50/70 , 50-0-60/61
0-0-50/71 , 0-0-0/0 , 0-1-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
0-0-0/0 , 0-0-50/0 , 1-1-50/3 , 9-0-0/0 , 99-0-50/3 , 13-0-50/5 , 9-0-0/0 , 9-0-0/0 , 2-0-50/71 , 50-0-60/62
0-0-0/0 , 0-0-0/0 , 0-0-50/71 , 0-0-0/0 , 99-0-50/71 , 99-0-50/71 , 0-0-0/0 , 9-1-0/0 , 1-0-50/71 , 50-0-60/63
_/FILE-rung_6.csv
_FILE-rung_10.csv
#VER=2.0
#LABEL=G90-G91
#COMMENT=Panel button G90 <-> G91
#PREVRUNG=9
#NEXTRUNG=11
1-0-50/52 , 9-0-0/0 , 1-0-50/39 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 50-0-60/85
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
_/FILE-rung_10.csv
_FILE-ioconf.csv
#VER=1.0
_/FILE-ioconf.csv
_FILE-com_params.txt
MODBUS_MASTER_SERIAL_PORT=
MODBUS_MASTER_SERIAL_SPEED=9600
MODBUS_MASTER_SERIAL_DATABITS=8
MODBUS_MASTER_SERIAL_STOPBITS=1
MODBUS_MASTER_SERIAL_PARITY=0
MODBUS_ELEMENT_OFFSET=0
MODBUS_MASTER_SERIAL_USE_RTS_TO_SEND=0
MODBUS_MASTER_TIME_INTER_FRAME=100
MODBUS_MASTER_TIME_OUT_RECEIPT=500
MODBUS_MASTER_TIME_AFTER_TRANSMIT=0
MODBUS_DEBUG_LEVEL=0
MODBUS_MAP_COIL_READ=0
MODBUS_MAP_COIL_WRITE=0
MODBUS_MAP_INPUT=0
MODBUS_MAP_HOLDING=0
MODBUS_MAP_REGISTER_READ=0
MODBUS_MAP_REGISTER_WRITE=0
_/FILE-com_params.txt
_FILE-general.txt
PERIODIC_REFRESH=1
SIZE_NBR_RUNGS=20
SIZE_NBR_BITS=20
SIZE_NBR_WORDS=20
SIZE_NBR_TIMERS=10
SIZE_NBR_MONOSTABLES=10
SIZE_NBR_COUNTERS=10
SIZE_NBR_TIMERS_IEC=10
SIZE_NBR_PHYS_INPUTS=90
SIZE_NBR_PHYS_OUTPUTS=90
SIZE_NBR_ARITHM_EXPR=100
SIZE_NBR_SECTIONS=10
SIZE_NBR_SYMBOLS=200
_/FILE-general.txt
_FILE-timers_iec.csv
1,30,1
2,5,1
2,5,2
2,1,2
2,1,2
2,1,2
2,5,2
2,1,2
1,0,0
1,0,0
_/FILE-timers_iec.csv
_/FILES_CLASSICLADDER
_FILE-rung_0.csv
#VER=2.0
#LABEL=drives-en
#COMMENT=Enable stepper drives and fan
#PREVRUNG=0
#NEXTRUNG=2
9-0-70/0 , 2-0-50/45 , 9-0-50/0 , 2-0-50/46 , 9-0-50/0 , 2-0-50/47 , 9-0-50/0 , 2-0-50/43 , 9-0-0/0 , 50-0-60/40
1-0-50/0 , 9-0-50/0 , 2-0-50/76 , 9-0-0/0 , 2-0-50/75 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 50-0-60/41
9-0-50/0 , 1-0-60/40 , 9-0-0/0 , 1-0-50/42 , 9-0-50/0 , 1-0-50/50 , 9-0-50/0 , 99-0-0/0 , 13-0-0/0 , 50-0-60/22
0-0-0/27 , 0-0-0/0 , 0-0-50/3 , 0-0-0/0 , 0-0-50/5 , 0-0-0/5 , 0-1-50/12 , 99-0-0/0 , 99-0-0/0 , 0-0-60/37
0-0-50/12 , 0-0-0/0 , 0-0-50/3 , 0-0-0/0 , 0-0-50/0 , 0-0-0/0 , 9-1-0/0 , 9-0-0/0 , 9-0-0/0 , 50-0-60/43
0-0-50/0 , 0-0-0/27 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 9-1-0/0 , 9-0-0/0 , 9-0-0/0 , 50-0-60/36
_/FILE-rung_0.csv
_FILE-modbusioconf.csv
#VER=1.0
_/FILE-modbusioconf.csv
_FILE-monostables.csv
1,0
1,0
1,0
1,0
1,0
1,0
1,0
1,0
1,0
1,0
_/FILE-monostables.csv
_FILE-rung_4.csv
#VER=2.0
#LABEL=wkw
#COMMENT=Werkzeugwechsler
#PREVRUNG=7
#NEXTRUNG=6
0-0-50/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
2-0-50/44 , 9-0-0/0 , 1-0-50/60 , 9-0-0/0 , 9-0-0/0 , 1-0-50/36 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 50-0-60/31
0-0-0/0 , 0-0-0/0 , 0-0-50/38 , 0-0-0/0 , 9-1-0/0 , 1-0-50/38 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 50-0-60/32
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 9-1-0/0 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 50-0-60/12
0-0-50/44 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 9-1-0/0 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 50-0-60/15
_/FILE-rung_4.csv
_FILE-counters.csv
0
0
0
0
0
0
0
0
0
0
_/FILE-counters.csv
_FILE-rung_7.csv
#VER=2.0
#LABEL=
#COMMENT=Spindle Run Forward
#PREVRUNG=5
#NEXTRUNG=4
1-0-60/35 , 0-0-0/0 , 0-0-50/64 , 0-0-50/0 , 0-0-50/0 , 0-0-0/0 , 9-0-0/0 , 2-0-50/53 , 9-0-0/0 , 50-0-60/53
0-0-0/0 , 9-1-0/0 , 9-0-50/0 , 1-0-50/7 , 9-0-50/0 , 9-0-0/0 , 0-1-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
0-0-0/0 , 0-1-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
0-0-0/0 , 0-1-0/0 , 0-0-50/65 , 0-0-0/0 , 0-0-50/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
0-0-0/0 , 9-1-0/0 , 9-0-0/0 , 1-0-50/5 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 2-0-50/53 , 9-0-0/0 , 50-0-60/54
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
_/FILE-rung_7.csv
_FILE-sequential.csv
#VER=1.0
S1,0,1701669204,114,0,0
S8,0,1701669204,114,0,0
S15,79,1701669204,114,0,0
S50,69,1816535154,97,103,32
S57,69,1816535154,97,103,32
S64,69,1816535154,97,103,32
S71,69,1816535154,97,103,32
S78,69,1816535154,97,103,32
_/FILE-sequential.csv
_FILE-rung_8.csv
#VER=2.0
#LABEL=prg-com
#COMMENT=Programm Run-Pause-Stop
#PREVRUNG=6
#NEXTRUNG=9
1-0-50/53 , 1-0-60/43 , 9-0-50/0 , 1-0-50/12 , 2-0-50/75 , 9-0-0/0 , 9-0-0/0 , 2-0-50/76 , 9-0-0/0 , 50-0-60/73
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 1-1-50/13 , 9-0-50/0 , 99-0-0/0 , 13-0-0/3 , 9-0-50/0 , 1-0-50/76 , 50-0-60/71
0-0-0/0 , 0-0-0/0 , 0-0-50/13 , 0-1-0/0 , 0-0-50/13 , 99-0-0/0 , 99-0-50/3 , 0-1-50/0 , 0-0-0/0 , 0-0-60/71
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-1-0/0 , 0-0-50/13 , 0-0-0/0 , 0-0-0/0 , 9-1-50/0 , 1-0-50/75 , 50-0-60/70
0-0-0/0 , 0-0-0/0 , 0-0-50/14 , 9-1-0/0 , 1-0-50/14 , 9-0-0/0 , 9-0-0/0 , 1-0-50/75 , 9-0-0/0 , 50-0-60/72
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-50/76 , 0-0-0/0 , 9-1-0/0 , 1-0-50/76 , 0-1-0/0 , 0-0-0/0
_/FILE-rung_8.csv
_FILE-rung_5.csv
#VER=2.0
#LABEL=Spdl-En
#COMMENT=Spindle enable
#PREVRUNG=3
#NEXTRUNG=7
1-0-50/62 , 9-0-0/0 , 1-0-50/44 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 9-0-50/0 , 50-0-60/51
1-0-60/40 , 9-0-0/0 , 1-0-50/44 , 1-0-50/50 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 50-0-60/35
0-0-0/0 , 0-1-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-50/7 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-60/53
0-0-0/0 , 1-1-50/50 , 9-0-50/0 , 2-0-50/62 , 9-0-0/0 , 0-0-50/5 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-60/54
0-0-0/0 , 0-0-0/0 , 9-1-50/0 , 2-0-50/44 , 9-0-0/0 , 9-1-50/0 , 2-0-50/53 , 9-0-0/0 , 9-0-0/0 , 50-0-60/55
0-0-0/0 , 0-0-0/0 , 9-1-50/0 , 1-0-50/6 , 9-0-0/0 , 0-1-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
_/FILE-rung_5.csv
_FILE-rung_3.csv
#VER=2.0
#LABEL=ang-jog-s
#COMMENT=Switch to angular jog speed
#PREVRUNG=1
#NEXTRUNG=5
0-0-50/9 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
2-0-50/19 , 2-0-50/17 , 9-0-50/0 , 2-0-50/11 , 2-0-50/22 , 9-0-0/0 , 2-0-50/10 , 2-0-50/21 , 9-0-0/0 , 50-0-0/1
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 1-0-50/9 , 0-0-0/0 , 0-0-0/0
1-0-0/1 , 9-0-0/0 , 1-0-50/51 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 1-1-50/20 , 9-1-0/0 , 50-0-60/47
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
_/FILE-rung_3.csv
_FILE-sections.csv
#VER=1.0
#NAME000=Prog1
000,0,-1,0,11,0
_/FILE-sections.csv
_FILE-rung_2.csv
#VER=2.0
#LABEL=home-btn
#COMMENT=home with panel button
#PREVRUNG=0
#NEXTRUNG=1
1-0-60/43 , 9-0-0/0 , 9-0-0/0 , 1-0-50/54 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 50-0-60/5
0-0-50/51 , 0-0-0/0 , 0-0-50/4 , 0-0-0/0 , 9-1-0/0 , 9-0-0/0 , 9-0-0/0 , 1-0-50/4 , 9-0-0/0 , 50-0-60/45
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
_/FILE-rung_2.csv
_FILE-timers.csv
1,0
1,0
1,0
1,0
1,0
1,0
1,0
1,0
1,0
1,0
_/FILE-timers.csv
_FILE-rung_1.csv
#VER=2.0
#LABEL=a-hme-man
#COMMENT=home A with Ao button
#PREVRUNG=2
#NEXTRUNG=3
1-0-50/54 , 2-0-50/59 , 9-0-0/0 , 1-0-50/58 , 9-0-0/0 , 99-0-0/0 , 13-0-0/6 , 9-0-0/0 , 9-0-0/0 , 50-0-0/0
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 99-0-0/0 , 99-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-50/0 , 0-0-0/0 , 0-0-0/2 , 0-0-0/0 , 0-0-0/0 , 0-0-60/46
2-0-0/0 , 9-0-0/0 , 9-0-0/0 , 99-0-50/0 , 13-0-0/2 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 50-0-60/46
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 99-0-0/0 , 99-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
_/FILE-rung_1.csv
_FILE-arithmetic_expressions.csv
#VER=2.0
_/FILE-arithmetic_expressions.csv
_FILE-symbols.csv
#VER=1.0
%I0,btn-usr1,
%I1,btn-usr2,
%I2,btn-m7,
%I3,btn-m8,
%I4,btn-home, l
%I5,btn-m4,
%I6,btn-m5,
%I7,btn-m3,
%I8,btn-y0,
%I9,btn-a-,
%I10,btn-z+,
%I11,btn-y+,
%I12,btn-prgSt,
%I13,btn-prgPs,
%I14,btn-prgCl,
%I15,btn-x0,
%I16,btn-z0,
%I17,btn-x-,
%I18,btn-4achs,
%I19,btn-x+,
%I20,btn-a+,
%I21,btn-z-,
%I22,btn-y-,
%I23,btn-a0,
%I36,btn-wzOut,
%I37,btn-usr3,
%I38,btn-wzIn,
%I39,btn-g91,
%I40,btn-usr5,
%I41,btn-usr4,
%I42,btn-drsEn,
%I43,drv-fault,
%I44,btn-splEn,
%I45,Err-Varm,
%I46,Err-Hspdl,
%I47,Err-Estp,
%I50,Mach-isOn,
%I51,mode=man,
%I52,mode=mdi,
%I53,mode=auto,
%I54,mode=jnt,
%I57,a-homed,
%I58,a-hmng,
%I59,a-prsnt,
%I60,spl-atRst,
%I62,spl-emcEn,
%I63,spl-emcDr,
%I70,m7-isOn,
%I71,m8-isOn,
%I75,led-prgRn,
%I76,led-prgPs,
%Q0,Q0,
%Q1,Q1,
%Q2,Q2,
%Q3,Q3,
%Q4,Q4,
%Q5,led-home,
%Q6,led-m4,
%Q7,led-m3,
%Q8,led-m8,
%Q9,led-m7,
%Q10,led-usr4,
%Q11,led-usr5,
%Q12,led-wzout,
%Q13,led-usr3,
%Q14,led-g91,
%Q15,led-wzin,
%Q16,led-usr1,
%Q17,led-usr2,
%Q18,Q18,
%Q19,led-prgps,
%Q20,led-prgst,
%Q21,led-4achs,
%Q22,rly-fan,
%Q23,Q23,
%Q24,Q24,
%Q25,Q25,
%Q26,Q26,
%Q27,Q27,
%Q28,Q28,
%Q29,Q29,
%Q30,Q30,
%Q31,rly-wzRls,
%Q32,rly-wzLck,
%Q33,rly-dose,
%Q34,Q34,
%Q35,led-splEn,
%Q36,led-drsEn,
%Q37,Q37,
%Q38,Q38,
%Q39,Q39,
%Q40,emc-en,
%Q41,btn-mach,
%Q43,drvs-en,
%Q45,home-all,
%Q46,home-aMan,
%Q47,jog-aSpd,
%Q51,spl-drv,
%Q53,m3En,
%Q54,m4En,
%Q55,m5En,
%Q60,m7-On,
%Q61,m7-Off,
%Q62,m8-On,
%Q63,m8-Off,
%Q70,prg-ps,
%Q71,prg-rsm,
%Q72,prg-stp,
%Q73,prg-run,
%Q80,zero-x,
%Q81,zero-y,
%Q82,zero-z,
%Q83,zero-a,
%Q85,btn-g91,
%Q87,btn-mode,
%B0,B0,
%B1,B1,
%B2,B2,
%B3,B3,
%B4,B4,
%B5,B5,
%B6,B6,
%B7,B7,
%B8,B8,
%B9,B9,
%B10,B10,
%B11,B11,
%B12,B12,
%B13,B13,
%B14,B14,
%B15,B15,
%B16,B16,
%B17,B17,
%B18,B18,
%B19,B19,
%B20,B20,
%B21,B21,
%B22,B22,
%B23,B23,
%B24,B24,
%B25,B25,
%B26,B26,
%B27,B27,
%B28,B28,
%B29,B29,
%B30,B30,
%B31,B31,
%B32,B32,
%B33,B33,
%B34,B34,
%B35,B35,
%B36,B36,
%B37,B37,
%B38,B38,
%B39,B39,
%W0,%W0,
%W1,%W1,
%W2,%W2,
%W3,%W3,
%W4,%W4,
%W5,%W5,
%W6,%W6,
%W7,%W7,
%W8,%W8,
%W9,%W9,
%W10,%W10,
%W11,%W11,
%W12,%W12,
%W13,%W13,
%W14,%W14,
%W15,%W15,
%W16,%W16,
%W17,%W17,
%W18,%W18,
%W19,%W19,
%IW0,%IW0,
%IW1,%IW1,
%IW2,%IW2,
%IW3,%IW3,
%IW4,%IW4,
%IW5,%IW5,
%IW6,%IW6,
%IW7,%IW7,
%IW8,%IW8,
%IW9,%IW9,
%QW0,%QW0,
%QW1,%QW1,
%QW2,%QW2,
%QW3,%QW3,
%QW4,%QW4,
%QW5,%QW5,
%QW6,%QW6,
%QW7,%QW7,
%QW8,%QW8,
%QW9,%QW9,
%IF0,%IF0,
%IF1,%IF1,
%IF2,%IF2,
_/FILE-symbols.csv
_FILE-rung_11.csv
#VER=2.0
#LABEL=mdi-hnd
#COMMENT=toggle mdi and hand modus
#PREVRUNG=10
#NEXTRUNG=-1
2-0-50/53 , 9-0-0/0 , 1-0-50/37 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 50-0-60/87
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
_/FILE-rung_11.csv
_FILE-rung_9.csv
#VER=2.0
#LABEL=zero-axis
#COMMENT=Zero X,Y,Z,A
#PREVRUNG=8
#NEXTRUNG=10
2-0-50/53 , 9-0-0/0 , 1-0-50/50 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 1-0-50/15 , 9-0-0/0 , 9-0-0/0 , 50-0-60/80
0-0-0/0 , 0-0-0/0 , 0-0-50/8 , 0-1-0/0 , 0-0-0/0 , 9-1-0/0 , 1-0-50/8 , 9-0-0/0 , 9-0-0/0 , 50-0-60/81
0-0-0/0 , 0-0-0/0 , 0-0-50/16 , 0-1-0/0 , 0-0-0/0 , 9-1-0/0 , 1-0-50/16 , 9-0-0/0 , 9-0-0/0 , 50-0-60/82
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-1-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
0-0-0/0 , 0-0-0/0 , 0-0-50/23 , 9-1-0/0 , 1-0-50/57 , 9-0-0/0 , 1-0-50/23 , 9-0-0/0 , 9-0-0/0 , 50-0-60/83
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
_/FILE-rung_9.csv
_FILE-rung_6.csv
#VER=2.0
#LABEL=wkw
#COMMENT=Werkzeugwechsler
#PREVRUNG=4
#NEXTRUNG=8
0-0-60/40 , 0-0-0/0 , 0-0-50/70 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-60/60
1-0-60/40 , 1-0-50/50 , 1-0-50/2 , 9-0-0/0 , 99-0-50/2 , 13-0-50/4 , 9-0-0/0 , 9-0-50/0 , 2-0-50/70 , 50-0-60/60
0-0-0/0 , 0-0-0/0 , 0-1-50/70 , 0-0-0/0 , 99-0-50/70 , 99-0-50/70 , 0-0-0/0 , 9-1-50/0 , 1-0-50/70 , 50-0-60/61
0-0-50/71 , 0-0-0/0 , 0-1-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
0-0-0/0 , 0-0-50/0 , 1-1-50/3 , 9-0-0/0 , 99-0-50/3 , 13-0-50/5 , 9-0-0/0 , 9-0-0/0 , 2-0-50/71 , 50-0-60/62
0-0-0/0 , 0-0-0/0 , 0-0-50/71 , 0-0-0/0 , 99-0-50/71 , 99-0-50/71 , 0-0-0/0 , 9-1-0/0 , 1-0-50/71 , 50-0-60/63
_/FILE-rung_6.csv
_FILE-rung_10.csv
#VER=2.0
#LABEL=G90-G91
#COMMENT=Panel button G90 <-> G91
#PREVRUNG=9
#NEXTRUNG=11
1-0-50/52 , 9-0-0/0 , 1-0-50/39 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 9-0-0/0 , 50-0-60/85
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0 , 0-0-0/0
_/FILE-rung_10.csv
_FILE-ioconf.csv
#VER=1.0
_/FILE-ioconf.csv
_FILE-com_params.txt
MODBUS_MASTER_SERIAL_PORT=
MODBUS_MASTER_SERIAL_SPEED=9600
MODBUS_MASTER_SERIAL_DATABITS=8
MODBUS_MASTER_SERIAL_STOPBITS=1
MODBUS_MASTER_SERIAL_PARITY=0
MODBUS_ELEMENT_OFFSET=0
MODBUS_MASTER_SERIAL_USE_RTS_TO_SEND=0
MODBUS_MASTER_TIME_INTER_FRAME=100
MODBUS_MASTER_TIME_OUT_RECEIPT=500
MODBUS_MASTER_TIME_AFTER_TRANSMIT=0
MODBUS_DEBUG_LEVEL=0
MODBUS_MAP_COIL_READ=0
MODBUS_MAP_COIL_WRITE=0
MODBUS_MAP_INPUT=0
MODBUS_MAP_HOLDING=0
MODBUS_MAP_REGISTER_READ=0
MODBUS_MAP_REGISTER_WRITE=0
_/FILE-com_params.txt
_FILE-general.txt
PERIODIC_REFRESH=1
SIZE_NBR_RUNGS=20
SIZE_NBR_BITS=20
SIZE_NBR_WORDS=20
SIZE_NBR_TIMERS=10
SIZE_NBR_MONOSTABLES=10
SIZE_NBR_COUNTERS=10
SIZE_NBR_TIMERS_IEC=10
SIZE_NBR_PHYS_INPUTS=90
SIZE_NBR_PHYS_OUTPUTS=90
SIZE_NBR_ARITHM_EXPR=100
SIZE_NBR_SECTIONS=10
SIZE_NBR_SYMBOLS=200
_/FILE-general.txt
_FILE-timers_iec.csv
1,30,1
2,5,1
2,5,2
2,1,2
2,1,2
2,1,2
2,5,2
2,1,2
1,0,0
1,0,0
_/FILE-timers_iec.csv
_/FILES_CLASSICLADDER