10 months 2 weeks ago #340003 by Ismacr63
Hello, I've bought my first VFD, a Vevor A2 8015 1.5kW model, for a 0.75kW, 1000rpm motor for my mini lathe. I've configured the most basic options and added an external potentiometer and a 3-position switch for forward and reverse.
I'd like to add two momentary switches, one for start and one for stop. Is that possible with my VFD? Can anyone help me with this?

I've attached the manual.

Please Log in to join the conversation.

More
10 months 2 weeks ago #340005 by tommylight
Replied by tommylight on topic VFD configuration help
You already have that with the 3 position switch.
If you want to use momentary switches for it, might need to add relays.

Please Log in to join the conversation.

More
10 months 2 weeks ago #340008 by Ismacr63
Replied by Ismacr63 on topic VFD configuration help
That's true, but I'd like to have the buttons because that's the configuration I've had until now.
What kind of relay do I need?

Please Log in to join the conversation.

More
10 months 2 weeks ago #340028 by tommylight
Replied by tommylight on topic VFD configuration help
Buttons, are they momentary or on/off ?

Please Log in to join the conversation.

More
10 months 2 weeks ago #340030 by Ismacr63
Replied by Ismacr63 on topic VFD configuration help
The buttons are momentary.

Please Log in to join the conversation.

More
10 months 2 weeks ago #340036 by NWE
Replied by NWE on topic VFD configuration help
If you use a normally open start button and a normally closed stop button, it appears it could work to set parameter 28 = 2 to make its signal relay operate when the inverter starts. Then it should be possible to wire it similar to a contactor with an aux. contact.

Please Log in to join the conversation.

More
10 months 2 weeks ago #340056 by Ismacr63
Replied by Ismacr63 on topic VFD configuration help
Thanks for your reply. That works fine, except I can't use the three-position switch for forward and reverse.
I've also noticed that when I press the stop button, I have to hold it down until the motor stops completely. If I release it before the motor stops, it doesn't stop and the RPMs increase again.
I'll keep this VFD (A2 8015) for a belt sander I'm building.
I bought another VFD, a Suswe SU600, for the lathe, and I'd like to do the same as with the other one: add a three-position switch for forward and reverse, and a start/stop button.

Please Log in to join the conversation.

More
10 months 3 days ago #340590 by Ismacr63
Replied by Ismacr63 on topic VFD configuration help
I received the Suswe SU-600 VFD today. I started by getting the motor to rotate. I configured it in Advanced Vector Control with the parameters from the motor's nameplate, but it's not producing any torque. What parameters would I need to configure to get good torque at low RPMs? The motor is rated at 0.86 kW, 380 V, 2.1 A, and 1000 RPM.