You need to make your calculations based on the screw pitch and reduction to get the encoder resolution.
It can lower your step rate depending on the hardware that you choose.
Please Log in to join the conversation.
I put three different encoders on my machine and scaled so I have .100 inch of travel per motor revolution which is what I require.
Encoder 1 has 250ppr and needs a scale factor of 10,000
Encoder 2 has 1000ppr and needs 40,000
Encoder 3 has 1024ppr and needs 20,480
Encoder 3 is only getting half the counts it should.
They are all the same BEI ABZC indexed encoders.
I can live with the lower count but does anyone know what happened?
Also a spare encoder is open collector not line driver. Is there a way to use it with a converter chip of some sort or should I get rid of it?
Please Log in to join the conversation.
Its possible to use open collector encoders but you may need pullup resistors
to 5V on the A/B/Z wires (most mesa encoder inputs have these pullups)
Please Log in to join the conversation.
It depends somewhat on the technology of the servo system.greeder88 wrote: What is the recommended CPR for milling machine encoders? I assume too high a count slows the rapid speed? Too low makes oval circles?
I have 20,000 counts/inch on X and Y and 40,000 counts/inch on Z on my
Bridgeport mill, with analog velocity servos. This works well.
However, on my minimill with PWM servos I have 128,000 counts/inch,
and wouldn't mind having more.
The only time encoder resolution is likely to be a speed limit is
with software generated step pulses and step-servos like the
Gecko G320 drives.
Too low resolution won't make oval circles, it will make stairsteps
on certain moves where one axis is moving slowly while the other
one moves fast.
As for open collector encoders, just use a resistor to pull all
outputs up to +5 V. Generally, 1 K Ohm resistors should work
fine.
Jon
Please Log in to join the conversation.
Also learned you should hook up the 0v first (While you mind is less confused). I found out the 0v wire is the killer of encoders if you get that wrong.
I changed the jumpers on the 7i77 to single ended and my open collector encoder worked!
With the jumpers switched would I still have a Differential encoder since the encoder has the A, A-.B,B-,Z,Z- ? Or does the jumper take the (not ones) out of action?
Please Log in to join the conversation.
By using A_ and B_ you are only providing half of the information, like using A and B only.
The use of the complementary information (A and A_ for example) is to provide better immunity for noise. If your system is not electrical noise active (for example if it does not have a VFD) then you do not need to use the complement, although it is recommended.
You cannot use B and B_ only, like you cannot use A and A_ only.
Wiring 0V first then 5V after or the way around makes no difference (I believe that you are wiring them with the power disconnected) !
Please Log in to join the conversation.
- tommylight
-
- Away
- Administrator
-
- Posts: 22010
- Thank you received: 3
Bumped into this, to old but for the sake of having correct information.greeder88 wrote: I an getting some weirdness with the scale factor.
I put three different encoders on my machine and scaled so I have .100 inch of travel per motor revolution which is what I require.
Encoder 1 has 250ppr and needs a scale factor of 10,000
Encoder 2 has 1000ppr and needs 40,000
Encoder 3 has 1024ppr and needs 20,480
Encoder 3 is only getting half the counts it should.
They are all the same BEI ABZC indexed encoders.
I can live with the lower count but does anyone know what happened?
Also a spare encoder is open collector not line driver. Is there a way to use it with a converter chip of some sort or should I get rid of it?
Encoder 3 should be set at 40960, you had it at half so you where getting half the counts.