Mesa 7i76 output current was created by Clive S
Mesa 7i76 card
Just for the sake of clarity in the manual it state 300mA max load. Would that be for each o/p or the total of all the outputs.
Thanks
Just for the sake of clarity in the manual it state 300mA max load. Would that be for each o/p or the total of all the outputs.
Thanks
Please Log in to join the conversation.
10 years 7 months ago #70868
by PCW
Replied by PCW on topic Mesa 7i76 output current
Outputs can drive 350 mA maximum but there is a 1.4A per chip limit
So if all 8 outputs in one chip were on at once, this would limit the individual output current to 175 mA