Analog signal linearity

More
8 years 10 months ago #103228 by Methier
Hi, this is my first post
I'm working with mesa 7i77+5i25, i have everything connected and working, I'm in the tunning part,
i decided to test if the analog signal was at the correct scale, by opening a opened a halscope, and tested the commanded speed and encoder feedback, all the PID gains to zero just because i wanted to see the output without any PID correction, then i noticed that at low speeds i get a matching speed signal between commanded speed and encoder feedback, but when i increased the signal to get higher speed i got a noticeable difference.
Based on that i measured the voltage at the output,

Commanded - Measured
Voltage(VDC) - Voltage(VDC)
10 - - - - - - - - - - - - - 9.55
9 - - - - - - - - - - - - - - 8.5
8 - - - - - - - - - - - - - - 7.6
7 - - - - - - - - - - - - - - 6.7
6 - - - - - - - - - - - - - - 5.9
5 - - - - - - - - - - - - - - 5.2
4 - - - - - - - - - - - - - - 4.3
3 - - - - - - - - - - - - - - 3.00
2 - - - - - - - - - - - - - - 2.02
1 - - - - - - - - - - - - - - 1.02
0 - - - - - - - - - - - - - - 0.05



Measurements where made with a 24VDC power supply connected to field voltage input, i checked if there was some noise with a oscilloscope and everything was ok, i made the tests inside my house so i don't think that it was external noise from the shop, ground connection is ok.

i know that is not a big deal, perhaps PID can compensate that difference, but i think it will improve the performance of the system.
Is there a function to linearize analog output?
i can program my own, that's why i like linuxcnc but if it is already made i can save some time and go to the next step and see those chips flying around.

Best Regards

Please Log in to join the conversation.

More
8 years 10 months ago #103231 by PCW
Replied by PCW on topic Analog signal linearity
7I77 analog linearity should be better than .1 % and .05V offset at 0 is way too high

How are you measuring the output?

Also check the 7I77s 5V source. If this is low, you can have analog output issues

Please Log in to join the conversation.

More
8 years 10 months ago #103232 by Methier
Replied by Methier on topic Analog signal linearity
negative lead to GND (from the same terminal block ofc)
positive to AOUT0

i checked with multimeter and oscilloscope, both gave me same readings.

Regards

Please Log in to join the conversation.

More
8 years 10 months ago #103233 by PCW
Replied by PCW on topic Analog signal linearity
I would check the 5V, If that is OK and you are sure about you multimeter accuracy,
I would get an RMA for the card as it clearly broken.

Please Log in to join the conversation.

More
8 years 10 months ago #103283 by andypugh
Replied by andypugh on topic Analog signal linearity

PCW wrote: are sure about you multimeter accuracy.


My multimeter gets inaccurate when the battery is low. (eventually it over-reads b a factor of two!)

Can you test with two multimeters and see if they agree?

The "lincurve" HAL component could correct for this, but maybe not reliably, because PCW says that something is wrong, so the error might not remain constant over time.

Please Log in to join the conversation.

More
8 years 10 months ago #103295 by Methier
Replied by Methier on topic Analog signal linearity
Hi, thanks for your reply
I'm waiting for another multimeter from a friend and I was using the 5v power supply from 5i25 board (readings gave me 4.85v), I bought an independient adjustable 5v power supply to see if there are any improvement.

I will do tests today at noon.

Best Regards

Please Log in to join the conversation.

More
8 years 6 months ago #109039 by Methier
Replied by Methier on topic Analog signal linearity
Hi, sry for the delay with my reply, the independent 5v psu made a good improvement with the analog out, perhaps because the PC is an old one the PSU is about to die, i did some tests with good results so i will keep the external one.

The problem now are the servo motors, quite old, and no maintenance from the last owner damaged im some way the feedback devices.

Anyway thanks for your help.

Please Log in to join the conversation.

Time to create page: 0.102 seconds