- Posts: 161
- Thank you received: 0
Does anyone have a link to a good tutorial on flashing a Mesa card 7i96e and 7i8
7 years 1 week ago #148115
by jools
Does anyone have a link to a good tutorial on flashing a Mesa card 7i96e and 7i8 was created by jools
As the title says prefferably a video if possible.
Cheers
Jools
Cheers
Jools
Please Log in to join the conversation.
- tommylight
-
- Offline
- Administrator
-
Less
More
- Posts: 22010
- Thank you received: 3
7 years 1 week ago #148118
by tommylight
Replied by tommylight on topic Does anyone have a link to a good tutorial on flashing a Mesa card 7i96e and 7i8
sudo mesaflash --board_type --readhmid
for normal PCI or PCI-E cards
For ethernet:
sudo mesaflash --device 7i96 --addr 10.10.10.10 --readhmid
Granted your board IP is set at 10.10.10.10 , or 192.168.1.121 from factory
For flashing the card
sudo mesaflash --device 7i96 --addr 10.10.10.10 --write name_of_the_file.bin
the bin file needs to be in the same directory as mesaflash utility
then
sudo mesaflash --device 7i96 --addr 10.10.10.10 --reload
then
sudo mesaflash --device 7i96 --addr 10.10.10.10 --readhmid.
for normal PCI or PCI-E cards
For ethernet:
sudo mesaflash --device 7i96 --addr 10.10.10.10 --readhmid
Granted your board IP is set at 10.10.10.10 , or 192.168.1.121 from factory
For flashing the card
sudo mesaflash --device 7i96 --addr 10.10.10.10 --write name_of_the_file.bin
the bin file needs to be in the same directory as mesaflash utility
then
sudo mesaflash --device 7i96 --addr 10.10.10.10 --reload
then
sudo mesaflash --device 7i96 --addr 10.10.10.10 --readhmid.
Please Log in to join the conversation.
7 years 1 week ago #148122
by PCW
Replied by PCW on topic Does anyone have a link to a good tutorial on flashing a Mesa card 7i96e and 7i8
A few minor nits:
1. You normally write .bit files with mesaflash
2. You don't need sudo for Ethernet cards
3. You don't need to specify the IP address if the card is set for 192.168.1.121
1. You normally write .bit files with mesaflash
2. You don't need sudo for Ethernet cards
3. You don't need to specify the IP address if the card is set for 192.168.1.121
Please Log in to join the conversation.
7 years 1 week ago #148199
by jools
Replied by jools on topic Does anyone have a link to a good tutorial on flashing a Mesa card 7i96e and 7i8
So for the 7i96 I power it up with 5v into the P3 connector while connected to ethernet.
Having downloaded mesaflash I make sure the correct .bin file is in the same directory. - Which .bin file do I choose and where is it? The file I downloaded from Mesa contains .pin and .bit.
Also which file do I choose? are there explanations of which ones are for which setup somewhere?
Confused on IP address now with the two comments. Documentation says default is 192.168.1.121 - Does this change Tommy's instructions? If so how?
Do I need to flash the 7i85s?
Also as a seperate can I connect my home switches direct to the inputs and drive them from that? Looking to go with fotek proximities NC which have a 6v to 30v operating window. Any help with if they need a seperate power supply or not and how to wire would be cool too.
Cheers
Jools
Having downloaded mesaflash I make sure the correct .bin file is in the same directory. - Which .bin file do I choose and where is it? The file I downloaded from Mesa contains .pin and .bit.
Also which file do I choose? are there explanations of which ones are for which setup somewhere?
Confused on IP address now with the two comments. Documentation says default is 192.168.1.121 - Does this change Tommy's instructions? If so how?
Do I need to flash the 7i85s?
Also as a seperate can I connect my home switches direct to the inputs and drive them from that? Looking to go with fotek proximities NC which have a 6v to 30v operating window. Any help with if they need a seperate power supply or not and how to wire would be cool too.
Cheers
Jools
Please Log in to join the conversation.
- tommylight
-
- Offline
- Administrator
-
Less
More
- Posts: 22010
- Thank you received: 3
7 years 1 week ago #148203
by tommylight
Replied by tommylight on topic Does anyone have a link to a good tutorial on flashing a Mesa card 7i96e and 7i8
forum.linuxcnc.org/27-driver-boards/3559...ethernet-mesa-boards
Ip is set from the factory to 192.168.1.121 but there is a jumper on the board to have it set at 10.10.10.10.
7i96 inputs can be used for NPN or PNP switches so any will do, just the wiring changes a bit.
You do need a separate power supply for the field power on the 7i96 and you can use that same source to power the switches.
Ip is set from the factory to 192.168.1.121 but there is a jumper on the board to have it set at 10.10.10.10.
7i96 inputs can be used for NPN or PNP switches so any will do, just the wiring changes a bit.
You do need a separate power supply for the field power on the 7i96 and you can use that same source to power the switches.
Please Log in to join the conversation.
7 years 1 week ago #148204
by PCW
Replied by PCW on topic Does anyone have a link to a good tutorial on flashing a Mesa card 7i96e and 7i8
If you have a 7I85S you will need 7i96_7i85sd.bit firmware
The IP address (192.168.1.121 or 10.10.10.10) depends on 7I96 jumpering
(see the 7I96 manual)
There is no firmware on the 7I85S
Looks like the 7i96_7i85sd firmware is not in the 7i96 zip file but here it is:
freeby.mesanet.com/7i96_7i85sd.bit
You can connect the proximity sensor outputs directly to the 7I96 isolated inputs
If you have NPN sensors you would connect the 7I96 input common to +12 or +24V
If you have PNP sensors you would connect the 7I96 input common to ground
The IP address (192.168.1.121 or 10.10.10.10) depends on 7I96 jumpering
(see the 7I96 manual)
There is no firmware on the 7I85S
Looks like the 7i96_7i85sd firmware is not in the 7i96 zip file but here it is:
freeby.mesanet.com/7i96_7i85sd.bit
You can connect the proximity sensor outputs directly to the 7I96 isolated inputs
If you have NPN sensors you would connect the 7I96 input common to +12 or +24V
If you have PNP sensors you would connect the 7I96 input common to ground
Please Log in to join the conversation.
7 years 1 week ago #148487
by jools
Replied by jools on topic Does anyone have a link to a good tutorial on flashing a Mesa card 7i96e and 7i8
Are there any wiring diagrams anywhere for the 7i96 and 7i85 combo?
Please Log in to join the conversation.
- tommylight
-
- Offline
- Administrator
-
Less
More
- Posts: 22010
- Thank you received: 3
7 years 1 week ago #148496
by tommylight
Replied by tommylight on topic Does anyone have a link to a good tutorial on flashing a Mesa card 7i96e and 7i8
You will need a DB25 cable, if you already do not have one.
Get is from:
mesanet.com
mesaus.com
eusurplus.com
Get is from:
mesanet.com
mesaus.com
eusurplus.com
Please Log in to join the conversation.
- tommylight
-
- Offline
- Administrator
-
Less
More
- Posts: 22010
- Thank you received: 3
7 years 1 week ago #148497
by tommylight
Replied by tommylight on topic Does anyone have a link to a good tutorial on flashing a Mesa card 7i96e and 7i8
@Jools,
Hmmmmm, why does your IP say you are in China ? are you using a proxy or VPN?
I cat try to mail you one since i have plenty of them, just to check if our f@#$% post office is usable. Had terrible service before, so maybe, just maybe they got their sh1t together.
Hmmmmm, why does your IP say you are in China ? are you using a proxy or VPN?
I cat try to mail you one since i have plenty of them, just to check if our f@#$% post office is usable. Had terrible service before, so maybe, just maybe they got their sh1t together.
Please Log in to join the conversation.
7 years 1 week ago #148534
by jools
Replied by jools on topic Does anyone have a link to a good tutorial on flashing a Mesa card 7i96e and 7i8
Ha I have no idea why my IP is Chinese though when I login on a new Apple device to my iCloud it does normally tell me that someone in London/MiltonKeynes or anyone else down south is logging on; I'm based in Lincoln though.....
Any chance you could take a photo of one and upload it here?
I have a block to 26 pin block to DB25 cable coming in the post tomorrow.
Cheers
Any chance you could take a photo of one and upload it here?
I have a block to 26 pin block to DB25 cable coming in the post tomorrow.
Cheers
Please Log in to join the conversation.
Time to create page: 0.102 seconds
