5 years 10 months ago #190753 by bevins

eighthaxis wrote: Thanks for the input Aciera you were right on that one!
I supplied 24VDC from an external power supply to terminals 10 and 18 and changed P0-06 to H000 and walla the drive is enabled.
The problem now is that it still is not physically responding to the external analog input. Fn-04 status indicator (Differential analog sample value) is at about 2060 but increases to 2360 when I apply 1.6VDC to the differential analog input(term. 19&20) so the drive is seeing the signal.
I also tried changing P0-04 to all 6 different control mode types so it not that value.
Getting closer any extra input is greatly appreciated.


Make sure your drive is set to velocity mode.

Please Log in to join the conversation.

More
5 years 10 months ago #190775 by eighthaxis
Thanks for the input but I already tried all 6 modes.
Here are my current settings.

Please Log in to join the conversation.

More
5 years 10 months ago #190914 by eighthaxis
VICTORY!
I finally figured it out today.
It was the P5-10 setting that needed to be calibrated.
The manual is very unclear on this part.
It works great now!
Thanks for all of the help.

Please Log in to join the conversation.

Time to create page: 0.078 seconds