7i80hd + 7i33 + 7i37 + 7i84
5 years 3 months ago #214914
by vre
Replied by vre on topic 7i80hd + 7i33 + 7i37 + 7i84
Because i can't find how to change the output voltage of 7i33
what settings must change for 0-2.5-5 V analog output ?
what settings must change for 0-2.5-5 V analog output ?
Please Log in to join the conversation.
5 years 3 months ago #214922
by PCW
Replied by PCW on topic 7i80hd + 7i33 + 7i37 + 7i84
You would need to set the PWM channel offset mode true
and bound the PID output to 2.5 (with a PWM scale of 10)
This assumes you are running LinuxCNC 2.8.1 or greater
and bound the PID output to 2.5 (with a PWM scale of 10)
This assumes you are running LinuxCNC 2.8.1 or greater
Please Log in to join the conversation.
5 years 3 months ago #214949
by vre
Replied by vre on topic 7i80hd + 7i33 + 7i37 + 7i84
From these settings
linuxcnc.org/docs/html/man/man9/pid.9.html
pid output bound is this?
pid output bound is this?
pid.N.output float out
The output of the PID loop, which goes to some actuator such as a motor.
Please Log in to join the conversation.
5 years 3 months ago #215244
by vre
Replied by vre on topic 7i80hd + 7i33 + 7i37 + 7i84
How to bound the PID output to 2.5 what are the settings?