How do you pass shielded servo motor cables through the cabinet wall/panel?
4 years 2 months ago #249113
by mgm
Replied by mgm on topic How do you pass shielded servo motor cables through the cabinet wall/panel?
The side on the Antieb is open with me
Please Log in to join the conversation.
4 years 2 months ago #249115
by arvidb
Note that you must still connect the ground conductor between the motor and the drive terminal, for safety.
Replied by arvidb on topic How do you pass shielded servo motor cables through the cabinet wall/panel?
You don't. Look at the Siemens video I linked above.So if you use a ground clamp as suggested by above links above, how do you connect the shield to the drive connector terminal block?
Note that you must still connect the ground conductor between the motor and the drive terminal, for safety.
Please Log in to join the conversation.
4 years 2 months ago #249117
by mgm
Replied by mgm on topic How do you pass shielded servo motor cables through the cabinet wall/panel?
I wouldn't know where to put the screen on my milling spindle. The junction box is in plastic.
A grounding cable is of course present!
A grounding cable is of course present!
Please Log in to join the conversation.
4 years 2 months ago #249150
by rodw
Ref: www.lamtechnologies.com/Product.aspx?lng=EN&idp=DS1076
Elsewhere, they suggest the cable pass through the cabinet intact (eg. via a cable grommet)
When I've used these drivers, I've also terminated the shield to a copper grounding post on the enclosusre as shown here.
Note we've deliberately chosen steppers over servos in this application (plasma table) to leverage the massive acceleration steppers provide. (5 m/sec/sec or higher)
Replied by rodw on topic How do you pass shielded servo motor cables through the cabinet wall/panel?
The video shows use of a cable for servos with an additional ground conductor. In the case of a 4 wire stepper system, some quality stepper drives require the shield to be terminated at the drive as this diagram from the manual of a Lam Technologies DS1076A shows.
So if you use a ground clamp as suggested by above links above, how do you connect the shield to the drive connector terminal block?
You don't. Look at the Siemens video I linked above.
Note that you must still connect the ground conductor between the motor and the drive terminal, for safety.
Attachment not found
Ref: www.lamtechnologies.com/Product.aspx?lng=EN&idp=DS1076
Elsewhere, they suggest the cable pass through the cabinet intact (eg. via a cable grommet)
When I've used these drivers, I've also terminated the shield to a copper grounding post on the enclosusre as shown here.
Attachment not found
Note we've deliberately chosen steppers over servos in this application (plasma table) to leverage the massive acceleration steppers provide. (5 m/sec/sec or higher)
Please Log in to join the conversation.
4 years 2 months ago #249153
by rodw
Replied by rodw on topic How do you pass shielded servo motor cables through the cabinet wall/panel?
So from my post above, I am still confused somewhat but it seems one thing that both Siemens and Lam have in common is not to use any connectors where the cables enter the cabinet. Elsewhere in the Lam manual it shows:
I guess use of a grounding clamps could be used instead of my pigtails to frame ground.
So best practice for both steppers and servos is not to do any soldering. Yippee!
Attachment not found
I guess use of a grounding clamps could be used instead of my pigtails to frame ground.
So best practice for both steppers and servos is not to do any soldering. Yippee!
Please Log in to join the conversation.
4 years 2 months ago #249176
by arvidb

I don't see anything about EMC compliance in the publicly available documentation for those drives. Maybe it's in the User Manual that's behind a registration wall? *doh* Maybe these drives aren't designed to meet any specific EMC standard and controlling EMI is just an afterthought? Or maybe they are controlling the rise times of the motor driver FETs to not produce high frequency EMI in the first place (at the expense of more heat) and have calculated that the pigtail connection of the shield is enough. Who knows?
Replied by arvidb on topic How do you pass shielded servo motor cables through the cabinet wall/panel?
Since the drives look to be insulated from the cabinet's grounded mount plate, connecting the shield with a clamp to the plate won't do you any good as I understand it. You are probably best off just following the instructions in the manual, paying close attention to the "it must be as much short at possible" part.I guess use of a grounding clamps could be used instead of my pigtails to frame ground.
I don't see anything about EMC compliance in the publicly available documentation for those drives. Maybe it's in the User Manual that's behind a registration wall? *doh* Maybe these drives aren't designed to meet any specific EMC standard and controlling EMI is just an afterthought? Or maybe they are controlling the rise times of the motor driver FETs to not produce high frequency EMI in the first place (at the expense of more heat) and have calculated that the pigtail connection of the shield is enough. Who knows?
Please Log in to join the conversation.
4 years 2 months ago #249177
by arvidb
But after reading about how the shield is the return path of common mode noise between motor frame and drive, I think a good solution is to attach the incoming cable shield with a P-clip to the aluminium plate that the motor will be mounted to. That should provide a low impedance path from the motor frame to the shield. I hope. At least that's the best idea I've been able to come up with!
Replied by arvidb on topic How do you pass shielded servo motor cables through the cabinet wall/panel?
Yeah I have similarly been scratching my head about how to connect the shield to these old servos:I wouldn't know where to put the screen on my milling spindle. The junction box is in plastic.
Attachment not found
But after reading about how the shield is the return path of common mode noise between motor frame and drive, I think a good solution is to attach the incoming cable shield with a P-clip to the aluminium plate that the motor will be mounted to. That should provide a low impedance path from the motor frame to the shield. I hope. At least that's the best idea I've been able to come up with!
Please Log in to join the conversation.
4 years 2 months ago #249181
by rodw
Replied by rodw on topic How do you pass shielded servo motor cables through the cabinet wall/panel?
@avidb, Normally you would leave the shield unattached at the motor and attach it to frame ground at the enclosure. I think you would use one of your grounding clamps as normal.
If for a plasma machine, you should attach a seperate ground wire from every motor that is run seperately back to the star ground point. Some industrial quality stepper motors actually have a screw terminal for this purpose. Alternatively use one of the motor mounting bolts. You also need to ensure that these ground wires bridge any motion rails to avoid EMI passing through the rail and its carriage. Hypertherm have a good tech note on grounding which I follow. www.hypertherm.com/Download?fileId=HYP103900&zip=False
Its probably best practice for any motor that does not have a dedicated ground wire.
So I suspect This would explain why Lam do it the way they do. The EMI is drained away by the grounding system.
If for a plasma machine, you should attach a seperate ground wire from every motor that is run seperately back to the star ground point. Some industrial quality stepper motors actually have a screw terminal for this purpose. Alternatively use one of the motor mounting bolts. You also need to ensure that these ground wires bridge any motion rails to avoid EMI passing through the rail and its carriage. Hypertherm have a good tech note on grounding which I follow. www.hypertherm.com/Download?fileId=HYP103900&zip=False
Its probably best practice for any motor that does not have a dedicated ground wire.
So I suspect This would explain why Lam do it the way they do. The EMI is drained away by the grounding system.
Please Log in to join the conversation.
4 years 2 months ago #249183
by arvidb
Most importantly, the two written sources explain their reasoning in a way that makes sense. Your call...
Replied by arvidb on topic How do you pass shielded servo motor cables through the cabinet wall/panel?
I'm not sure why you would say that since it's exactly the opposite of what's recommended by the sources I gave earlier. E.g. from the Danfoss document:@avidb, Normally you would leave the shield unattached at the motor and attach it to frame ground at the enclosure.
It is important to realize that the effect of a shielded cable is reduced when only one end is terminated. It is very important to terminate correctly both ends of the motor cable, otherwise interference problems may occur.
Most importantly, the two written sources explain their reasoning in a way that makes sense. Your call...
Which is exactly what you want to avoid since it creates a big current loop for the noise to radiate from. See the Electrical Engineering Portal images. You also want to keep the motor noise away from ground circuitry used by other equipment to which it can otherwise be conducted. You want the noise return path to be through the shield, not through motion rails or paths shared with feedback circuitry.So I suspect This would explain why Lam do it the way they do. The EMI is drained away by the grounding system.
Please Log in to join the conversation.
4 years 2 months ago #249184
by Aciera
Replied by Aciera on topic How do you pass shielded servo motor cables through the cabinet wall/panel?
Using pigtails to connect cable shielding is generally bad practice. Although I readily admit to have done it myself in the past. Of course EMI protection is more important in some installations than in others but motor drives being notorious for producing electromagnetic interference should be handled with extra diligence.
There is a ton of information on the web covering this. Here are just a few examples:
www.edn.com/never-use-pigtails-on-cable-shields/
www.rfemcdevelopment.eu/lv/emc-basics/emc-blog/147-emc-pigtail
In a cabinet one can use a ground busbar like this:
www.phoenixcontact.com/en-au/technologie...-in-control-cabinets
Personally I use P-Clamps and bolt those to busbars or the grounded backplate in the cabinet as those shield clamps can get a bit pricey. The only reason I see why companies like LAM suggest the use of (short) pigtails is to make wiring of their product look "easier".
The installation manual of a name brand VFD is usually a good source for proper grounding techniques.
But att the end of the day it's still a lot better to use shielded cabling with short pigtails than using unshielded cabling.
Edit
Just to be clear, I don't mean to be in anyway authorative about the matter or put anybodies work down. But since this has come up I thought I'd share what I had to learn (sometimes the hard way) in the past.
There is a ton of information on the web covering this. Here are just a few examples:
www.edn.com/never-use-pigtails-on-cable-shields/
www.rfemcdevelopment.eu/lv/emc-basics/emc-blog/147-emc-pigtail
In a cabinet one can use a ground busbar like this:
www.phoenixcontact.com/en-au/technologie...-in-control-cabinets
Personally I use P-Clamps and bolt those to busbars or the grounded backplate in the cabinet as those shield clamps can get a bit pricey. The only reason I see why companies like LAM suggest the use of (short) pigtails is to make wiring of their product look "easier".
The installation manual of a name brand VFD is usually a good source for proper grounding techniques.
But att the end of the day it's still a lot better to use shielded cabling with short pigtails than using unshielded cabling.
Edit
Just to be clear, I don't mean to be in anyway authorative about the matter or put anybodies work down. But since this has come up I thought I'd share what I had to learn (sometimes the hard way) in the past.
Please Log in to join the conversation.