Mesa 7I77 and Milltronics mill wiring

More
3 years 10 months ago #259312 by brianTruck
Would you run the analog signal through the enable pins so the if the e-stop was pushed the analog signal would disconnect from the drives or does the 7i77 disconnect the analog signal on estop internally?

Please Log in to join the conversation.

More
3 years 10 months ago #259317 by PCW
You could possibly damage the 7I77 card if you shorted all analog
outputs at once

If the analog enable hal pin is false, the 7i77's analog outputs are all set to 0V.
This and the drive enable(s) are the normal way motion is disabled when LinuxCNC
is not running or after a fault.

It's important that the  global drive enable s is controlled by LinuxCNC,
so the the drives are not enabled until LinuxCNC is running and the position
feedback loop is closed, otherwise the drives may drift slowly.

Please Log in to join the conversation.

More
3 years 10 months ago #259318 by Masiwood123
I think it turns it off, i.e. I think it's 0v when the machine is not moving, regardless of whether it's enabled or estop is on. it is optional for you to find the wires that brought the analog voltage from the controller to the drivers, so that with some power source..battery or similar 0-10v, you can check whether the motors are started by applying the voltage. the other thing that worries me, and there are people who know, is is that signal the same for the 7i77 sourcing or sinking version of the card? do you have the exact manufacturer ,model number or tag of those drivers, or a more detailed schematic of the driver itself?

Please Log in to join the conversation.

More
3 years 10 months ago #259321 by brianTruck
These are the drives.

Please Log in to join the conversation.

More
3 years 10 months ago #259325 by Masiwood123
4.4.3 SIGNAL INPUT:
The GA370 has two signal input configurations controlled by JP1. Configuration A (JP1 set on A) has two
single-ended inputs SIG. IN. (J1-2) and AUX. IN. (J1-1). Configuration B (JP1 set on B) has one single-ended
input AUX. IN (J1-1) and one differential input DIFF. IN (J2-1), DIFF. RET. (J2-2). (Refer to Appendix B,
drawing 370-3003). Typically when operating in the velocity mode, the input signal range is ±10 VDC. The
input voltage is summed with a precision DC tachometer to provide accurate velocity control at the servo motor
shaft (see fig. 3.1). The Signal Gain potentiometer RV2 (20 K), and Auxiliary Gain potentiometer RV1 (20 K),
adjust the motor velocity desired for a given input voltage velocity command (see 4.2 for recommended wire
type & size).

as I briefly looked at the manual, it seems that SigIN(1-2) or AuxIN(1-1) is an analog input if the factory drivers are set to A configuration..according to that, the power supply should be ..pin 4(GND) pin 2 (analog input voltage) I'm not sure, someone else on the forum if he can look at the instructions.. is your driver assembly all on one board, or are the driver cards separate for each axis? in any case, I would personally check the input with a lower voltage, say a 1.5v battery... if the motors turn, only then I would try via 7i77..
 

Please Log in to join the conversation.

More
3 years 10 months ago #259326 by Masiwood123

Please Log in to join the conversation.

More
3 years 10 months ago #259330 by brianTruck
I altered the drawing of one axis to reflect how it is really wired (22 is ground).

Please Log in to join the conversation.

More
3 years 10 months ago #259342 by Masiwood123
pin number 1 seems ok to me and it should be + from the controller and auxIn on the driver.. but according to the driver semi here it says that pin 4 is the common ground for the tacho (otherwise it generates current when the motor turns and gives feedback to the driver on the pin 3), and for the analog input.. if that is the arrangement of the pins in reality, I would try to disconnect that 22 ground and try with the battery, 

Attachment not found

- on pin 4 and plus on pin 1. with protective gloves, rubber boots and a helmet of course-:)

Please Log in to join the conversation.

More
3 years 10 months ago #259344 by Masiwood123
why 8? I also don't understand how this diode Cr on 22 is connected and what it is for..again need someone who understands to interpret it..Tomo help!

Please Log in to join the conversation.

More
3 years 10 months ago #259346 by Masiwood123
if one of your motors is free, you can try to spin it somehow, and measure if it gives any current between pins 4 and 3 (tacho), of course with the machine completely turned off.

Please Log in to join the conversation.