- Posts: 34
- Thank you received: 0
Mesa 7i96s with 5 encoders and Modbus
2 years 1 month ago #310664
by nartburg
Mesa 7i96s with 5 encoders and Modbus was created by nartburg
Dear folks,
I have a mesa 7i96s and want to set up 5 encoders and a pktUART Modbus connection.
So following talla83 youtube videos I got myself the efinity toolchain and started my experiments:
Adding the additional encoder input was straight forward except that my encoders are differential and additional encoder input on the mesa card take an a b signal so I had to get optical isolated rs485 to ttl boards
Now the pktUART part bugs me -- .as I want to use the smart serial as well.
so the first question: Is it possible to use two pins of the expansion port for Modbus communication?
the modified bitfile compiles (or whatever it is called) flashing is OK reloading is OK a mesaflash --read shows the pins (sry I can not attach it at the moment as I'm not in the shop at the moment) the modbus component description loads and at debug level 3 try's to send and receive but nothing is happening on the assigned pins.
I have a mesa 7i96s and want to set up 5 encoders and a pktUART Modbus connection.
So following talla83 youtube videos I got myself the efinity toolchain and started my experiments:
Adding the additional encoder input was straight forward except that my encoders are differential and additional encoder input on the mesa card take an a b signal so I had to get optical isolated rs485 to ttl boards
Now the pktUART part bugs me -- .as I want to use the smart serial as well.
so the first question: Is it possible to use two pins of the expansion port for Modbus communication?
the modified bitfile compiles (or whatever it is called) flashing is OK reloading is OK a mesaflash --read shows the pins (sry I can not attach it at the moment as I'm not in the shop at the moment) the modbus component description loads and at debug level 3 try's to send and receive but nothing is happening on the assigned pins.
Please Log in to join the conversation.
2 years 1 month ago #310665
by PCW
Replied by PCW on topic Mesa 7i96s with 5 encoders and Modbus
Typically you would use 3 pins for Modbus: RX, TX, and TXEN
Please Log in to join the conversation.
2 years 1 month ago #310709
by nartburg
Replied by nartburg on topic Mesa 7i96s with 5 encoders and Modbus
Now in the shop I retrived the .vhd File used to generate the bitfile
library IEEE;
use IEEE.std_logic_1164.all; -- defines std_logic types
use IEEE.STD_LOGIC_ARITH.ALL;
use IEEE.STD_LOGIC_UNSIGNED.ALL;
-- Copyright (C) 2007, Peter C. Wallace, Mesa Electronics
-- www.mesanet.com
--
-- This program is is licensed under a disjunctive dual license giving you
-- the choice of one of the two following sets of free software/open source
-- licensing terms:
--
-- * GNU General Public License (GPL), version 2.0 or later
-- * 3-clause BSD License
--
--
-- The GNU GPL License:
--
-- This program is free software; you can redistribute it and/or modify
-- it under the terms of the GNU General Public License as published by
-- the Free Software Foundation; either version 2 of the License, or
-- (at your option) any later version.
--
-- This program is distributed in the hope that it will be useful,
-- but WITHOUT ANY WARRANTY; without even the implied warranty of
-- MERCHANTABILITY or FITNESS FOR A PARTICULAR PURPOSE. See the
-- GNU General Public License for more details.
--
-- You should have received a copy of the GNU General Public License
-- along with this program; if not, write to the Free Software
-- Foundation, Inc., 51 Franklin St, Fifth Floor, Boston, MA 02110-1301 USA
--
--
-- The 3-clause BSD License:
--
-- Redistribution and use in source and binary forms, with or without
-- modification, are permitted provided that the following conditions
-- are met:
--
-- * Redistributions of source code must retain the above copyright
-- notice, this list of conditions and the following disclaimer.
--
-- * Redistributions in binary form must reproduce the above
-- copyright notice, this list of conditions and the following
-- disclaimer in the documentation and/or other materials
-- provided with the distribution.
--
-- * Neither the name of Mesa Electronics nor the names of its
-- contributors may be used to endorse or promote products
-- derived from this software without specific prior written
-- permission.
--
--
-- Disclaimer:
--
-- THIS SOFTWARE IS PROVIDED BY THE COPYRIGHT HOLDERS AND CONTRIBUTORS
-- "AS IS" AND ANY EXPRESS OR IMPLIED WARRANTIES, INCLUDING, BUT NOT
-- LIMITED TO, THE IMPLIED WARRANTIES OF MERCHANTABILITY AND FITNESS
-- FOR A PARTICULAR PURPOSE ARE DISCLAIMED. IN NO EVENT SHALL THE
-- COPYRIGHT OWNER OR CONTRIBUTORS BE LIABLE FOR ANY DIRECT, INDIRECT,
-- INCIDENTAL, SPECIAL, EXEMPLARY, OR CONSEQUENTIAL DAMAGES (INCLUDING,
-- BUT NOT LIMITED TO, PROCUREMENT OF SUBSTITUTE GOODS OR SERVICES;
-- LOSS OF USE, DATA, OR PROFITS; OR BUSINESS INTERRUPTION) HOWEVER
-- CAUSED AND ON ANY THEORY OF LIABILITY, WHETHER IN CONTRACT, STRICT
-- LIABILITY, OR TORT (INCLUDING NEGLIGENCE OR OTHERWISE) ARISING IN
-- ANY WAY OUT OF THE USE OF THIS SOFTWARE, EVEN IF ADVISED OF THE
-- POSSIBILITY OF SUCH DAMAGE.
--
use work.IDROMConst.all;
package PIN_7I96SD_Test_51 is
constant ModuleID : ModuleIDType :
(HM2DPLLTag, x"00", ClockLowTag, x"01", HM2DPLLBaseRateAddr&PadT, HM2DPLLNumRegs, x"00", HM2DPLLMPBitMask),
(WatchDogTag, x"00", ClockLowTag, x"01", WatchDogTimeAddr&PadT, WatchDogNumRegs, x"00", WatchDogMPBitMask),
(IOPortTag, x"00", ClockLowTag, x"03", PortAddr&PadT, IOPortNumRegs, x"00", IOPortMPBitMask),
(OutMTag, x"00", ClockLowTag, x"01", OutMDataAddr&PadT, OutMNumRegs, x"00", OutMMPBitMask),
(PWMTag, x"00", ClockHighTag, x"01", PWMValAddr&PadT, PWMNumRegs, x"00", PWMMPBitMask),
(StepGenTag, x"02", ClockLowTag, x"05", StepGenRateAddr&PadT, StepGenNumRegs, x"00", StepGenMPBitMask),
(QcountTag, x"02", ClockLowTag, x"06", QcounterAddr&PadT, QCounterNumRegs, x"00", QCounterMPBitMask),
(SSerialTag, x"00", ClockLowTag, x"01", SSerialCommandAddr&PadT, SSerialNumRegs, x"10", SSerialMPBitMask),
(XFrmrOutTag, x"00", ClockLowTag, x"01", XFrmrDataAddr&PadT, XFrmrNumRegs, x"00", XFrmrMPBitMask ),
(InMTag, x"00", ClockLowTag, x"01", InMControlAddr&PadT, InMNumRegs, x"00", InMMPBitMask),
(LEDTag, x"00", ClockLowTag, x"01", LEDAddr&PadT, LEDNumRegs, x"00", LEDMPBitMask),
(PktUARTTTag, x"02", ClockLowTag, x"01", PktUARTTDataAddr&PadT, PktUARTTNumRegs, x"00", PktUARTTMPBitMask),
(PktUARTRTag, x"02", ClockLowTag, x"01", PktUARTRDataAddr&PadT, PktUARTRNumRegs, x"00", PktUARTRMPBitMask),
(NullTag, x"00", NullTag, x"00", NullAddr&PadT, x"00", x"00", x"00000000"),
(NullTag, x"00", NullTag, x"00", NullAddr&PadT, x"00", x"00", x"00000000"),
(NullTag, x"00", NullTag, x"00", NullAddr&PadT, x"00", x"00", x"00000000"),
(NullTag, x"00", NullTag, x"00", NullAddr&PadT, x"00", x"00", x"00000000"),
(NullTag, x"00", NullTag, x"00", NullAddr&PadT, x"00", x"00", x"00000000"),
(NullTag, x"00", NullTag, x"00", NullAddr&PadT, x"00", x"00", x"00000000"),
(NullTag, x"00", NullTag, x"00", NullAddr&PadT, x"00", x"00", x"00000000"),
(NullTag, x"00", NullTag, x"00", NullAddr&PadT, x"00", x"00", x"00000000"),
(NullTag, x"00", NullTag, x"00", NullAddr&PadT, x"00", x"00", x"00000000"),
(NullTag, x"00", NullTag, x"00", NullAddr&PadT, x"00", x"00", x"00000000"),
(NullTag, x"00", NullTag, x"00", NullAddr&PadT, x"00", x"00", x"00000000"),
(NullTag, x"00", NullTag, x"00", NullAddr&PadT, x"00", x"00", x"00000000"),
(NullTag, x"00", NullTag, x"00", NullAddr&PadT, x"00", x"00", x"00000000"),
(NullTag, x"00", NullTag, x"00", NullAddr&PadT, x"00", x"00", x"00000000"),
(NullTag, x"00", NullTag, x"00", NullAddr&PadT, x"00", x"00", x"00000000"),
(NullTag, x"00", NullTag, x"00", NullAddr&PadT, x"00", x"00", x"00000000"),
(NullTag, x"00", NullTag, x"00", NullAddr&PadT, x"00", x"00", x"00000000"),
(NullTag, x"00", NullTag, x"00", NullAddr&PadT, x"00", x"00", x"00000000"),
(InMWidth0Tag, x"00", NullTag, x"00", NullAddr&PadT, x"00", x"00", x"0000000B") -- hide this tag here until we find a better way
);
constant PinDesc : PinDescType :
-- Base func sec unit sec func sec pin
--
IOPortTag & x"00" & InMTag & InMData0Pin, -- I/O 00 embedded 7I96 Simple I/O
IOPortTag & x"00" & InMTag & InMData1Pin, -- I/O 01
IOPortTag & x"00" & InMTag & InMData2Pin, -- I/O 02
IOPortTag & x"00" & InMTag & InMData3Pin, -- I/O 03
IOPortTag & x"00" & InMTag & InMData4Pin, -- I/O 04
IOPortTag & x"00" & InMTag & InMData5Pin, -- I/O 05
IOPortTag & x"00" & InMTag & InMData6Pin, -- I/O 06
IOPortTag & x"00" & InMTag & InMData7Pin, -- I/O 07
IOPortTag & x"00" & InMTag & InMData8Pin, -- I/O 08
IOPortTag & x"00" & InMTag & InMData9Pin, -- I/O 09
IOPortTag & x"00" & InMTag & InMDataAPin, -- I/O 10
IOPortTag & x"00" & XfrmrOutTag & XfrmrOut0Pin, -- I/O 11
IOPortTag & x"00" & XfrmrOutTag & XfrmrOut1Pin, -- I/O 12
IOPortTag & x"00" & XfrmrOutTag & XfrmrOut2Pin, -- I/O 13
IOPortTag & x"00" & XfrmrOutTag & XfrmrOut3Pin, -- I/O 14
IOPortTag & x"00" & OutMTag & OutMData4Pin, -- I/O 15
IOPortTag & x"00" & OutMTag & OutMData5Pin, -- I/O 16
IOPortTag & x"00" & StepGenTag & StepGenStepPin, -- I/O 17 embedded 7I96 Step/Dir/Enc/Serial
IOPortTag & x"00" & StepGenTag & StepGenDirPin, -- I/O 18
IOPortTag & x"01" & StepGenTag & StepGenStepPin, -- I/O 19
IOPortTag & x"01" & StepGenTag & StepGenDirPin, -- I/O 20
IOPortTag & x"02" & StepGenTag & StepGenStepPin, -- I/O 21
IOPortTag & x"02" & StepGenTag & StepGenDirPin, -- I/O 22
IOPortTag & x"03" & StepGenTag & StepGenStepPin, -- I/O 23
IOPortTag & x"03" & StepGenTag & StepGenDirPin, -- I/O 24
IOPortTag & x"04" & StepGenTag & StepGenStepPin, -- I/O 25
IOPortTag & x"04" & StepGenTag & StepGenDirPin, -- I/O 26
IOPortTag & x"00" & QCountTag & QCountQAPin, -- I/O 27
IOPortTag & x"00" & QCountTag & QCountQBPin, -- I/O 28
IOPortTag & x"00" & QCountTag & QCountIdxPin, -- I/O 29
IOPortTag & x"00" & SSerialTag & SSerialRX0Pin, -- I/O 30
IOPortTag & x"00" & SSerialTag & SSerialTX0Pin, -- I/O 31
IOPortTag & x"00" & SSerialTag & SSerialTXEn0Pin, -- I/O 32
IOPortTag & x"00" & XfrmrOutTag & XfrmrRefPin, -- I/O 33
-- Expansion port
IOPortTag & x"01" & QCountTag & QCountQAPin, -- I/O 34 PIN 1
IOPortTag & x"01" & QCountTag & QCountQBPin, -- I/O 35 PIN 14
IOPortTag & x"02" & QCountTag & QCountQAPin, -- I/O 36 PIN 2
IOPortTag & x"02" & QCountTag & QCountQBPin, -- I/O 37 PIN 15
IOPortTag & x"03" & QCountTag & QCountQAPin, -- I/O 38 PIN 3
IOPortTag & x"03" & QCountTag & QCountQBPin, -- I/O 39 PIN 16
IOPortTag & x"04" & QCountTag & QCountQAPin, -- I/O 40 PIN 4
IOPortTag & x"04" & QCountTag & QCountQBPin, -- I/O 41 PIN 17
IOPortTag & x"05" & QCountTag & QCountQAPin, -- I/O 42 PIN 5
IOPortTag & x"05" & QCountTag & QCountQBPin, -- I/O 43 PIN 18
IOPortTag & x"00" & PktUARTTTag & PktUTDataPin, -- I/O 44 PIN 6
IOPortTag & x"00" & PktUARTRTag & PktURDataPin, -- I/O 45 PIN 19
IOPortTag & x"00" & NullTag & x"00", -- I/O 46 PIN 9
IOPortTag & x"00" & NullTag & x"00", -- I/O 47 PIN 10
IOPortTag & x"00" & NullTag & x"00", -- I/O 48 PIN 11
IOPortTag & x"00" & NullTag & x"00", -- I/O 49 PIN 12
IOPortTag & x"00" & NullTag & x"00", -- I/O 50 PIN 13
LIOPortTag & x"00" & PWMTag & PWMAOutPin, -- 7I96S analog out PWM
LIOPortTag & x"00" & PWMTag & PWMBDirPin, -- dummy for now
emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,
emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,
emptypin,emptypin,emptypin,emptypin,emptypin,
emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,emptypin, -- added for IDROM v3
emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,
emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,
emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,
emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,
emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,
emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,
emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,
emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,emptypin);
end package PIN_7I96SD_Test_51;
and the output of the mesaflash --read
Configuration Name: HOSTMOT2
General configuration information:
BoardName : MESA7I96
FPGA Size: 20 KGates
FPGA Pins: 256
Number of IO Ports: 3
Width of one I/O port: 17
Clock Low frequency: 100.0000 MHz
Clock High frequency: 160.0000 MHz
IDROM Type: 3
Instance Stride 0: 4
Instance Stride 1: 64
Register Stride 0: 256
Register Stride 1: 256
Modules in configuration:
Module: DPLL
There are 1 of DPLL in configuration
Version: 0
Registers: 7
BaseAddress: 7000
ClockFrequency: 100.000 MHz
Register Stride: 256 bytes
Instance Stride: 4 bytes
Module: WatchDog
There are 1 of WatchDog in configuration
Version: 0
Registers: 3
BaseAddress: 0C00
ClockFrequency: 100.000 MHz
Register Stride: 256 bytes
Instance Stride: 4 bytes
Module: IOPort
There are 3 of IOPort in configuration
Version: 0
Registers: 5
BaseAddress: 1000
ClockFrequency: 100.000 MHz
Register Stride: 256 bytes
Instance Stride: 4 bytes
Module: OutM
There are 1 of OutM in configuration
Version: 0
Registers: 1
BaseAddress: B000
ClockFrequency: 100.000 MHz
Register Stride: 256 bytes
Instance Stride: 4 bytes
Module: PWM
There are 1 of PWM in configuration
Version: 0
Registers: 5
BaseAddress: 4100
ClockFrequency: 160.000 MHz
Register Stride: 256 bytes
Instance Stride: 4 bytes
Module: StepGen
There are 5 of StepGen in configuration
Version: 2
Registers: 10
BaseAddress: 2000
ClockFrequency: 100.000 MHz
Register Stride: 256 bytes
Instance Stride: 4 bytes
Module: QCount
There are 6 of QCount in configuration
Version: 2
Registers: 5
BaseAddress: 3000
ClockFrequency: 100.000 MHz
Register Stride: 256 bytes
Instance Stride: 4 bytes
Module: SSerial
There are 1 of SSerial in configuration
Version: 0
Registers: 6
BaseAddress: 5B00
ClockFrequency: 100.000 MHz
Register Stride: 256 bytes
Instance Stride: 64 bytes
Module: SSR
There are 1 of SSR in configuration
Version: 0
Registers: 2
BaseAddress: 7D00
ClockFrequency: 100.000 MHz
Register Stride: 256 bytes
Instance Stride: 4 bytes
Module: InM
There are 1 of InM in configuration
Version: 0
Registers: 5
BaseAddress: 8500
ClockFrequency: 100.000 MHz
Register Stride: 256 bytes
Instance Stride: 4 bytes
Module: LED
There are 1 of LED in configuration
Version: 0
Registers: 1
BaseAddress: 0200
ClockFrequency: 100.000 MHz
Register Stride: 256 bytes
Instance Stride: 4 bytes
Module: PktUARTTX
There are 1 of PktUARTTX in configuration
Version: 2
Registers: 4
BaseAddress: 6100
ClockFrequency: 100.000 MHz
Register Stride: 256 bytes
Instance Stride: 4 bytes
Module: PktUARTRX
There are 1 of PktUARTRX in configuration
Version: 2
Registers: 4
BaseAddress: 6500
ClockFrequency: 100.000 MHz
Register Stride: 256 bytes
Instance Stride: 4 bytes
Configuration pin-out:
IO Connections for TB3 -> 7I96_0
Pin# I/O Pri. func Sec. func Chan Sec. Pin func Sec. Pin Dir
TB3-1 0 IOPort InM 0 Input0_EncA0 (In)
TB3-2 1 IOPort InM 0 Input1_EncB0 (In)
TB3-3 2 IOPort InM 0 Input2_EncA1 (In)
TB3-4 3 IOPort InM 0 Input3_EncB1 (In)
TB3-5 4 IOPort InM 0 Input4_EncA2 (In)
TB3-6 5 IOPort InM 0 Input5_EncB2 (In)
TB3-7 6 IOPort InM 0 Input6_EncA3 (In)
TB3-8 7 IOPort InM 0 Input7_EncB3 (In)
TB3-9 8 IOPort InM 0 Input8 (In)
TB3-10 9 IOPort InM 0 Input9 (In)
TB3-11 10 IOPort InM 0 Input10 (In)
TB3-13,14 11 IOPort SSR 0 Out-00 (Out)
TB3-15,16 12 IOPort SSR 0 Out-01 (Out)
TB3-17,18 13 IOPort SSR 0 Out-02 (Out)
TB3-19,20 14 IOPort SSR 0 Out-03 (Out)
TB3-21,22 15 IOPort OutM 0 Output4 (Out)
TB3-23,24 16 IOPort OutM 0 Output5 (Out)
IO Connections for TB1/TB2 -> 7I96_1
Pin# I/O Pri. func Sec. func Chan Sec. Pin func Sec. Pin Dir
TB1-2,3 17 IOPort StepGen 0 Step/Table1 (Out)
TB1-4,5 18 IOPort StepGen 0 Dir/Table2 (Out)
TB1-8,9 19 IOPort StepGen 1 Step/Table1 (Out)
TB1-10,11 20 IOPort StepGen 1 Dir/Table2 (Out)
TB1-14,15 21 IOPort StepGen 2 Step/Table1 (Out)
TB1-16,17 22 IOPort StepGen 2 Dir/Table2 (Out)
TB1-20,21 23 IOPort StepGen 3 Step/Table1 (Out)
TB1-22,23 24 IOPort StepGen 3 Dir/Table2 (Out)
TB2-2,3 25 IOPort StepGen 4 Step/Table1 (Out)
TB2-4,5 26 IOPort StepGen 4 Dir/Table2 (Out)
TB2-7,8 27 IOPort QCount 0 Quad-A (In)
TB2-10,11 28 IOPort QCount 0 Quad-B (In)
TB2-13,14 29 IOPort QCount 0 Quad-IDX (In)
TB2-16,17 30 IOPort SSerial 0 RXData0 (In)
TB2-18,19 31 IOPort SSerial 0 TXData0 (Out)
Internal-TXEn 32 IOPort SSerial 0 TXEn0 (Out)
Internal 33 IOPort SSR 0 AC Ref (Out)
IO Connections for P1 -> 7I96_2
Pin# I/O Pri. func Sec. func Chan Sec. Pin func Sec. Pin Dir
P1-01/DB25-01 34 IOPort QCount 1 Quad-A (In)
P1-02/DB25-14 35 IOPort QCount 1 Quad-B (In)
P1-03/DB25-02 36 IOPort QCount 2 Quad-A (In)
P1-04/DB25-15 37 IOPort QCount 2 Quad-B (In)
P1-05/DB25-03 38 IOPort QCount 3 Quad-A (In)
P1-06/DB25-16 39 IOPort QCount 3 Quad-B (In)
P1-07/DB25-04 40 IOPort QCount 4 Quad-A (In)
P1-08/DB25-17 41 IOPort QCount 4 Quad-B (In)
P1-09/DB25-05 42 IOPort QCount 5 Quad-A (In)
P1-11/DB25-06 43 IOPort QCount 5 Quad-B (In)
P1-13/DB25-07 44 IOPort PktUARTTX 0 TXData (Out)
P1-15/DB25-08 45 IOPort PktUARTRX 0 RXData (In)
P1-17/DB25-09 46 IOPort None
P1-19/DB25-10 47 IOPort None
P1-21/DB25-11 48 IOPort None
P1-23/DB25-12 49 IOPort None
P1-25/DB25-13 50 IOPort None
then i hooked my osciloscope between ch1 gnd - pin7 / ch2 gnd - pin8
and tried Andy Pugh's bash script found in HM2_PKTUART after adding the s for the 7I96s
# First setup the DDR and Alt Source regs for the 7I96
mesaflash --device 7i96 --addr 10.10.10.10 --wpo 0x1100=0x1F800
mesaflash --device 7i96 --addr 10.10.10.10 --wpo 0x1104=0x1C3FF
mesaflash --device 7i96 --addr 10.10.10.10 --wpo 0x1200=0x1F800
mesaflash --device 7i96 --addr 10.10.10.10 --wpo 0x1204=0x1C3FF
# Next set the baud rate DDS's for 9600 baud
mesaflash --device 7i96 --addr 10.10.10.10 --wpo 0x6300=0x65
mesaflash --device 7i96 --addr 10.10.10.10 --wpo 0x6700=0x65
# setup the TX and RX mode registers
mesaflash --device 7i96 --addr 10.10.10.10 --wpo 0x6400=0x00062840
mesaflash --device 7i96 --addr 10.10.10.10 --wpo 0x6800=0x3FC61408
# Reset the TX and RX UARTS
mesaflash --device 7i96 --addr 10.10.10.10 --wpo 0x6400=0x80010000
mesaflash --device 7i96 --addr 10.10.10.10 --wpo 0x6800=0x80010000
# load 7 bytes of data into the TX UART
mesaflash --device 7i96 --addr 10.10.10.10 --wpo 0x6100=0x54535251
mesaflash --device 7i96 --addr 10.10.10.10 --wpo 0x6100=0x58575655
mesaflash --device 7i96 --addr 10.10.10.10 --wpo 0x6100=0x64636261
mesaflash --device 7i96 --addr 10.10.10.10 --wpo 0x6100=0x68676665
# Command the TX UART to send 8 bytes twice
mesaflash --device 7i96 --addr 10.10.10.10 --wpo 0x6200=0x08
mesaflash --device 7i96 --addr 10.10.10.10 --wpo 0x6200=0x08
sleep .1
# display the RX mode reg, RX count, and the data
mesaflash --device 7i96 --addr 10.10.10.10 --rpo 0x6800
mesaflash --device 7i96 --addr 10.10.10.10 --rpo 0x6600
mesaflash --device 7i96 --addr 10.10.10.10 --rpo 0x6500
mesaflash --device 7i96 --addr 10.10.10.10 --rpo 0x6500
mesaflash --device 7i96 --addr 10.10.10.10 --rpo 0x6800
mesaflash --device 7i96 --addr 10.10.10.10 --rpo 0x6600
mesaflash --device 7i96 --addr 10.10.10.10 --rpo 0x6500
mesaflash --device 7i96 --addr 10.10.10.10 --rpo 0x6500
Nothing -- constant 5V on both channels
pls advice
library IEEE;
use IEEE.std_logic_1164.all; -- defines std_logic types
use IEEE.STD_LOGIC_ARITH.ALL;
use IEEE.STD_LOGIC_UNSIGNED.ALL;
-- Copyright (C) 2007, Peter C. Wallace, Mesa Electronics
-- www.mesanet.com
--
-- This program is is licensed under a disjunctive dual license giving you
-- the choice of one of the two following sets of free software/open source
-- licensing terms:
--
-- * GNU General Public License (GPL), version 2.0 or later
-- * 3-clause BSD License
--
--
-- The GNU GPL License:
--
-- This program is free software; you can redistribute it and/or modify
-- it under the terms of the GNU General Public License as published by
-- the Free Software Foundation; either version 2 of the License, or
-- (at your option) any later version.
--
-- This program is distributed in the hope that it will be useful,
-- but WITHOUT ANY WARRANTY; without even the implied warranty of
-- MERCHANTABILITY or FITNESS FOR A PARTICULAR PURPOSE. See the
-- GNU General Public License for more details.
--
-- You should have received a copy of the GNU General Public License
-- along with this program; if not, write to the Free Software
-- Foundation, Inc., 51 Franklin St, Fifth Floor, Boston, MA 02110-1301 USA
--
--
-- The 3-clause BSD License:
--
-- Redistribution and use in source and binary forms, with or without
-- modification, are permitted provided that the following conditions
-- are met:
--
-- * Redistributions of source code must retain the above copyright
-- notice, this list of conditions and the following disclaimer.
--
-- * Redistributions in binary form must reproduce the above
-- copyright notice, this list of conditions and the following
-- disclaimer in the documentation and/or other materials
-- provided with the distribution.
--
-- * Neither the name of Mesa Electronics nor the names of its
-- contributors may be used to endorse or promote products
-- derived from this software without specific prior written
-- permission.
--
--
-- Disclaimer:
--
-- THIS SOFTWARE IS PROVIDED BY THE COPYRIGHT HOLDERS AND CONTRIBUTORS
-- "AS IS" AND ANY EXPRESS OR IMPLIED WARRANTIES, INCLUDING, BUT NOT
-- LIMITED TO, THE IMPLIED WARRANTIES OF MERCHANTABILITY AND FITNESS
-- FOR A PARTICULAR PURPOSE ARE DISCLAIMED. IN NO EVENT SHALL THE
-- COPYRIGHT OWNER OR CONTRIBUTORS BE LIABLE FOR ANY DIRECT, INDIRECT,
-- INCIDENTAL, SPECIAL, EXEMPLARY, OR CONSEQUENTIAL DAMAGES (INCLUDING,
-- BUT NOT LIMITED TO, PROCUREMENT OF SUBSTITUTE GOODS OR SERVICES;
-- LOSS OF USE, DATA, OR PROFITS; OR BUSINESS INTERRUPTION) HOWEVER
-- CAUSED AND ON ANY THEORY OF LIABILITY, WHETHER IN CONTRACT, STRICT
-- LIABILITY, OR TORT (INCLUDING NEGLIGENCE OR OTHERWISE) ARISING IN
-- ANY WAY OUT OF THE USE OF THIS SOFTWARE, EVEN IF ADVISED OF THE
-- POSSIBILITY OF SUCH DAMAGE.
--
use work.IDROMConst.all;
package PIN_7I96SD_Test_51 is
constant ModuleID : ModuleIDType :

(HM2DPLLTag, x"00", ClockLowTag, x"01", HM2DPLLBaseRateAddr&PadT, HM2DPLLNumRegs, x"00", HM2DPLLMPBitMask),
(WatchDogTag, x"00", ClockLowTag, x"01", WatchDogTimeAddr&PadT, WatchDogNumRegs, x"00", WatchDogMPBitMask),
(IOPortTag, x"00", ClockLowTag, x"03", PortAddr&PadT, IOPortNumRegs, x"00", IOPortMPBitMask),
(OutMTag, x"00", ClockLowTag, x"01", OutMDataAddr&PadT, OutMNumRegs, x"00", OutMMPBitMask),
(PWMTag, x"00", ClockHighTag, x"01", PWMValAddr&PadT, PWMNumRegs, x"00", PWMMPBitMask),
(StepGenTag, x"02", ClockLowTag, x"05", StepGenRateAddr&PadT, StepGenNumRegs, x"00", StepGenMPBitMask),
(QcountTag, x"02", ClockLowTag, x"06", QcounterAddr&PadT, QCounterNumRegs, x"00", QCounterMPBitMask),
(SSerialTag, x"00", ClockLowTag, x"01", SSerialCommandAddr&PadT, SSerialNumRegs, x"10", SSerialMPBitMask),
(XFrmrOutTag, x"00", ClockLowTag, x"01", XFrmrDataAddr&PadT, XFrmrNumRegs, x"00", XFrmrMPBitMask ),
(InMTag, x"00", ClockLowTag, x"01", InMControlAddr&PadT, InMNumRegs, x"00", InMMPBitMask),
(LEDTag, x"00", ClockLowTag, x"01", LEDAddr&PadT, LEDNumRegs, x"00", LEDMPBitMask),
(PktUARTTTag, x"02", ClockLowTag, x"01", PktUARTTDataAddr&PadT, PktUARTTNumRegs, x"00", PktUARTTMPBitMask),
(PktUARTRTag, x"02", ClockLowTag, x"01", PktUARTRDataAddr&PadT, PktUARTRNumRegs, x"00", PktUARTRMPBitMask),
(NullTag, x"00", NullTag, x"00", NullAddr&PadT, x"00", x"00", x"00000000"),
(NullTag, x"00", NullTag, x"00", NullAddr&PadT, x"00", x"00", x"00000000"),
(NullTag, x"00", NullTag, x"00", NullAddr&PadT, x"00", x"00", x"00000000"),
(NullTag, x"00", NullTag, x"00", NullAddr&PadT, x"00", x"00", x"00000000"),
(NullTag, x"00", NullTag, x"00", NullAddr&PadT, x"00", x"00", x"00000000"),
(NullTag, x"00", NullTag, x"00", NullAddr&PadT, x"00", x"00", x"00000000"),
(NullTag, x"00", NullTag, x"00", NullAddr&PadT, x"00", x"00", x"00000000"),
(NullTag, x"00", NullTag, x"00", NullAddr&PadT, x"00", x"00", x"00000000"),
(NullTag, x"00", NullTag, x"00", NullAddr&PadT, x"00", x"00", x"00000000"),
(NullTag, x"00", NullTag, x"00", NullAddr&PadT, x"00", x"00", x"00000000"),
(NullTag, x"00", NullTag, x"00", NullAddr&PadT, x"00", x"00", x"00000000"),
(NullTag, x"00", NullTag, x"00", NullAddr&PadT, x"00", x"00", x"00000000"),
(NullTag, x"00", NullTag, x"00", NullAddr&PadT, x"00", x"00", x"00000000"),
(NullTag, x"00", NullTag, x"00", NullAddr&PadT, x"00", x"00", x"00000000"),
(NullTag, x"00", NullTag, x"00", NullAddr&PadT, x"00", x"00", x"00000000"),
(NullTag, x"00", NullTag, x"00", NullAddr&PadT, x"00", x"00", x"00000000"),
(NullTag, x"00", NullTag, x"00", NullAddr&PadT, x"00", x"00", x"00000000"),
(NullTag, x"00", NullTag, x"00", NullAddr&PadT, x"00", x"00", x"00000000"),
(InMWidth0Tag, x"00", NullTag, x"00", NullAddr&PadT, x"00", x"00", x"0000000B") -- hide this tag here until we find a better way
);
constant PinDesc : PinDescType :

-- Base func sec unit sec func sec pin
--
IOPortTag & x"00" & InMTag & InMData0Pin, -- I/O 00 embedded 7I96 Simple I/O
IOPortTag & x"00" & InMTag & InMData1Pin, -- I/O 01
IOPortTag & x"00" & InMTag & InMData2Pin, -- I/O 02
IOPortTag & x"00" & InMTag & InMData3Pin, -- I/O 03
IOPortTag & x"00" & InMTag & InMData4Pin, -- I/O 04
IOPortTag & x"00" & InMTag & InMData5Pin, -- I/O 05
IOPortTag & x"00" & InMTag & InMData6Pin, -- I/O 06
IOPortTag & x"00" & InMTag & InMData7Pin, -- I/O 07
IOPortTag & x"00" & InMTag & InMData8Pin, -- I/O 08
IOPortTag & x"00" & InMTag & InMData9Pin, -- I/O 09
IOPortTag & x"00" & InMTag & InMDataAPin, -- I/O 10
IOPortTag & x"00" & XfrmrOutTag & XfrmrOut0Pin, -- I/O 11
IOPortTag & x"00" & XfrmrOutTag & XfrmrOut1Pin, -- I/O 12
IOPortTag & x"00" & XfrmrOutTag & XfrmrOut2Pin, -- I/O 13
IOPortTag & x"00" & XfrmrOutTag & XfrmrOut3Pin, -- I/O 14
IOPortTag & x"00" & OutMTag & OutMData4Pin, -- I/O 15
IOPortTag & x"00" & OutMTag & OutMData5Pin, -- I/O 16
IOPortTag & x"00" & StepGenTag & StepGenStepPin, -- I/O 17 embedded 7I96 Step/Dir/Enc/Serial
IOPortTag & x"00" & StepGenTag & StepGenDirPin, -- I/O 18
IOPortTag & x"01" & StepGenTag & StepGenStepPin, -- I/O 19
IOPortTag & x"01" & StepGenTag & StepGenDirPin, -- I/O 20
IOPortTag & x"02" & StepGenTag & StepGenStepPin, -- I/O 21
IOPortTag & x"02" & StepGenTag & StepGenDirPin, -- I/O 22
IOPortTag & x"03" & StepGenTag & StepGenStepPin, -- I/O 23
IOPortTag & x"03" & StepGenTag & StepGenDirPin, -- I/O 24
IOPortTag & x"04" & StepGenTag & StepGenStepPin, -- I/O 25
IOPortTag & x"04" & StepGenTag & StepGenDirPin, -- I/O 26
IOPortTag & x"00" & QCountTag & QCountQAPin, -- I/O 27
IOPortTag & x"00" & QCountTag & QCountQBPin, -- I/O 28
IOPortTag & x"00" & QCountTag & QCountIdxPin, -- I/O 29
IOPortTag & x"00" & SSerialTag & SSerialRX0Pin, -- I/O 30
IOPortTag & x"00" & SSerialTag & SSerialTX0Pin, -- I/O 31
IOPortTag & x"00" & SSerialTag & SSerialTXEn0Pin, -- I/O 32
IOPortTag & x"00" & XfrmrOutTag & XfrmrRefPin, -- I/O 33
-- Expansion port
IOPortTag & x"01" & QCountTag & QCountQAPin, -- I/O 34 PIN 1
IOPortTag & x"01" & QCountTag & QCountQBPin, -- I/O 35 PIN 14
IOPortTag & x"02" & QCountTag & QCountQAPin, -- I/O 36 PIN 2
IOPortTag & x"02" & QCountTag & QCountQBPin, -- I/O 37 PIN 15
IOPortTag & x"03" & QCountTag & QCountQAPin, -- I/O 38 PIN 3
IOPortTag & x"03" & QCountTag & QCountQBPin, -- I/O 39 PIN 16
IOPortTag & x"04" & QCountTag & QCountQAPin, -- I/O 40 PIN 4
IOPortTag & x"04" & QCountTag & QCountQBPin, -- I/O 41 PIN 17
IOPortTag & x"05" & QCountTag & QCountQAPin, -- I/O 42 PIN 5
IOPortTag & x"05" & QCountTag & QCountQBPin, -- I/O 43 PIN 18
IOPortTag & x"00" & PktUARTTTag & PktUTDataPin, -- I/O 44 PIN 6
IOPortTag & x"00" & PktUARTRTag & PktURDataPin, -- I/O 45 PIN 19
IOPortTag & x"00" & NullTag & x"00", -- I/O 46 PIN 9
IOPortTag & x"00" & NullTag & x"00", -- I/O 47 PIN 10
IOPortTag & x"00" & NullTag & x"00", -- I/O 48 PIN 11
IOPortTag & x"00" & NullTag & x"00", -- I/O 49 PIN 12
IOPortTag & x"00" & NullTag & x"00", -- I/O 50 PIN 13
LIOPortTag & x"00" & PWMTag & PWMAOutPin, -- 7I96S analog out PWM
LIOPortTag & x"00" & PWMTag & PWMBDirPin, -- dummy for now
emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,
emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,
emptypin,emptypin,emptypin,emptypin,emptypin,
emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,emptypin, -- added for IDROM v3
emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,
emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,
emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,
emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,
emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,
emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,
emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,
emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,emptypin,emptypin);
end package PIN_7I96SD_Test_51;
and the output of the mesaflash --read
Configuration Name: HOSTMOT2
General configuration information:
BoardName : MESA7I96
FPGA Size: 20 KGates
FPGA Pins: 256
Number of IO Ports: 3
Width of one I/O port: 17
Clock Low frequency: 100.0000 MHz
Clock High frequency: 160.0000 MHz
IDROM Type: 3
Instance Stride 0: 4
Instance Stride 1: 64
Register Stride 0: 256
Register Stride 1: 256
Modules in configuration:
Module: DPLL
There are 1 of DPLL in configuration
Version: 0
Registers: 7
BaseAddress: 7000
ClockFrequency: 100.000 MHz
Register Stride: 256 bytes
Instance Stride: 4 bytes
Module: WatchDog
There are 1 of WatchDog in configuration
Version: 0
Registers: 3
BaseAddress: 0C00
ClockFrequency: 100.000 MHz
Register Stride: 256 bytes
Instance Stride: 4 bytes
Module: IOPort
There are 3 of IOPort in configuration
Version: 0
Registers: 5
BaseAddress: 1000
ClockFrequency: 100.000 MHz
Register Stride: 256 bytes
Instance Stride: 4 bytes
Module: OutM
There are 1 of OutM in configuration
Version: 0
Registers: 1
BaseAddress: B000
ClockFrequency: 100.000 MHz
Register Stride: 256 bytes
Instance Stride: 4 bytes
Module: PWM
There are 1 of PWM in configuration
Version: 0
Registers: 5
BaseAddress: 4100
ClockFrequency: 160.000 MHz
Register Stride: 256 bytes
Instance Stride: 4 bytes
Module: StepGen
There are 5 of StepGen in configuration
Version: 2
Registers: 10
BaseAddress: 2000
ClockFrequency: 100.000 MHz
Register Stride: 256 bytes
Instance Stride: 4 bytes
Module: QCount
There are 6 of QCount in configuration
Version: 2
Registers: 5
BaseAddress: 3000
ClockFrequency: 100.000 MHz
Register Stride: 256 bytes
Instance Stride: 4 bytes
Module: SSerial
There are 1 of SSerial in configuration
Version: 0
Registers: 6
BaseAddress: 5B00
ClockFrequency: 100.000 MHz
Register Stride: 256 bytes
Instance Stride: 64 bytes
Module: SSR
There are 1 of SSR in configuration
Version: 0
Registers: 2
BaseAddress: 7D00
ClockFrequency: 100.000 MHz
Register Stride: 256 bytes
Instance Stride: 4 bytes
Module: InM
There are 1 of InM in configuration
Version: 0
Registers: 5
BaseAddress: 8500
ClockFrequency: 100.000 MHz
Register Stride: 256 bytes
Instance Stride: 4 bytes
Module: LED
There are 1 of LED in configuration
Version: 0
Registers: 1
BaseAddress: 0200
ClockFrequency: 100.000 MHz
Register Stride: 256 bytes
Instance Stride: 4 bytes
Module: PktUARTTX
There are 1 of PktUARTTX in configuration
Version: 2
Registers: 4
BaseAddress: 6100
ClockFrequency: 100.000 MHz
Register Stride: 256 bytes
Instance Stride: 4 bytes
Module: PktUARTRX
There are 1 of PktUARTRX in configuration
Version: 2
Registers: 4
BaseAddress: 6500
ClockFrequency: 100.000 MHz
Register Stride: 256 bytes
Instance Stride: 4 bytes
Configuration pin-out:
IO Connections for TB3 -> 7I96_0
Pin# I/O Pri. func Sec. func Chan Sec. Pin func Sec. Pin Dir
TB3-1 0 IOPort InM 0 Input0_EncA0 (In)
TB3-2 1 IOPort InM 0 Input1_EncB0 (In)
TB3-3 2 IOPort InM 0 Input2_EncA1 (In)
TB3-4 3 IOPort InM 0 Input3_EncB1 (In)
TB3-5 4 IOPort InM 0 Input4_EncA2 (In)
TB3-6 5 IOPort InM 0 Input5_EncB2 (In)
TB3-7 6 IOPort InM 0 Input6_EncA3 (In)
TB3-8 7 IOPort InM 0 Input7_EncB3 (In)
TB3-9 8 IOPort InM 0 Input8 (In)
TB3-10 9 IOPort InM 0 Input9 (In)
TB3-11 10 IOPort InM 0 Input10 (In)
TB3-13,14 11 IOPort SSR 0 Out-00 (Out)
TB3-15,16 12 IOPort SSR 0 Out-01 (Out)
TB3-17,18 13 IOPort SSR 0 Out-02 (Out)
TB3-19,20 14 IOPort SSR 0 Out-03 (Out)
TB3-21,22 15 IOPort OutM 0 Output4 (Out)
TB3-23,24 16 IOPort OutM 0 Output5 (Out)
IO Connections for TB1/TB2 -> 7I96_1
Pin# I/O Pri. func Sec. func Chan Sec. Pin func Sec. Pin Dir
TB1-2,3 17 IOPort StepGen 0 Step/Table1 (Out)
TB1-4,5 18 IOPort StepGen 0 Dir/Table2 (Out)
TB1-8,9 19 IOPort StepGen 1 Step/Table1 (Out)
TB1-10,11 20 IOPort StepGen 1 Dir/Table2 (Out)
TB1-14,15 21 IOPort StepGen 2 Step/Table1 (Out)
TB1-16,17 22 IOPort StepGen 2 Dir/Table2 (Out)
TB1-20,21 23 IOPort StepGen 3 Step/Table1 (Out)
TB1-22,23 24 IOPort StepGen 3 Dir/Table2 (Out)
TB2-2,3 25 IOPort StepGen 4 Step/Table1 (Out)
TB2-4,5 26 IOPort StepGen 4 Dir/Table2 (Out)
TB2-7,8 27 IOPort QCount 0 Quad-A (In)
TB2-10,11 28 IOPort QCount 0 Quad-B (In)
TB2-13,14 29 IOPort QCount 0 Quad-IDX (In)
TB2-16,17 30 IOPort SSerial 0 RXData0 (In)
TB2-18,19 31 IOPort SSerial 0 TXData0 (Out)
Internal-TXEn 32 IOPort SSerial 0 TXEn0 (Out)
Internal 33 IOPort SSR 0 AC Ref (Out)
IO Connections for P1 -> 7I96_2
Pin# I/O Pri. func Sec. func Chan Sec. Pin func Sec. Pin Dir
P1-01/DB25-01 34 IOPort QCount 1 Quad-A (In)
P1-02/DB25-14 35 IOPort QCount 1 Quad-B (In)
P1-03/DB25-02 36 IOPort QCount 2 Quad-A (In)
P1-04/DB25-15 37 IOPort QCount 2 Quad-B (In)
P1-05/DB25-03 38 IOPort QCount 3 Quad-A (In)
P1-06/DB25-16 39 IOPort QCount 3 Quad-B (In)
P1-07/DB25-04 40 IOPort QCount 4 Quad-A (In)
P1-08/DB25-17 41 IOPort QCount 4 Quad-B (In)
P1-09/DB25-05 42 IOPort QCount 5 Quad-A (In)
P1-11/DB25-06 43 IOPort QCount 5 Quad-B (In)
P1-13/DB25-07 44 IOPort PktUARTTX 0 TXData (Out)
P1-15/DB25-08 45 IOPort PktUARTRX 0 RXData (In)
P1-17/DB25-09 46 IOPort None
P1-19/DB25-10 47 IOPort None
P1-21/DB25-11 48 IOPort None
P1-23/DB25-12 49 IOPort None
P1-25/DB25-13 50 IOPort None
then i hooked my osciloscope between ch1 gnd - pin7 / ch2 gnd - pin8
and tried Andy Pugh's bash script found in HM2_PKTUART after adding the s for the 7I96s
# First setup the DDR and Alt Source regs for the 7I96
mesaflash --device 7i96 --addr 10.10.10.10 --wpo 0x1100=0x1F800
mesaflash --device 7i96 --addr 10.10.10.10 --wpo 0x1104=0x1C3FF
mesaflash --device 7i96 --addr 10.10.10.10 --wpo 0x1200=0x1F800
mesaflash --device 7i96 --addr 10.10.10.10 --wpo 0x1204=0x1C3FF
# Next set the baud rate DDS's for 9600 baud
mesaflash --device 7i96 --addr 10.10.10.10 --wpo 0x6300=0x65
mesaflash --device 7i96 --addr 10.10.10.10 --wpo 0x6700=0x65
# setup the TX and RX mode registers
mesaflash --device 7i96 --addr 10.10.10.10 --wpo 0x6400=0x00062840
mesaflash --device 7i96 --addr 10.10.10.10 --wpo 0x6800=0x3FC61408
# Reset the TX and RX UARTS
mesaflash --device 7i96 --addr 10.10.10.10 --wpo 0x6400=0x80010000
mesaflash --device 7i96 --addr 10.10.10.10 --wpo 0x6800=0x80010000
# load 7 bytes of data into the TX UART
mesaflash --device 7i96 --addr 10.10.10.10 --wpo 0x6100=0x54535251
mesaflash --device 7i96 --addr 10.10.10.10 --wpo 0x6100=0x58575655
mesaflash --device 7i96 --addr 10.10.10.10 --wpo 0x6100=0x64636261
mesaflash --device 7i96 --addr 10.10.10.10 --wpo 0x6100=0x68676665
# Command the TX UART to send 8 bytes twice
mesaflash --device 7i96 --addr 10.10.10.10 --wpo 0x6200=0x08
mesaflash --device 7i96 --addr 10.10.10.10 --wpo 0x6200=0x08
sleep .1
# display the RX mode reg, RX count, and the data
mesaflash --device 7i96 --addr 10.10.10.10 --rpo 0x6800
mesaflash --device 7i96 --addr 10.10.10.10 --rpo 0x6600
mesaflash --device 7i96 --addr 10.10.10.10 --rpo 0x6500
mesaflash --device 7i96 --addr 10.10.10.10 --rpo 0x6500
mesaflash --device 7i96 --addr 10.10.10.10 --rpo 0x6800
mesaflash --device 7i96 --addr 10.10.10.10 --rpo 0x6600
mesaflash --device 7i96 --addr 10.10.10.10 --rpo 0x6500
mesaflash --device 7i96 --addr 10.10.10.10 --rpo 0x6500
Nothing -- constant 5V on both channels
pls advice
Please Log in to join the conversation.
2 years 1 month ago #310714
by PCW
Replied by PCW on topic Mesa 7i96s with 5 encoders and Modbus
I would try creating a .mod file and doing an actual test
Please Log in to join the conversation.
2 years 1 month ago #310718
by nartburg
Replied by nartburg on topic Mesa 7i96s with 5 encoders and Modbus
Created .mod file
#define MAX_MSG_LEN 16
#define DEBUG 3
static const hm2_modbus_chan_descriptor_t channels[] = {
{HAL_S32, 6, 0x000, 1,"write"},
{HAL_S32, 3, 0x100, 1,"read"},
};
loading in .hal file:
.
.
.
addf pid.z.do-pid-calcs servo-thread
addf pid.s.do-pid-calcs servo-thread
addf [HMOT](CARD0).write servo-thread
setp [HMOT](CARD0).dpll.01.timer-us -50
setp [HMOT](CARD0).stepgen.timer-number 1
loadrt my-vfd ports=hm2_7i96s.0.pktuart.0
addf my-vfd.00 servo-thread
# external output signals
# external input signals
# --- MAX-HOME-Z ---
net max-home-z <= [HMOT](CARD0).inm.00.input-00-not
.
.
.
Output:
.
.
WAIT_FOR_DATA_FRAME - rxmode = 16000F0C
1002 TIMEOUT_RESET 3
START txstaus = 00001460 rxstatus = 16000F0C
building packet 6 0 start pin 0
building packet 3 100 start pin 1
Sending to hm2_7i96s.0.pktuart.0 8 bytes 01 03 01 0000 01 85 F6
WAIT_FOR_SENDBEGIN RX 1460 TX 16000F0C
WAIT_FOR_SEND_COMPLETE RX 16000F0C TX 2014E0
.
.
.
While the oszi is still showing a constant 5Volts
#define MAX_MSG_LEN 16
#define DEBUG 3
static const hm2_modbus_chan_descriptor_t channels[] = {
{HAL_S32, 6, 0x000, 1,"write"},
{HAL_S32, 3, 0x100, 1,"read"},
};
loading in .hal file:
.
.
.
addf pid.z.do-pid-calcs servo-thread
addf pid.s.do-pid-calcs servo-thread
addf [HMOT](CARD0).write servo-thread
setp [HMOT](CARD0).dpll.01.timer-us -50
setp [HMOT](CARD0).stepgen.timer-number 1
loadrt my-vfd ports=hm2_7i96s.0.pktuart.0
addf my-vfd.00 servo-thread
# external output signals
# external input signals
# --- MAX-HOME-Z ---
net max-home-z <= [HMOT](CARD0).inm.00.input-00-not
.
.
.
Output:
.
.
WAIT_FOR_DATA_FRAME - rxmode = 16000F0C
1002 TIMEOUT_RESET 3
START txstaus = 00001460 rxstatus = 16000F0C
building packet 6 0 start pin 0
building packet 3 100 start pin 1
Sending to hm2_7i96s.0.pktuart.0 8 bytes 01 03 01 0000 01 85 F6
WAIT_FOR_SENDBEGIN RX 1460 TX 16000F0C
WAIT_FOR_SEND_COMPLETE RX 16000F0C TX 2014E0
.
.
.
While the oszi is still showing a constant 5Volts
Please Log in to join the conversation.
2 years 1 month ago #310720
by PCW
Replied by PCW on topic Mesa 7i96s with 5 encoders and Modbus
I would try standard 7I96S+PktUART firmware (using
the TB2 RS-485 interface) and then work backwards to
find out where the issue is.
the TB2 RS-485 interface) and then work backwards to
find out where the issue is.
Please Log in to join the conversation.
2 years 1 month ago #310765
by nartburg
Replied by nartburg on topic Mesa 7i96s with 5 encoders and Modbus
So tried tb2 Rs-485 interface with PIN_7I96SD_PKT.vhd and
1 GND
2 RX+,TX+ 390 Ohm pulldown to GND (1)
3 RX-,TX-
4 RX+,TX+
5 RX-,TX1- 390 Ohm pullup to 5V (6)
6 +5V
same,same but different:
NO signal on the bus;
but rxmode changed from 16000F0c to 1600F8E
1 GND
2 RX+,TX+ 390 Ohm pulldown to GND (1)
3 RX-,TX-
4 RX+,TX+
5 RX-,TX1- 390 Ohm pullup to 5V (6)
6 +5V
same,same but different:
NO signal on the bus;
but rxmode changed from 16000F0c to 1600F8E
Please Log in to join the conversation.
2 years 1 month ago #310770
by PCW
Replied by PCW on topic Mesa 7i96s with 5 encoders and Modbus
I would try the standard firmware with the sample relay .mod file since that is known to work
I would also use 7i96sd_pktv2.bin since its the latest (though both have been tested)
I would also use 7i96sd_pktv2.bin since its the latest (though both have been tested)
Please Log in to join the conversation.
2 years 1 month ago #310779
by nartburg
Replied by nartburg on topic Mesa 7i96s with 5 encoders and Modbus
where to find relay.mod?
Please Log in to join the conversation.
2 years 1 month ago #310780
by PCW
Replied by PCW on topic Mesa 7i96s with 5 encoders and Modbus
Not sure where is in in a normal install but in the source it's:
src/hal/drivers/mesa-hostmot2/modbus/relayboard.mod
src/hal/drivers/mesa-hostmot2/modbus/relayboard.mod
Please Log in to join the conversation.