Strange stepgen behaviour with 7i95t_1pktv2d firmware

More
1 year 11 months ago #313817 by Finngineering
Thank you for investing time in this. Of course, if the issue is not reproducible for you, the "return on investment" for you looking for the cause is very low.

I have done a bit of investigation myself, by looking at the network traffic. There will be quite a bit of information here, but I would say the conclusion is that the jump in position-fb is not visible in the packets from the 7i95T. In other words, the cause almost has to be somewhere on the linuxcnc side.

I changed my config to enable some debugging information and reducing the "modules" as much as possible (while still having the jump in position-fb):
Code:
loadrt threads name1=servo-thread period1=1000000 loadrt hostmot2 debug_module_descriptors=1 debug_modules=1 loadrt hm2_eth board_ip="10.10.10.10" config="num_stepgens=5 num_ssrs=0 num_inmuxs=0 num_leds=0" # This causes jumps in hm2_7i95.0.stepgen.00.position-fb addf hm2_7i95.0.read          servo-thread addf hm2_7i95.0.write         servo-thread loadrt maho_vfd ports=hm2_7i95.0.pktuart.0 addf maho_vfd.00 servo-thread start

The console output from starting the script is:
Code:
$ halcmd -f pktuart_bug.hal  Note: Using POSIX realtime hm2: loading Mesa HostMot2 driver version 0.15 hm2_eth: loading Mesa AnyIO HostMot2 ethernet driver version 0.2 hm2_eth: 10.10.10.10: INFO: Hardware address (MAC): 00:60:1b:15:80:02 hm2_eth: discovered 7I95T hm2/hm2_7i95.0: Low Level init 0.15 hm2/hm2_7i95.0: Module Descriptor 0 at 0x0440: hm2/hm2_7i95.0:     General Function Tag: 26 (Hostmot2 DPLL) hm2/hm2_7i95.0:     Version: 0 hm2/hm2_7i95.0:     Clock Tag: 1 (100.000 MHz) hm2/hm2_7i95.0:     Instances: 1 hm2/hm2_7i95.0:     Base Address: 0x7000 hm2/hm2_7i95.0:     -- Num Registers: 7 hm2/hm2_7i95.0:     Register Stride: 0x00000100 hm2/hm2_7i95.0:     -- Instance Stride: 0x00000004 hm2/hm2_7i95.0:     -- Multiple Registers: 0x00000000 hm2/hm2_7i95.0: Module Descriptor 1 at 0x044C: hm2/hm2_7i95.0:     General Function Tag: 2 (Watchdog) hm2/hm2_7i95.0:     Version: 0 hm2/hm2_7i95.0:     Clock Tag: 1 (100.000 MHz) hm2/hm2_7i95.0:     Instances: 1 hm2/hm2_7i95.0:     Base Address: 0x0C00 hm2/hm2_7i95.0:     -- Num Registers: 3 hm2/hm2_7i95.0:     Register Stride: 0x00000100 hm2/hm2_7i95.0:     -- Instance Stride: 0x00000004 hm2/hm2_7i95.0:     -- Multiple Registers: 0x00000000 hm2/hm2_7i95.0: Module Descriptor 2 at 0x0458: hm2/hm2_7i95.0:     General Function Tag: 3 (IOPort) hm2/hm2_7i95.0:     Version: 0 hm2/hm2_7i95.0:     Clock Tag: 1 (100.000 MHz) hm2/hm2_7i95.0:     Instances: 2 hm2/hm2_7i95.0:     Base Address: 0x1000 hm2/hm2_7i95.0:     -- Num Registers: 5 hm2/hm2_7i95.0:     Register Stride: 0x00000100 hm2/hm2_7i95.0:     -- Instance Stride: 0x00000004 hm2/hm2_7i95.0:     -- Multiple Registers: 0x0000001F hm2/hm2_7i95.0: Module Descriptor 3 at 0x0464: hm2/hm2_7i95.0:     General Function Tag: 12 (Muxed Encoder) hm2/hm2_7i95.0:     Version: 4 hm2/hm2_7i95.0:     Clock Tag: 1 (100.000 MHz) hm2/hm2_7i95.0:     Instances: 6 hm2/hm2_7i95.0:     Base Address: 0x3600 hm2/hm2_7i95.0:     -- Num Registers: 5 hm2/hm2_7i95.0:     Register Stride: 0x00000100 hm2/hm2_7i95.0:     -- Instance Stride: 0x00000004 hm2/hm2_7i95.0:     -- Multiple Registers: 0x00000003 hm2/hm2_7i95.0: Module Descriptor 4 at 0x0470: hm2/hm2_7i95.0:     General Function Tag: 13 (Muxed Encoder Select) hm2/hm2_7i95.0:     Version: 0 hm2/hm2_7i95.0:     Clock Tag: 1 (100.000 MHz) hm2/hm2_7i95.0:     Instances: 1 hm2/hm2_7i95.0:     Base Address: 0x0000 hm2/hm2_7i95.0:     -- Num Registers: 0 hm2/hm2_7i95.0:     Register Stride: 0x00000100 hm2/hm2_7i95.0:     -- Instance Stride: 0x00000004 hm2/hm2_7i95.0:     -- Multiple Registers: 0x00000000 hm2/hm2_7i95.0: Module Descriptor 5 at 0x047C: hm2/hm2_7i95.0:     General Function Tag: 27 (PktUART Transmit Channel) hm2/hm2_7i95.0:     Version: 2 hm2/hm2_7i95.0:     Clock Tag: 1 (100.000 MHz) hm2/hm2_7i95.0:     Instances: 1 hm2/hm2_7i95.0:     Base Address: 0x6100 hm2/hm2_7i95.0:     -- Num Registers: 4 hm2/hm2_7i95.0:     Register Stride: 0x00000100 hm2/hm2_7i95.0:     -- Instance Stride: 0x00000004 hm2/hm2_7i95.0:     -- Multiple Registers: 0x0000000F hm2/hm2_7i95.0: Module Descriptor 6 at 0x0488: hm2/hm2_7i95.0:     General Function Tag: 28 (PktUART Receive Channel) hm2/hm2_7i95.0:     Version: 2 hm2/hm2_7i95.0:     Clock Tag: 1 (100.000 MHz) hm2/hm2_7i95.0:     Instances: 1 hm2/hm2_7i95.0:     Base Address: 0x6500 hm2/hm2_7i95.0:     -- Num Registers: 4 hm2/hm2_7i95.0:     Register Stride: 0x00000100 hm2/hm2_7i95.0:     -- Instance Stride: 0x00000004 hm2/hm2_7i95.0:     -- Multiple Registers: 0x0000000F hm2/hm2_7i95.0: Module Descriptor 7 at 0x0494: hm2/hm2_7i95.0:     General Function Tag: 193 (Smart Serial Interface) hm2/hm2_7i95.0:     Version: 0 hm2/hm2_7i95.0:     Clock Tag: 1 (100.000 MHz) hm2/hm2_7i95.0:     Instances: 1 hm2/hm2_7i95.0:     Base Address: 0x5B00 hm2/hm2_7i95.0:     -- Num Registers: 6 hm2/hm2_7i95.0:     Register Stride: 0x00000100 hm2/hm2_7i95.0:     -- Instance Stride: 0x00000040 hm2/hm2_7i95.0:     -- Multiple Registers: 0x0000003C hm2/hm2_7i95.0: Module Descriptor 8 at 0x04A0: hm2/hm2_7i95.0:     General Function Tag: 5 (StepGen) hm2/hm2_7i95.0:     Version: 2 hm2/hm2_7i95.0:     Clock Tag: 1 (100.000 MHz) hm2/hm2_7i95.0:     Instances: 6 hm2/hm2_7i95.0:     Base Address: 0x2000 hm2/hm2_7i95.0:     -- Num Registers: 10 hm2/hm2_7i95.0:     Register Stride: 0x00000100 hm2/hm2_7i95.0:     -- Instance Stride: 0x00000004 hm2/hm2_7i95.0:     -- Multiple Registers: 0x000001FF hm2/hm2_7i95.0: Module Descriptor 9 at 0x04AC: hm2/hm2_7i95.0:     General Function Tag: 195 (SSR) hm2/hm2_7i95.0:     Version: 0 hm2/hm2_7i95.0:     Clock Tag: 1 (100.000 MHz) hm2/hm2_7i95.0:     Instances: 1 hm2/hm2_7i95.0:     Base Address: 0x7D00 hm2/hm2_7i95.0:     -- Num Registers: 2 hm2/hm2_7i95.0:     Register Stride: 0x00000100 hm2/hm2_7i95.0:     -- Instance Stride: 0x00000004 hm2/hm2_7i95.0:     -- Multiple Registers: 0x00000003 hm2/hm2_7i95.0: Module Descriptor 10 at 0x04B8: hm2/hm2_7i95.0:     General Function Tag: 30 (InMux Input Mux) hm2/hm2_7i95.0:     Version: 0 hm2/hm2_7i95.0:     Clock Tag: 1 (100.000 MHz) hm2/hm2_7i95.0:     Instances: 1 hm2/hm2_7i95.0:     Base Address: 0x8000 hm2/hm2_7i95.0:     -- Num Registers: 5 hm2/hm2_7i95.0:     Register Stride: 0x00000100 hm2/hm2_7i95.0:     -- Instance Stride: 0x00000004 hm2/hm2_7i95.0:     -- Multiple Registers: 0x0000001F hm2/hm2_7i95.0: Module Descriptor 11 at 0x04C4: hm2/hm2_7i95.0:     General Function Tag: 128 (LED) hm2/hm2_7i95.0:     Version: 0 hm2/hm2_7i95.0:     Clock Tag: 1 (100.000 MHz) hm2/hm2_7i95.0:     Instances: 1 hm2/hm2_7i95.0:     Base Address: 0x0200 hm2/hm2_7i95.0:     -- Num Registers: 1 hm2/hm2_7i95.0:     Register Stride: 0x00000100 hm2/hm2_7i95.0:     -- Instance Stride: 0x00000004 hm2/hm2_7i95.0:     -- Multiple Registers: 0x00000000 hm2/hm2_7i95.0: created PktUART Interface function hm2_7i95.0.pktuart.0. hm2/hm2_7i95.0: Smart Serial Firmware Version 43 Board hm2_7i95.0.7i84.0.0 Hardware Mode 0 = standard Board hm2_7i95.0.7i84.0.0 Software Mode 0 = input_output Board hm2_7i95.0.7i84.0.0 Software Mode 1 = io_analog_fieldvoltage Board hm2_7i95.0.7i84.0.0 Software Mode 2 = io_encoder_analog hm2/hm2_7i95.0: 58 I/O Pins used: hm2/hm2_7i95.0:     IO Pin 000 (TB3-02/TB3-03): StepGen #0, pin Step (Output) hm2/hm2_7i95.0:     IO Pin 001 (TB3-04/TB3-05): StepGen #0, pin Direction (Output) hm2/hm2_7i95.0:     IO Pin 002 (TB3-08/TB3-09): StepGen #1, pin Step (Output) hm2/hm2_7i95.0:     IO Pin 003 (TB3-10/TB3-11): StepGen #1, pin Direction (Output) hm2/hm2_7i95.0:     IO Pin 004 (TB3-14/TB3-15): StepGen #2, pin Step (Output) hm2/hm2_7i95.0:     IO Pin 005 (TB3-16/TB3-17): StepGen #2, pin Direction (Output) hm2/hm2_7i95.0:     IO Pin 006 (TB3-20/TB3-21): StepGen #3, pin Step (Output) hm2/hm2_7i95.0:     IO Pin 007 (TB3-22/TB3-23): StepGen #3, pin Direction (Output) hm2/hm2_7i95.0:     IO Pin 008 (TB4-02/TB4-03): StepGen #4, pin Step (Output) hm2/hm2_7i95.0:     IO Pin 009 (TB4-04/TB4-05): StepGen #4, pin Direction (Output) hm2/hm2_7i95.0:     IO Pin 010 (TB4-08/TB4-09): IOPort hm2/hm2_7i95.0:     IO Pin 011 (TB4-10/TB4-11): IOPort hm2/hm2_7i95.0:     IO Pin 012 (TB4-14/TB4-15): Smart Serial Interface #0, pin rx0 (Input) hm2/hm2_7i95.0:     IO Pin 013 (TB4-16/TB4-17): Smart Serial Interface #0, pin tx0 (Output) hm2/hm2_7i95.0:     IO Pin 014 (TB3-16/TB3-17): Smart Serial Interface #0, pin txen0 (Output) hm2/hm2_7i95.0:     IO Pin 015 (TB4-20/TB4-21): PktUART Receive Channel #0, pin RX Data (Input) hm2/hm2_7i95.0:     IO Pin 016 (TB4-22/TB4-23): PktUART Transmit Channel #0, pin TX Data (Output) hm2/hm2_7i95.0:     IO Pin 017 (TB4-22/TB4-23): PktUART Transmit Channel #0, pin Drv Enable (Output) hm2/hm2_7i95.0:     IO Pin 018 (TB1-01/TB1-09): Muxed Encoder #0, pin Muxed A (Input) hm2/hm2_7i95.0:     IO Pin 019 (TB1-04/TB1-12): Muxed Encoder #0, pin Muxed B (Input) hm2/hm2_7i95.0:     IO Pin 020 (TB1-07/TB1-15): Muxed Encoder #0, pin Muxed Index (Input) hm2/hm2_7i95.0:     IO Pin 021 (TB1-17/TB2-01): Muxed Encoder #1, pin Muxed A (Input) hm2/hm2_7i95.0:     IO Pin 022 (TB1-20/TB2-04): Muxed Encoder #1, pin Muxed B (Input) hm2/hm2_7i95.0:     IO Pin 023 (TB1-23/TB2-07): Muxed Encoder #1, pin Muxed Index (Input) hm2/hm2_7i95.0:     IO Pin 024 (TB2-09/TB2-17): Muxed Encoder #2, pin Muxed A (Input) hm2/hm2_7i95.0:     IO Pin 025 (TB2-12/TB2-20): Muxed Encoder #2, pin Muxed B (Input) hm2/hm2_7i95.0:     IO Pin 026 (TB2-15/TB2-23): Muxed Encoder #2, pin Muxed Index (Input) hm2/hm2_7i95.0:     IO Pin 027 (Internal EncMux): Muxed Encoder Select #0, pin Mux Select 0 (Output) hm2/hm2_7i95.0:     IO Pin 028 (Internal InMux0): IOPort hm2/hm2_7i95.0:     IO Pin 029 (Internal InMux1): IOPort hm2/hm2_7i95.0:     IO Pin 030 (Internal InMux2): IOPort hm2/hm2_7i95.0:     IO Pin 031 (Internal InMux3): IOPort hm2/hm2_7i95.0:     IO Pin 032 (Internal InMux4): IOPort hm2/hm2_7i95.0:     IO Pin 033 (Internal InMuxData): IOPort hm2/hm2_7i95.0:     IO Pin 034 (TB5-13/TB5-14): IOPort hm2/hm2_7i95.0:     IO Pin 035 (TB5-15/TB5-16): IOPort hm2/hm2_7i95.0:     IO Pin 036 (TB5-17/TB5-18): IOPort hm2/hm2_7i95.0:     IO Pin 037 (TB5-19/TB5-20): IOPort hm2/hm2_7i95.0:     IO Pin 038 (TB5-21/TB5-22): IOPort hm2/hm2_7i95.0:     IO Pin 039 (TB5-23/TB5-24): IOPort hm2/hm2_7i95.0:     IO Pin 040 (internal): IOPort hm2/hm2_7i95.0:     IO Pin 041 (P1-01/DB25-01): IOPort hm2/hm2_7i95.0:     IO Pin 042 (P1-02/DB25-14): IOPort hm2/hm2_7i95.0:     IO Pin 043 (P1-03/DB25-02): IOPort hm2/hm2_7i95.0:     IO Pin 044 (P1-04/DB25-15): IOPort hm2/hm2_7i95.0:     IO Pin 045 (P1-05/DB25-03): IOPort hm2/hm2_7i95.0:     IO Pin 046 (P1-06/DB25-16): IOPort hm2/hm2_7i95.0:     IO Pin 047 (P1-07/DB25-04): IOPort hm2/hm2_7i95.0:     IO Pin 048 (P1-08/DB25-17): IOPort hm2/hm2_7i95.0:     IO Pin 049 (P1-09/DB25-05): IOPort hm2/hm2_7i95.0:     IO Pin 050 (P1-11/DB25-06): IOPort hm2/hm2_7i95.0:     IO Pin 051 (P1-13/DB25-07): IOPort hm2/hm2_7i95.0:     IO Pin 052 (P1-15/DB25-08): IOPort hm2/hm2_7i95.0:     IO Pin 053 (P1-17/DB25-09): IOPort hm2/hm2_7i95.0:     IO Pin 054 (P1-19/DB25-10): IOPort hm2/hm2_7i95.0:     IO Pin 055 (P1-21/DB25-11): IOPort hm2/hm2_7i95.0:     IO Pin 056 (P1-23/DB25-12): IOPort hm2/hm2_7i95.0:     IO Pin 057 (P1-25/DB25-13): IOPort hm2/hm2_7i95.0: HM2 Modules used: hm2/hm2_7i95.0: Encoders: 6 hm2/hm2_7i95.0:     clock_frequency: 100000000 Hz (100.000 MHz) hm2/hm2_7i95.0:     version: 4 hm2/hm2_7i95.0:     counter_addr: 0x3600 hm2/hm2_7i95.0:     latch_control_addr: 0x3700 hm2/hm2_7i95.0:     timestamp_div_addr: 0x3800 hm2/hm2_7i95.0:     timestamp_count_addr: 0x3900 hm2/hm2_7i95.0:     filter_rate_addr: 0x3A00 hm2/hm2_7i95.0:     timestamp_div: 0x0000 hm2/hm2_7i95.0:     instance 0: hm2/hm2_7i95.0:         hw: hm2/hm2_7i95.0:             counter = 4aec.0001 hm2/hm2_7i95.0:             latch/control = 0000.0800 hm2/hm2_7i95.0:             prev_control = 0000.0800 hm2/hm2_7i95.0:     instance 1: hm2/hm2_7i95.0:         hw: hm2/hm2_7i95.0:             counter = 0000.0000 hm2/hm2_7i95.0:             latch/control = 0000.0800 hm2/hm2_7i95.0:             prev_control = 0000.0800 hm2/hm2_7i95.0:     instance 2: hm2/hm2_7i95.0:         hw: hm2/hm2_7i95.0:             counter = 90db.ffff hm2/hm2_7i95.0:             latch/control = 0000.0800 hm2/hm2_7i95.0:             prev_control = 0000.0800 hm2/hm2_7i95.0:     instance 3: hm2/hm2_7i95.0:         hw: hm2/hm2_7i95.0:             counter = 003d.ffff hm2/hm2_7i95.0:             latch/control = 0000.0800 hm2/hm2_7i95.0:             prev_control = 0000.0800 hm2/hm2_7i95.0:     instance 4: hm2/hm2_7i95.0:         hw: hm2/hm2_7i95.0:             counter = 0000.0000 hm2/hm2_7i95.0:             latch/control = 0000.0800 hm2/hm2_7i95.0:             prev_control = 0000.0800 hm2/hm2_7i95.0:     instance 5: hm2/hm2_7i95.0:         hw: hm2/hm2_7i95.0:             counter = 0000.0000 hm2/hm2_7i95.0:             latch/control = 0000.0800 hm2/hm2_7i95.0:             prev_control = 0000.0800 hm2/hm2_7i95.0: SSerial: 1 hm2/hm2_7i95.0:   version 43 hm2/hm2_7i95.0:     instance 0: hm2/hm2_7i95.0:         Command Addr 0x5b00 hm2/hm2_7i95.0:         Data Addr    0x5c00 hm2/hm2_7i95.0:         port 0 device hm2_7i95.0.7i84.0.0 hm2/hm2_7i95.0:              Parameters: hm2/hm2_7i95.0:                    RecordType = 0xa0 hm2/hm2_7i95.0:                    DataLength = 0x20 hm2/hm2_7i95.0:                    DataType = 0x01 hm2/hm2_7i95.0:                    DataDir = 0x00 hm2/hm2_7i95.0:                    ParmMax 1.00 hm2/hm2_7i95.0:                    ParmMin 0.00 hm2/hm2_7i95.0:                    SizeOf ParmMin 0x04 hm2/hm2_7i95.0:                    ParmAddr = 0x0808 hm2/hm2_7i95.0:                    UnitString = none hm2/hm2_7i95.0:                    NameString = input hm2/hm2_7i95.0:                    RecordType = 0xa0 hm2/hm2_7i95.0:                    DataLength = 0x10 hm2/hm2_7i95.0:                    DataType = 0x01 hm2/hm2_7i95.0:                    DataDir = 0x80 hm2/hm2_7i95.0:                    ParmMax 1.00 hm2/hm2_7i95.0:                    ParmMin 0.00 hm2/hm2_7i95.0:                    SizeOf ParmMin 0x04 hm2/hm2_7i95.0:                    ParmAddr = 0x0800 hm2/hm2_7i95.0:                    UnitString = none hm2/hm2_7i95.0:                    NameString = output hm2/hm2_7i95.0:              Globals: hm2/hm2_7i95.0:                    RecordType = 0xa0 hm2/hm2_7i95.0:                    DataLength = 0x08 hm2/hm2_7i95.0:                    DataType = 0x02 hm2/hm2_7i95.0:                    DataDir = 0x00 hm2/hm2_7i95.0:                    ParmMax 36.29 hm2/hm2_7i95.0:                    ParmMin 0.00 hm2/hm2_7i95.0:                    SizeOf ParmMin 4 hm2/hm2_7i95.0:                    ParmAddr = 0x0810 hm2/hm2_7i95.0:                    UnitString = volts hm2/hm2_7i95.0:                    NameString = analogin0 hm2/hm2_7i95.0:                    RecordType = 0xa0 hm2/hm2_7i95.0:                    DataLength = 0x08 hm2/hm2_7i95.0:                    DataType = 0x02 hm2/hm2_7i95.0:                    DataDir = 0x00 hm2/hm2_7i95.0:                    ParmMax 36.29 hm2/hm2_7i95.0:                    ParmMin 0.00 hm2/hm2_7i95.0:                    SizeOf ParmMin 4 hm2/hm2_7i95.0:                    ParmAddr = 0x0811 hm2/hm2_7i95.0:                    UnitString = volts hm2/hm2_7i95.0:                    NameString = analogin1 hm2/hm2_7i95.0:                    RecordType = 0xa0 hm2/hm2_7i95.0:                    DataLength = 0x08 hm2/hm2_7i95.0:                    DataType = 0x02 hm2/hm2_7i95.0:                    DataDir = 0x00 hm2/hm2_7i95.0:                    ParmMax 36.29 hm2/hm2_7i95.0:                    ParmMin 0.00 hm2/hm2_7i95.0:                    SizeOf ParmMin 4 hm2/hm2_7i95.0:                    ParmAddr = 0x0812 hm2/hm2_7i95.0:                    UnitString = volts hm2/hm2_7i95.0:                    NameString = analogin2 hm2/hm2_7i95.0:                    RecordType = 0xa0 hm2/hm2_7i95.0:                    DataLength = 0x08 hm2/hm2_7i95.0:                    DataType = 0x02 hm2/hm2_7i95.0:                    DataDir = 0x00 hm2/hm2_7i95.0:                    ParmMax 36.29 hm2/hm2_7i95.0:                    ParmMin 0.00 hm2/hm2_7i95.0:                    SizeOf ParmMin 4 hm2/hm2_7i95.0:                    ParmAddr = 0x0813 hm2/hm2_7i95.0:                    UnitString = volts hm2/hm2_7i95.0:                    NameString = analogin3 hm2/hm2_7i95.0:                    RecordType = 0xa0 hm2/hm2_7i95.0:                    DataLength = 0x08 hm2/hm2_7i95.0:                    DataType = 0x08 hm2/hm2_7i95.0:                    DataDir = 0x00 hm2/hm2_7i95.0:                    ParmMax 0.00 hm2/hm2_7i95.0:                    ParmMin 0.00 hm2/hm2_7i95.0:                    SizeOf ParmMin 4 hm2/hm2_7i95.0:                    ParmAddr = 0x09a0 hm2/hm2_7i95.0:                    UnitString = counts hm2/hm2_7i95.0:                    NameString = enc0 hm2/hm2_7i95.0:                    RecordType = 0xa0 hm2/hm2_7i95.0:                    DataLength = 0x08 hm2/hm2_7i95.0:                    DataType = 0x08 hm2/hm2_7i95.0:                    DataDir = 0x00 hm2/hm2_7i95.0:                    ParmMax 0.00 hm2/hm2_7i95.0:                    ParmMin 0.00 hm2/hm2_7i95.0:                    SizeOf ParmMin 4 hm2/hm2_7i95.0:                    ParmAddr = 0x09a2 hm2/hm2_7i95.0:                    UnitString = counts hm2/hm2_7i95.0:                    NameString = enc1 hm2/hm2_7i95.0:                    RecordType = 0xa0 hm2/hm2_7i95.0:                    DataLength = 0x10 hm2/hm2_7i95.0:                    DataType = 0x02 hm2/hm2_7i95.0:                    DataDir = 0x00 hm2/hm2_7i95.0:                    ParmMax 36.29 hm2/hm2_7i95.0:                    ParmMin 0.00 hm2/hm2_7i95.0:                    SizeOf ParmMin 4 hm2/hm2_7i95.0:                    ParmAddr = 0x08a6 hm2/hm2_7i95.0:                    UnitString = volts hm2/hm2_7i95.0:                    NameString = fieldvoltagea hm2/hm2_7i95.0:                    RecordType = 0xa0 hm2/hm2_7i95.0:                    DataLength = 0x10 hm2/hm2_7i95.0:                    DataType = 0x02 hm2/hm2_7i95.0:                    DataDir = 0x00 hm2/hm2_7i95.0:                    ParmMax 36.29 hm2/hm2_7i95.0:                    ParmMin 0.00 hm2/hm2_7i95.0:                    SizeOf ParmMin 4 hm2/hm2_7i95.0:                    ParmAddr = 0x08a8 hm2/hm2_7i95.0:                    UnitString = volts hm2/hm2_7i95.0:                    NameString = fieldvoltageb hm2/hm2_7i95.0:                    RecordType = 0xa0 hm2/hm2_7i95.0:                    DataLength = 0x10 hm2/hm2_7i95.0:                    DataType = 0x02 hm2/hm2_7i95.0:                    DataDir = 0x00 hm2/hm2_7i95.0:                    ParmMax 0.00 hm2/hm2_7i95.0:                    ParmMin 0.00 hm2/hm2_7i95.0:                    SizeOf ParmMin 4 hm2/hm2_7i95.0:                    ParmAddr = 0x095c hm2/hm2_7i95.0:                    UnitString = none hm2/hm2_7i95.0:                    NameString = swrevision hm2/hm2_7i95.0:                    RecordType = 0xa0 hm2/hm2_7i95.0:                    DataLength = 0x10 hm2/hm2_7i95.0:                    DataType = 0x02 hm2/hm2_7i95.0:                    DataDir = 0x00 hm2/hm2_7i95.0:                    ParmMax 0.00 hm2/hm2_7i95.0:                    ParmMin 0.00 hm2/hm2_7i95.0:                    SizeOf ParmMin 4 hm2/hm2_7i95.0:                    ParmAddr = 0x0974 hm2/hm2_7i95.0:                    UnitString = none hm2/hm2_7i95.0:                    NameString = hwrevision hm2/hm2_7i95.0:                    RecordType = 0xa0 hm2/hm2_7i95.0:                    DataLength = 0x20 hm2/hm2_7i95.0:                    DataType = 0x04 hm2/hm2_7i95.0:                    DataDir = 0x00 hm2/hm2_7i95.0:                    ParmMax 0.00 hm2/hm2_7i95.0:                    ParmMin 0.00 hm2/hm2_7i95.0:                    SizeOf ParmMin 4 hm2/hm2_7i95.0:                    ParmAddr = 0x0078 hm2/hm2_7i95.0:                    UnitString = none hm2/hm2_7i95.0:                    NameString = nvunitnumber hm2/hm2_7i95.0:                    RecordType = 0xa0 hm2/hm2_7i95.0:                    DataLength = 0x10 hm2/hm2_7i95.0:                    DataType = 0x04 hm2/hm2_7i95.0:                    DataDir = 0x40 hm2/hm2_7i95.0:                    ParmMax 0.00 hm2/hm2_7i95.0:                    ParmMin 0.00 hm2/hm2_7i95.0:                    SizeOf ParmMin 4 hm2/hm2_7i95.0:                    ParmAddr = 0x0064 hm2/hm2_7i95.0:                    UnitString = none hm2/hm2_7i95.0:                    NameString = nvwatchdogtimeout hm2/hm2_7i95.0:                    RecordType = 0xa0 hm2/hm2_7i95.0:                    DataLength = 0x10 hm2/hm2_7i95.0:                    DataType = 0x02 hm2/hm2_7i95.0:                    DataDir = 0x40 hm2/hm2_7i95.0:                    ParmMax 0.00 hm2/hm2_7i95.0:                    ParmMin 0.00 hm2/hm2_7i95.0:                    SizeOf ParmMin 4 hm2/hm2_7i95.0:                    ParmAddr = 0x0998 hm2/hm2_7i95.0:                    UnitString = none hm2/hm2_7i95.0:                    NameString = encmode0 hm2/hm2_7i95.0:                    RecordType = 0xa0 hm2/hm2_7i95.0:                    DataLength = 0x10 hm2/hm2_7i95.0:                    DataType = 0x02 hm2/hm2_7i95.0:                    DataDir = 0x40 hm2/hm2_7i95.0:                    ParmMax 0.00 hm2/hm2_7i95.0:                    ParmMin 0.00 hm2/hm2_7i95.0:                    SizeOf ParmMin 4 hm2/hm2_7i95.0:                    ParmAddr = 0x099a hm2/hm2_7i95.0:                    UnitString = none hm2/hm2_7i95.0:                    NameString = encmode1 hm2/hm2_7i95.0:                    RecordType = 0xa0 hm2/hm2_7i95.0:                    DataLength = 0x10 hm2/hm2_7i95.0:                    DataType = 0x04 hm2/hm2_7i95.0:                    DataDir = 0x40 hm2/hm2_7i95.0:                    ParmMax 0.00 hm2/hm2_7i95.0:                    ParmMin 0.00 hm2/hm2_7i95.0:                    SizeOf ParmMin 4 hm2/hm2_7i95.0:                    ParmAddr = 0x0066 hm2/hm2_7i95.0:                    UnitString = none hm2/hm2_7i95.0:                    NameString = nvencmode0 hm2/hm2_7i95.0:                    RecordType = 0xa0 hm2/hm2_7i95.0:                    DataLength = 0x10 hm2/hm2_7i95.0:                    DataType = 0x04 hm2/hm2_7i95.0:                    DataDir = 0x40 hm2/hm2_7i95.0:                    ParmMax 0.00 hm2/hm2_7i95.0:                    ParmMin 0.00 hm2/hm2_7i95.0:                    SizeOf ParmMin 4 hm2/hm2_7i95.0:                    ParmAddr = 0x0068 hm2/hm2_7i95.0:                    UnitString = none hm2/hm2_7i95.0:                    NameString = nvencmode1 hm2/hm2_7i95.0:              Modes: hm2/hm2_7i95.0:                RecordType = 0xb0 hm2/hm2_7i95.0:                ModeIndex = 0x00 hm2/hm2_7i95.0:                ModeType = 0x00 hm2/hm2_7i95.0:                Unused = 0 hm2/hm2_7i95.0:                NameString = standard hm2/hm2_7i95.0:                RecordType = 0xb0 hm2/hm2_7i95.0:                ModeIndex = 0x00 hm2/hm2_7i95.0:                ModeType = 0x01 hm2/hm2_7i95.0:                Unused = 0 hm2/hm2_7i95.0:                NameString = input_output hm2/hm2_7i95.0:  hm2/hm2_7i95.0: StepGen: 5 hm2/hm2_7i95.0:     clock_frequency: 100000000 Hz (100.000 MHz) hm2/hm2_7i95.0:     version: 2 hm2/hm2_7i95.0:     step_rate_addr: 0x2000 hm2/hm2_7i95.0:     accumulator_addr: 0x2100 hm2/hm2_7i95.0:     mode_addr: 0x2200 hm2/hm2_7i95.0:     dir_setup_time_addr: 0x2300 hm2/hm2_7i95.0:     dir_hold_time_addr: 0x2400 hm2/hm2_7i95.0:     pulse_width_addr: 0x2500 hm2/hm2_7i95.0:     pulse_idle_width_addr: 0x2600 hm2/hm2_7i95.0:     table_sequence_data_setup_addr: 0x2700 hm2/hm2_7i95.0:     table_sequence_length_addr: 0x2800 hm2/hm2_7i95.0:     master_dds_addr: 0x2900 hm2/hm2_7i95.0:     instance 0: hm2/hm2_7i95.0:         enable = 0 hm2/hm2_7i95.0:         hw: hm2/hm2_7i95.0:             step_rate = 0x00000000 hm2/hm2_7i95.0:             accumulator = 0x00000000 hm2/hm2_7i95.0:             mode = 0x00000000 hm2/hm2_7i95.0:             dir_setup_time = 0x00003FFF (163830 ns) hm2/hm2_7i95.0:             dir_hold_time = 0x00003FFF (163830 ns) hm2/hm2_7i95.0:             pulse_width = 0x00003FFF (163830 ns) hm2/hm2_7i95.0:             pulse_idle_width = 0x00003FFF (163830 ns) hm2/hm2_7i95.0:     instance 1: hm2/hm2_7i95.0:         enable = 0 hm2/hm2_7i95.0:         hw: hm2/hm2_7i95.0:             step_rate = 0x00000000 hm2/hm2_7i95.0:             accumulator = 0x00000000 hm2/hm2_7i95.0:             mode = 0x00000000 hm2/hm2_7i95.0:             dir_setup_time = 0x00003FFF (163830 ns) hm2/hm2_7i95.0:             dir_hold_time = 0x00003FFF (163830 ns) hm2/hm2_7i95.0:             pulse_width = 0x00003FFF (163830 ns) hm2/hm2_7i95.0:             pulse_idle_width = 0x00003FFF (163830 ns) hm2/hm2_7i95.0:     instance 2: hm2/hm2_7i95.0:         enable = 0 hm2/hm2_7i95.0:         hw: hm2/hm2_7i95.0:             step_rate = 0x00000000 hm2/hm2_7i95.0:             accumulator = 0x00000000 hm2/hm2_7i95.0:             mode = 0x00000000 hm2/hm2_7i95.0:             dir_setup_time = 0x00003FFF (163830 ns) hm2/hm2_7i95.0:             dir_hold_time = 0x00003FFF (163830 ns) hm2/hm2_7i95.0:             pulse_width = 0x00003FFF (163830 ns) hm2/hm2_7i95.0:             pulse_idle_width = 0x00003FFF (163830 ns) hm2/hm2_7i95.0:     instance 3: hm2/hm2_7i95.0:         enable = 0 hm2/hm2_7i95.0:         hw: hm2/hm2_7i95.0:             step_rate = 0x00000000 hm2/hm2_7i95.0:             accumulator = 0x00000000 hm2/hm2_7i95.0:             mode = 0x00000000 hm2/hm2_7i95.0:             dir_setup_time = 0x00003FFF (163830 ns) hm2/hm2_7i95.0:             dir_hold_time = 0x00003FFF (163830 ns) hm2/hm2_7i95.0:             pulse_width = 0x00003FFF (163830 ns) hm2/hm2_7i95.0:             pulse_idle_width = 0x00003FFF (163830 ns) hm2/hm2_7i95.0:     instance 4: hm2/hm2_7i95.0:         enable = 0 hm2/hm2_7i95.0:         hw: hm2/hm2_7i95.0:             step_rate = 0x00000000 hm2/hm2_7i95.0:             accumulator = 0x00000000 hm2/hm2_7i95.0:             mode = 0x00000000 hm2/hm2_7i95.0:             dir_setup_time = 0x00003FFF (163830 ns) hm2/hm2_7i95.0:             dir_hold_time = 0x00003FFF (163830 ns) hm2/hm2_7i95.0:             pulse_width = 0x00003FFF (163830 ns) hm2/hm2_7i95.0:             pulse_idle_width = 0x00003FFF (163830 ns) hm2/hm2_7i95.0: IO Ports: 2 hm2/hm2_7i95.0:     clock_frequency: 100000000 Hz (100.000 MHz) hm2/hm2_7i95.0:     version: 0 hm2/hm2_7i95.0:     data_addr: 0x1000 hm2/hm2_7i95.0:     ddr_addr: 0x1100 hm2/hm2_7i95.0:     alt_source_addr: 0x1200 hm2/hm2_7i95.0:     open_drain_addr: 0x1300 hm2/hm2_7i95.0:     output_invert_addr: 0x1400 hm2/hm2_7i95.0:     instance 0: hm2/hm2_7i95.0:         data_read = 0x1427BFFF hm2/hm2_7i95.0:         data_write = 0x000000 hm2/hm2_7i95.0:         ddr = 0x8036000 hm2/hm2_7i95.0:         alt_source = 0xFFFF3FF hm2/hm2_7i95.0:         open_drain = 0x000000 hm2/hm2_7i95.0:         output_invert = 0x000000 hm2/hm2_7i95.0:     instance 1: hm2/hm2_7i95.0:         data_read = 0x1FFFFFEF hm2/hm2_7i95.0:         data_write = 0x000000 hm2/hm2_7i95.0:         ddr = 0x000000 hm2/hm2_7i95.0:         alt_source = 0x000000 hm2/hm2_7i95.0:         open_drain = 0x000000 hm2/hm2_7i95.0:         output_invert = 0x000000 hm2/hm2_7i95.0: Watchdog: 1 hm2/hm2_7i95.0:     clock_frequency: 100000000 Hz (100.000 MHz) hm2/hm2_7i95.0:     version: 0 hm2/hm2_7i95.0:     timer_addr: 0x0C00 hm2/hm2_7i95.0:     status_addr: 0x0D00 hm2/hm2_7i95.0:     reset_addr: 0x0E00 hm2/hm2_7i95.0:     instance 0: hm2/hm2_7i95.0:         param timeout_ns = 5000000 hm2/hm2_7i95.0:         pin has_bit = 0 hm2/hm2_7i95.0:         reg timer = 0x80000000 hm2/hm2_7i95.0: registered

I took a network capture of running the script and stopped it only once I had seen a position-fb peak in halscope. The file is attached. I also created a small python program to parse the capture file, and I have attached that as well. With the parse and capture file, I run the following commands:
Code:
$ ./lbp16.py capture.pcap > capture.txt $ $ cat capture.txt | grep "ADDRESS 0x2000" | grep -v "DATA 0x0000000000000000000000000000000000000000" $ $ cat capture.txt | grep "ADDRESS 0x2100" | grep -v "DATA 0x0000000000000000000000000000000000000000" $

None of the commands generate any output. This means that step rate register 0x2000 is never written anything else than 0, and the accumulator registers 0x2100 never reads anything else than 0.

I'm not exactly sure what my next step is at the moment. But if you think mesa modbus is the prime suspect, I might start looking around at that code.
 

Attachment not found


 

Attachment not found



edit: I added the the output from parsing the capture file by lbp16.py (plain text)
 

Attachment not found


edit2: Editing messed up the code codes... hopefully fixed now

Please Log in to join the conversation.

More
1 year 11 months ago #313834 by Finngineering
For information, and in case it gives somebody any ideas. I started looking at the mesa_modbus.c.tmpl code, and modified it to output its internal state as a HAL pin. Attached a screenshot from halscope where the state is visible alongside the jump in position-fb.
 

Attachment not found



The states are defined by:
Code:
enum {     START,     WAIT_FOR_SEND_BEGIN,     WAIT_FOR_SEND_COMPLETE,     WAIT_FOR_DATA_FRAME,     WAIT_FOR_FRAME_SIZES,     WAIT_FOR_DATA,     FETCH_MORE_DATA,     WAIT_A_BIT,     WAIT_FOR_RX_CLEAR,     RESET_WAIT, };

So, we start in state WAIT_FOR_DATA_FRAME, then go to RESET_WAIT for a few cycles, and the in either state START or WAIT_FOR_SEND_BEGIN, the jump in position-fb occurs.

Please Log in to join the conversation.

More
1 year 11 months ago #313837 by Finngineering
Well, I found something already. There is a divide-by-zero on line 525 below (line numbers differ slightly from official code), because inst->hal->rate is not initialized in the code, and at least in my case it defaults to zero. Changing it to 1 from halshow causes the jumps in position-fb to stop. At least for now :)
 

Attachment not found



I guess the divide by zero causes a fault/interrupt handler to be called and the execution state/context may be lost/upset? At least I'm imagining something like that. If somebody can produce a better or more accurate explanation, it would be interesting to hear.

This seems to me like a clear bug. Is somebody able to take this forward from here, or give me advice on how I can make a bug report?

edit: The hal pin related to inst->hal->rate is named update-hz. I though I'd point that out, as the connection is by no means apparent from the screenshot.

Please Log in to join the conversation.

More
1 year 11 months ago #313842 by PCW
Maybe related to the bug I mentioned with update rate:

   If you ever set the update rate to 0 (maximum), changing to a
    non-zero rate will not work (communication stops)

 

Please Log in to join the conversation.

More
1 year 11 months ago #313851 by Finngineering
Yes, that may very well be the case. The following lines are from the code (but not directly following each other like shown):
Code:
static long timer = 0; ... if (inst->hal->rate > 0 && (timer -= period) > 0) break; ... timer = 1e9 / inst->hal->rate;
When update-hz is 0, then there is also a division by zero in the last line. Maybe what effects this have depends on the system. The result of the division may be +infinity (which is a valid float). When that is the casted to a 64 bit(?) long, that may give a very big number, which during the next iteration causes the if statement to take the "break" branch for practically all time in the future. There are lots of "ifs" here, and I think that at least some things are implementation dependent.

Please Log in to join the conversation.