1 year 3 months ago #332379 by jmelson
Nope, Variable Reluctance resolvers require quite a bit more excitation drive, and not all resolver circuits can handle these. Tamagawa is a leading manufacturer of these, but they also make "brushless resolvers" which require MUCH less drive. In the data sheets, they sometimes state the excitation impedance as a complex number, something like 95 + 135j Ohms at some frequency. The higher these numbers, the less drive current the resolver requires. Common brands of brushless resolvers seen on older equipment are Singer-Kearfott and Harowe Controls.
Sin/Cos encoders are not magnetic devices, but often optical linear scales (can also be rotary) where the raw optical signal is brought out, either as a voltage or a current. The reason for this is interpolator boxes can be attached to increase the encoder resolution. Back in the "old days" linear scales often had native resolution of 100 lines per inch or so, so interpolation was required to get proper machine accuracy. Nowadays, high-resolution optical gratings can be made easily, so this stuff is rarely seen today.
Jon

Please Log in to join the conversation.

More
1 year 3 months ago #332434 by andypugh
I think that Granite Devices drives handle resolvers, but the current drive (IONI) only handles 700W. (you need at least twice that)
The older "Argon" drive might fit the bill, though it's a bit down on power compared to the existing drives.
granitedevices.com/oldsite/digital-servo-drive-argon
Lists the following feedback sources:
Incremental encoder
• Analog Sin/Cos encoder
• Resolver/synchro
• Serial SSI & BiSS (upcoming feature)
• Tachogenerator
• Hall sensors

What is the feedback system used for axis position? Are there separate scales, or does that rely on the resolvers on the motors too?

STMBL would work, but doesn't fit your "industrial" and "don't want to build it myself" criteria. (though see the thread about a new STMBL on this forum.)

Please Log in to join the conversation.

More
1 year 3 months ago #332453 by nanowhat

What is the feedback system used for axis position? Are there separate scales, or does that rely on the resolvers on the motors too?
 
There aren't any other position sensors, so the motor resolvers must serve both commutation and position feedback.

Please Log in to join the conversation.

More
1 year 2 months ago #332754 by andypugh
In that case things may get a little complicated. It comes down to how the controller gets its position information. Often the drive will excite the resolvers, use them for commutation, and then pass a quadrature signal out to the rest of the system.

The Mesa 7i49 and (I expect) the Granite devices drives expect to be providing the excitation signal, and will typically sample position at or around the peak in the excitation signal. If the controller is also sampling this signal for position feedback then it's going to get complicated.

Do you have any details of the drive to motor and drive to contoller wiring? Is there any motor-to-controller wiring?

Please Log in to join the conversation.

More
1 year 2 months ago #332925 by nanowhat
There is no wiring between the motors and controller: all power and signals pass through the drives. The wiring diagram doesn't help: communication to the control, whether data or discrete signal, isn't explained (i.e. wire xxx connects terminal y1 to x1, but you don't get to know what it does).

Given that I can't actually test the questionable motor properly, I think it may make more sense to replace the motors with modern servo systems.

Please Log in to join the conversation.

More
1 year 2 months ago #332980 by sivaraj
www.kollmorgen.com/sites/default/files/p...9032002701_A_5.1.pdf
The Page-86 in above DMC2 drive manual gives general resolver specification recomended by drive

www.wittenstein.de/download/operating-manual-tpm-plus-en.pdf
The Page-36 in this manual has resolver specification used by Wittenstein motor

It uses Tamakawa Brushless resolver
www.tamagawa-seiki.com/products/resolver...martsyn-builtin.html

Please Log in to join the conversation.

More
1 year 2 months ago #333062 by andypugh
Resolvers are very good (and very expensive) they will never break. (the bulbs in old optical encoders would burn out eventually, LEDs tend to last longer, but can still fail)

Given that only one drive has failed, have you looked at repairing it? It's unlikely that a hybrid system of one servo under LinuxCNC control and one under original control control would work very well.

Have you asked Mesa if the 8i20 is likely to come back into stock?
Do you know the power and voltage spec of the motors?

(I am on a train on mobile data, not in a good position to look through documentation links)

Please Log in to join the conversation.