- Posts: 4
- Thank you received: 0
7i97T + 7i74 + 7i84U – No Smart Serial Communication
1 month 2 weeks ago #349637
by Cristy13
7i97T + 7i74 + 7i84U – No Smart Serial Communication was created by Cristy13
Hi,I am retrofitting a CNC lathe with LinuxCNC and I have the following Mesa hardware:
I am using firmware:
MD5:
I also verified the firmware in flash with:
and I get:
gives only:
but no 7i84U devices are listed.I tested 7i84U boards on CH1 and CH2 of the 7i74 with the same result.On the 7i84U:
I also tested the 7i97T P2 interface with W21 UP and P2 disconnected:
Result:
So that test appears to pass.
also shows the expected Smart Serial signals:
on the 7i97T and
for the 7i74 channels.I also tried loading HostMot2 manually:
The 7i97T loads and registers normally, but the 7i84U is still not detected.Everything is new hardware.At this point I suspect either the 7i74 itself, the IDC26/DB25 path between P2 and the 7i74, or something I am missing in the Smart Serial configuration.Does anyone have a known-good 7i97T + 7i74 + 7i84U setup and can tell me what I should test next?In particular:
- 1x Mesa 7i97T
- 1x Mesa 7i74
- 4x Mesa 7i84U
- IDC26 to DB25 adapter
- DB25 male-male 1:1 cable between 7i97T P2 and 7i74
- standard straight-through CAT5e cables between 7i74 and 7i84U
Code:
192.168.1.121
Code:
7i97t_7i74d.bin
Code:
4130ebee623115267327c166f8da9d39
Code:
mesaflash --device 7I97T --addr 192.168.1.121 --verify /home/cnc/7i97t_7i74d.bin
Code:
Board FLASH memory verified successfully
Code:
mesaflash --device 7I97T --addr 192.168.1.121 --sserial
Code:
SSLBP port 0:
Code:
SSLBP Version: 1.43
Code:
SSLBP Channels: 8
Code:
SSLBP Baud Rate: 2500000
- W3 = LEFT / operate mode / 2.5 Mbaud
- VIN = about 28 V
- VFIELD A = about 28 V
- VFIELD B = about 28 V
- CR2 ON
- CR7 ON
- CR5 red ON
- CR6 green OFF / never blinks
- CR1 is ON
- I initially measured only about 4.5 V
- I changed it to external regulated 5 V supply
- now TB1 measures 5.08 V
- the problem is still exactly the same
Code:
1-1, 2-2, 3-3, 4-4, 5-5, 6-6, 7-7, 8-8
Code:
mesaflash --device 7I97T --addr 192.168.1.121 --rpo 0x1008
Code:
0001FFFF
Code:
readhmid
Code:
RXData0/TXData0
Code:
RXData1...7 / TXData1...7
Code:
halrun
Code:
loadrt hostmot2
Code:
loadrt hm2_eth board_ip=192.168.1.121 config="sserial_port_0=x0xxxxxx"
- Is
correct for a 7i84U connected to CH1 of the 7i74?Code:sserial_port_0=x0xxxxxx
- Is there a direct test for TX/RX on the 7i74 without an oscilloscope?
- Are there any jumpers/settings on the 7i74 or 7i84U that I may have missed?
Please Log in to join the conversation.
1 month 2 weeks ago #349638
by PCW
Replied by PCW on topic 7i97T + 7i74 + 7i84U – No Smart Serial Communication
I would try:
config="sserial_port_0=00000000"
Might also be a DB25 cable issue, not all adapters are wired correctly for this use.
config="sserial_port_0=00000000"
Might also be a DB25 cable issue, not all adapters are wired correctly for this use.
Please Log in to join the conversation.
1 month 2 weeks ago #349639
by Cristy13
Replied by Cristy13 on topic 7i97T + 7i74 + 7i84U – No Smart Serial Communication
I used this two cables for connection.
eusurplus.com/index.php?route=product/pr...t_id=108&search=db25
eusurplus.com/index.php?route=product/pr...t_id=109&search=db25
Thank you for your answer.
eusurplus.com/index.php?route=product/pr...t_id=108&search=db25
eusurplus.com/index.php?route=product/pr...t_id=109&search=db25
Thank you for your answer.
Please Log in to join the conversation.
1 month 2 weeks ago #349640
by PCW
Replied by PCW on topic 7i97T + 7i74 + 7i84U – No Smart Serial Communication
I can try duplicating this later today.
Please Log in to join the conversation.
1 month 2 weeks ago #349641
by Cristy13
Replied by Cristy13 on topic 7i97T + 7i74 + 7i84U – No Smart Serial Communication
ok. thank you very much
Please Log in to join the conversation.
1 month 2 weeks ago #349643
by PCW
Replied by PCW on topic 7i97T + 7i74 + 7i84U – No Smart Serial Communication
Well naturally, no problem found...
pcw@pcw-HP-Compaq-Elite-8300-USDT:~/bitfiles$ md5sum 7i97t_7i74d.bin
4130ebee623115267327c166f8da9d39 7i97t_7i74d.bin
7I97T with that firmware finds 7I84Us on all (1..7) 7I74 channels
7I74 channel 0 (lower left if facing the jacks) is not used with this firmware
as port 0 channel 0 is on the 7I97T card.
This is with our normal DB25M-IDC26 cable (and 7I74 powered over cable)
For external power make sure you have both the 7I74 and 7I97T Jumpered correctly:
7I97T W22 DOWN
7I74 W1 DOWN
Also note the 7I74 channel 1 is the top/left jack
facing the jacks, they are numbered:
1 3 5 7
0 2 4 6
pcw@pcw-HP-Compaq-Elite-8300-USDT:~/bitfiles$ md5sum 7i97t_7i74d.bin
4130ebee623115267327c166f8da9d39 7i97t_7i74d.bin
7I97T with that firmware finds 7I84Us on all (1..7) 7I74 channels
7I74 channel 0 (lower left if facing the jacks) is not used with this firmware
as port 0 channel 0 is on the 7I97T card.
This is with our normal DB25M-IDC26 cable (and 7I74 powered over cable)
For external power make sure you have both the 7I74 and 7I97T Jumpered correctly:
7I97T W22 DOWN
7I74 W1 DOWN
Also note the 7I74 channel 1 is the top/left jack
facing the jacks, they are numbered:
1 3 5 7
0 2 4 6
Please Log in to join the conversation.
1 month 2 weeks ago #349645
by Cristy13
Replied by Cristy13 on topic 7i97T + 7i74 + 7i84U – No Smart Serial Communication
Thank you very much. I found the problem.
With:
config="sserial_port_0=00000000"
the 7I84U boards are detected correctly.
At the moment I have only two 7I84U boards powered with 28V, and LinuxCNC detects both of them on channels 5 and 7:
hm2_7i97.0.7i84.0.5
hm2_7i97.0.7i84.0.7
So the 7I97T, 7I74, firmware, adapter and DB25 cable are all working correctly.
The main issue was that I was previously using:
config="sserial_port_0=x0xxxxxx"
and I had also misunderstood the physical channel numbering on the 7I74.
I will now power the other two 7I84U boards and test all four.
Thank you again for your help.
With:
config="sserial_port_0=00000000"
the 7I84U boards are detected correctly.
At the moment I have only two 7I84U boards powered with 28V, and LinuxCNC detects both of them on channels 5 and 7:
hm2_7i97.0.7i84.0.5
hm2_7i97.0.7i84.0.7
So the 7I97T, 7I74, firmware, adapter and DB25 cable are all working correctly.
The main issue was that I was previously using:
config="sserial_port_0=x0xxxxxx"
and I had also misunderstood the physical channel numbering on the 7I74.
I will now power the other two 7I84U boards and test all four.
Thank you again for your help.
Please Log in to join the conversation.
Time to create page: 0.107 seconds