Blew up my VFD; need advice
- kenthompson
- Topic Author
- Offline
- New Member
-
Less
More
2 years 10 months ago #289212
by kenthompson
Blew up my VFD; need advice was created by kenthompson
A short occurred in my spindle wiring (my fault, bad solder joint) and my VFD produced a large 'snap' before dying (power light blinking on and off). Looked inside the VFD and some physical interconnects blew out.
I am concerned that my spindle may be damaged and potentially introducing a short. Ordered a new VFD, but I want to confirm my Spindle isn't going to damage the new one once hooked up.
How can I test the spindle to confirm? I have a multi meter.. should I test for shorts across pins? Please help.
I am concerned that my spindle may be damaged and potentially introducing a short. Ordered a new VFD, but I want to confirm my Spindle isn't going to damage the new one once hooked up.
How can I test the spindle to confirm? I have a multi meter.. should I test for shorts across pins? Please help.
Please Log in to join the conversation.
2 years 10 months ago #289216
by PCW
Replied by PCW on topic Blew up my VFD; need advice
You could verify that the phase-phase resistance was the same for all
connections, and that the phase to Ground resistance was infinite.
connections, and that the phase to Ground resistance was infinite.
Please Log in to join the conversation.
- kenthompson
- Topic Author
- Offline
- New Member
-
Less
More
- Posts: 9
- Thank you received: 0
2 years 10 months ago #289223
by kenthompson
Replied by kenthompson on topic Blew up my VFD; need advice
Resistance same across pairs, and infinite from phase to ground. Thank you!