MPG Mesa 7i73 im stuck
8 years 4 months ago #113073
by andypugh
A binary-coded switch is more efficient with IO. But I am confused by your description.
Do you mean:
So that B and D have identical outputs?
Replied by andypugh on topic MPG Mesa 7i73 im stuck
lesureia wrote: when selecting a it turns yellow
when selecting b it turns yellow with d
when selecting c it turns yellow
when selecting d it turns d and b yellow
A binary-coded switch is more efficient with IO. But I am confused by your description.
Do you mean:
| Position | OutA | OutB | OutC | OutD |
| A | 1 | 0 | 0 | 0 |
| B | 0 | 1 | 0 | 1 |
| C | 0 | 0 | 1 | 0 |
| D | 0 | 1 | 0 | 1 |
So that B and D have identical outputs?
Please Log in to join the conversation.
8 years 4 months ago #113074
by lesureia
Replied by lesureia on topic MPG Mesa 7i73 im stuck
Thats looks correct in your diagram i doublechecked.
Yes B and D are identical.
And thanks for your kind help.
im away this weekend but will be back on monday
/Rickard.L
Yes B and D are identical.
And thanks for your kind help.
im away this weekend but will be back on monday
/Rickard.L
Please Log in to join the conversation.
8 years 4 months ago #113075
by andypugh
That sounds wrong. (it makes the switch useless).
Perhaps there are some wires touching where they shouldn't or some other wiring fault?
Replied by andypugh on topic MPG Mesa 7i73 im stuck
lesureia wrote: Thats looks correct in your diagram i doublechecked.
Yes B and D are identical.
That sounds wrong. (it makes the switch useless).
Perhaps there are some wires touching where they shouldn't or some other wiring fault?