Joint limit switch errors
- norbertfarquharsh
- Topic Author
- Offline
- Senior Member
-
I have used a meter to check the wiring and checked for the continuity of the wiring and that the limit switches showed a closed contact.
Halmeter also shows True on Parports11, 12, and 13 which are the ports for the X, Y, and Z axes.
I will attach a screen shot showing the Axis interface so you will see the system software load and the error messages. I will also attach the .hal and .ini files that were just created this morning.
I will appreciate any suggestions
Please Log in to join the conversation.
The way they are connected in hal, they should be be low until you hit home/limit
Please Log in to join the conversation.
i had that also and the mashine tryed to home in wrong direction
Please Log in to join the conversation.
- norbertfarquharsh
- Topic Author
- Offline
- Senior Member
-
- Posts: 58
- Thank you received: 0
I tried that on two of the axes and was more puzzled. When I tried that, the True did not change to False as I thought it should. I thought that maybe it was not reactive under those circumstances and that was why it did not change.
Does that give you a clue?
Please Log in to join the conversation.
- norbertfarquharsh
- Topic Author
- Offline
- Senior Member
-
- Posts: 58
- Thank you received: 0
Please Log in to join the conversation.
and the parallel port pins do not change when you activate the limit switches,
This suggest that you have a hardware problem like bad BOB, broken wire
bad parallel port, etc etc
Please Log in to join the conversation.
- norbertfarquharsh
- Topic Author
- Offline
- Senior Member
-
- Posts: 58
- Thank you received: 0
Thanks again.
Please Log in to join the conversation.
norbertfarquharsh wrote: Thank you for your reply. I was puzzled by too much information. I have a back up computer and tried it and it also showed the same problem.I thought maybe there might be a broken wire but completely rewired the limit switches and thought that was all working. But the only common thing would seem to be the BOB which you mention. i will try to get a replacement for that.
Thanks again.
What bob are you using as if it is one of the cheap China one with the blue relay on it. The need 12-24V for the input pins to work
Please Log in to join the conversation.
- norbertfarquharsh
- Topic Author
- Offline
- Senior Member
-
- Posts: 58
- Thank you received: 0
The BOB I am using is from Xylotex and has been in use for maybe 4 years, but I do not remember exactly.. It has no relays on it. I have already ordered a new one from Xylotex and will see what happens then. Just cannot figure the logic of the system to see how the errors occur.
Please Log in to join the conversation.
- tommylight
-
- Offline
- Administrator
-
- Posts: 22010
- Thank you received: 3
Some bobs have jumpers for setting them as pullup or pulldown.
Please Log in to join the conversation.