The Estop and the axis control need to be out of Estop for the relay to be on.
Here is the relevent code.
# --- ESTOP-OUT ---
net estop-out hm2_5i25.0.7i77.0.0.output-07
# ---estop signals---
net estop-loopout iocontrol.0.emc-enable-in <= estop-latch.0.ok-out
net estop-loopin <= iocontrol.0.user-enable-out => estop-latch.0.ok-in
net estop-reset iocontrol.0.user-request-enable => estop-latch.0.reset
net remote-estop estop-latch.0.fault-in <= hm2_5i25.0.7i77.0.0.input-00-not
Thanks in advance for any help
MarkD
Attachment not found
Attachment not found
Please Log in to join the conversation.
Please Log in to join the conversation.
markd wrote: I am having a problem getting the Estop Loop working as I would like. There is a NC external Estop connected to input00 which works as expected with axis. The problem is that I need output07 connected to the Estop loop to control a relay.
The Estop and the axis control need to be out of Estop for the relay to be on.
Here is the relevent code.
# --- ESTOP-OUT ---
net estop-out hm2_5i25.0.7i77.0.0.output-07
# ---estop signals---
net estop-loopout iocontrol.0.emc-enable-in <= estop-latch.0.ok-out
net estop-loopin <= iocontrol.0.user-enable-out => estop-latch.0.ok-in
net estop-reset iocontrol.0.user-request-enable => estop-latch.0.reset
net remote-estop estop-latch.0.fault-in <= hm2_5i25.0.7i77.0.0.input-00-not
Thanks in advance for any help
MarkD
Attachment not found
Attachment not found
You need to use estop-latch.0.fault-out
Please Log in to join the conversation.
- markd
- Topic Author
- New Member
-
- Thank you received: 0
I added the line
net estop-out <= estop-latch.0.fault-out
The Estop loop now works as expected.