Parker AC10 via mb2hal: unreliable communication

More
5 years 1 month ago #221908 by plovdiv
I'm connecting to a Parker AC10 VFD via USB/Modbus from linuxcnc 2.8.2.
But the connection is unreliable. There are sucessfull commands but a lot of errors too:
CRC
Connection timed out: select
Request for slave 128 ignored (not 1)

Looks like a physical i.e. wiring problem, but there is a nicely terminated twisted pair wiring between VFD and USBtoRS485.
Even more the same wiring worked well with the Parkers antecessor a huangyang VFD.

Any ideas?



 

Please Log in to join the conversation.

More
5 years 4 weeks ago #221960 by andypugh
Not really a solution, but I see a lot of failed updates with my HY VFD under modbus control when I look at the output.

My solution is not to look at the output :-)

The spindle seems to work just fine.

Please Log in to join the conversation.

More
5 years 4 weeks ago #221964 by plovdiv

Not really a solution, but I see a lot of failed updates with my HY VFD under modbus control when I look at the output.
My solution is not to look at the output :-)
The spindle seems to work just fine.
:) I'ld love to not look, but dropout rate is to high.
Optical isolated USB/RS485 and new wiring will be the next in poking around in the dark.

Please Log in to join the conversation.

More
5 years 4 weeks ago #221982 by persei8
How much different is that VFD from a Huanyang? If it's close, you are welcome to try out my custom made VFD HAL component. It was made specifically for a GT Series but if you can program a bit, it should be adaptable. It can go for hours without a single communication error.
Jim

Please Log in to join the conversation.

More
5 years 4 weeks ago #222002 by 0x2102
Try using an RS485 adapter with A/B and GND connection instead of those simple USB with A/B only. I had similar issues before, if I remember correctly.

Please Log in to join the conversation.

More
5 years 3 weeks ago #222483 by Todd Zuercher
I had a problem with a bunch of Lenze ACTech drives, where if the commanded speed was less than the minimum setting set in the drive the communication would show a Modbus comm error in Linuxcnc. So when ever the spindle was stopped and the speed was set to zero I saw a constant string of comm errors. The slolution was to disable the minimum speed limit in the drive and do the limiting in Linuxcnc. No more comm errors.

Please Log in to join the conversation.

More
5 years 3 weeks ago #222499 by plovdiv
Meanwhile I could solve the case by using another USB2RS485 adaptor..

The old one showed some weird behavior on the scope. With only 250 mV dU between A+ and B- it was inside standard but obviously outside the parker AC10s expectations. 

Attachment not found

.

The new one (with GND connection by the way) showed of better :) 

Attachment not found

Please Log in to join the conversation.