I have closed the loop, need a little help with PID tuning

More
2 years 7 months ago #296626 by slowpoke
Focus is on X axis, if I can get that sorted should be easy to implement the other joints.

System:

Ditron linear scales feeding both a Ditron DRO and encoder 0 on Mesa 7i95t.

ac servo that has integrated encoder feeding back to ac servo driver hardware, So I could also tune the ac servos PID parameters, however when operating in LinuxCNC open loop mode the ac servo settings are behaving rather well. Fast, no hunting basically perfect except ballscrew error of about 0.005" that is easily measured between external DRO displayed value vs. value in Axis.
Update on backlash:  I created two near identical versions (one open loop with backlash compensation) and the other closed loop. The open loop with compensation is actually quite accurate. With backlash compensation enabled in the the closed loop version it actually makes things much worse and introduces an error of the backlash value on each move, so interesting but not helping.

Using tommylights as well as Hakan's zx45 hal and ini examples I now have my system operating closed loop.

With high vales of P(1000) my system hunts excessively, as I decrease P; 400,200,100,50,25,10, 5 the hunting goes from pretty wild to barely perceivable with error oscillating very slowly (a few tenths over 2 seconds). Sometimes it undershoots an other times it overshoots and then corrects.

I have no experience tuning PID loops other than using the self tuning feature for the ac servos which seemed to work however I learned little during the process.

I have attached my  .ini and hal files

Advice please.
 

Attachment not found



 

Attachment not found

Attachment not found

Attachment not found

Please Log in to join the conversation.

More
2 years 7 months ago #296636 by chris@cnc
You must decide what PID is the master.
In open loop is P1000 normal value in linuxcnc ini. In closed loop you should start with P1 and go slowly higher.
Quick and dirty guide -> If your axis starts to oscillating, decrease P 10%. You could also try to add a deadband value.
Next step cut a circle and if round good job.

Other idea is to decrease the PID in Servodrive and increase P in linuxcnc. High end tune is to look in halshow how close command and feedback position together.
But this need much time, much coffee and little luck.

Please Log in to join the conversation.

More
2 years 7 months ago #296643 by cakeslob
if its using linear scales, do you even need backlash comp?

Please Log in to join the conversation.

More
2 years 7 months ago #296644 by slowpoke

if its using linear scales, do you even need backlash comp?
 

Answer appears to be NO, backlash compensation in closed loop makes things worse.

Focus is now on PID tuning, any PID tuning advice is welcome.

Please Log in to join the conversation.

More
2 years 7 months ago #296645 by PCW
Backlash compensation makes no sense with linear scale feedback
(since the scales don't have any backlash and represent the actual position very closely)

With linear scale feedback, you can correct for various ballscrew
errors, including scale, periodic and expansion, BUT you cannot easily fix
backlash, This is best eliminated mechanically.

 

Please Log in to join the conversation.

More
2 years 7 months ago #296652 by slowpoke

Backlash compensation makes no sense with linear scale feedback
(since the scales don't have any backlash and represent the actual position very closely)

With linear scale feedback, you can correct for various ballscrew
errors, including scale, periodic and expansion, BUT you cannot easily fix
backlash, This is best eliminated mechanically.
Thanks,
I sort of figured that out with my backlash compensated open-loop vs, closed-loop test (results above).

I do have some angular contact bearings that I might install to reduce, however for the moment I'm going to try and see if I can find PID parameters that will work, at the moment I need to turn P way down to stop hunting.

Any and all PID tuning advice is welcome.

If all else fails, I'm going to go back to the ac servo tuning software but I much prefer to try and solve this with Linux PID control.

Please Log in to join the conversation.

More
2 years 7 months ago #296664 by tommylight
FF1 is still 1 in the ini file, chances are that will not be correct for almost any machine with normal output scaling, so have a play with some values, start from 0.1 increments, watch the f-error on the scope if it gets bigger or smaller after a change, if lower, try smaller increments, example 0.3 makes the least f-error so try 2.5 and 3.5, again example 2.5 has lower f-error and we know 0.3 is better than 0.2 then it must be between those values, so try 2.6, 2.7 etc.