7i76e input output singals
2 years 6 months ago #297500
by Yannis
7i76e input output singals was created by Yannis
[url=https://www.facebook.com/groups/465128047350433/user/1186219141/?__cft__[0]=AZXp2iAvjPKVttWtEo_h-9s-ccv4qEPy6k0ub7zQ0ht-JGnU3HYOsg79OvJq67HNRT6-DUJ59gB9r1Zj5rZiXV_56ofNC1C82eUB0EDDl3ndsKjJ_Tp5gudk1G1rNiIKNMmi-e_liDLK-Z-ZlLnL-0ew&__tn__=-]K-R]Hello[/url] Im trying to setup a new pc on a existing machine with 7i76e. The output singals for the spindle and the Zaxis brake are working properly .The input singals for the limit switch are not working.What m i missing here? Following the ini and hal files
Attachment not found
Attachment not found
Please Log in to join the conversation.
2 years 6 months ago #297502
by PCW
Replied by PCW on topic 7i76e input output singals
The physical switch input signals names (home-x and both-x):
#--- HOME-X ---
net home-x <=> hm2_7i76e.0.7i76.0.0.input-05
net both-x <=> hm2_7i76e.0.7i76.0.0.input-04
do not match the names (or functions) connected to LinuxCNC's motion component:
# ---setup home / limit switch signals---
net x-home-sw => joint.0.home-sw-in
net x-neg-limit => joint.0.neg-lim-sw-in
net x-pos-limit => joint.0.pos-lim-sw-in
This is true for all joints.
#--- HOME-X ---
net home-x <=> hm2_7i76e.0.7i76.0.0.input-05
net both-x <=> hm2_7i76e.0.7i76.0.0.input-04
do not match the names (or functions) connected to LinuxCNC's motion component:
# ---setup home / limit switch signals---
net x-home-sw => joint.0.home-sw-in
net x-neg-limit => joint.0.neg-lim-sw-in
net x-pos-limit => joint.0.pos-lim-sw-in
This is true for all joints.
Please Log in to join the conversation.
2 years 6 months ago #297561
by Yannis
Replied by Yannis on topic 7i76e input output singals
In my old config i have connected all the driver fault with this
# --- ALL-LIMIT ---
net all-limit <= hm2_7i76e.0.7i76.0.0.input-11
to put the machine on estop when a driver failed
How can i do that in my new config?
# --- ALL-LIMIT ---
net all-limit <= hm2_7i76e.0.7i76.0.0.input-11
to put the machine on estop when a driver failed
How can i do that in my new config?
Please Log in to join the conversation.
2 years 6 months ago #297576
by PCW
Replied by PCW on topic 7i76e input output singals
net drive_fault joint.0.amp-fault-in <= hm2_7i76e.0.7i76.0.0.input-11
or if you have free inputs:
net drive_fault_0 joint.0.amp-fault-in <= hm2_7i76e.0.7i76.0.0.input-11
net drive_fault_1 joint.1.amp-fault-in <= hm2_7i76e.0.7i76.0.0.input-12
net drive_fault_2 joint.1.amp-fault-in <= hm2_7i76e.0.7i76.0.0.input-13
Both will work(halt the machine on a a drive fault) , but the first won't
indicate which drive is at fault
or if you have free inputs:
net drive_fault_0 joint.0.amp-fault-in <= hm2_7i76e.0.7i76.0.0.input-11
net drive_fault_1 joint.1.amp-fault-in <= hm2_7i76e.0.7i76.0.0.input-12
net drive_fault_2 joint.1.amp-fault-in <= hm2_7i76e.0.7i76.0.0.input-13
Both will work(halt the machine on a a drive fault) , but the first won't
indicate which drive is at fault
Please Log in to join the conversation.
2 years 6 months ago #297625
by Yannis
Replied by Yannis on topic 7i76e input output singals
Also detect another bug
When i try to do RUN FROM HERE with right click the machine running the program from the beginning
Any suggestions
When i try to do RUN FROM HERE with right click the machine running the program from the beginning
Any suggestions
Please Log in to join the conversation.
- tommylight
-
- Offline
- Administrator
-
Less
More
- Posts: 22010
- Thank you received: 3
2 years 6 months ago #297634
by tommylight
Replied by tommylight on topic 7i76e input output singals
First left click on the line, then right click and run from here.