- Posts: 13
- Thank you received: 0
7i97t Mesaflash Problem
9 months 4 weeks ago #340848
by Robin123
Replied by Robin123 on topic 7i97t Mesaflash Problem
Furthermore, the Mesa disconnects after approximately 5 minutes with these values. The 1A Ff fuse doesn't blow, but the wire deforms. I suspect that due to increased contact resistance, the voltage at the Mesa is no longer sufficient.
Please Log in to join the conversation.
9 months 4 weeks ago #340850
by PCW
Replied by PCW on topic 7i97t Mesaflash Problem
Yes, the PWM value (from the PID component) should increase as the position
error increases.
Did you check the 5V power?
Are CR23 and CR27 (Yellow LEDs near the center of the card) both fully illuminated?
(these LEDS indicate the analog +16/-12V power supply operation)
error increases.
Did you check the 5V power?
Are CR23 and CR27 (Yellow LEDs near the center of the card) both fully illuminated?
(these LEDS indicate the analog +16/-12V power supply operation)
Please Log in to join the conversation.
9 months 4 weeks ago #340875
by Robin123
Replied by Robin123 on topic 7i97t Mesaflash Problem
The lower LED is slightly dim. I adjusted the voltage; it was 4.6V, now it's 5.1V. When I move the axis, the fuse trips immediately, but the wire only deforms slightly more. Is 1A too low, or is the Mesa fuse defective?
Please Log in to join the conversation.
- tommylight
-
- Away
- Administrator
-
Less
More
- Posts: 22012
- Thank you received: 3
9 months 4 weeks ago #340877
by tommylight
Replied by tommylight on topic 7i97t Mesaflash Problem
I would venture a guess at wrong wiring, so first check if analog grounds are wired correctly, from your explanation this seems to be the reason.
Please Log in to join the conversation.
9 months 4 weeks ago #340878
by Robin123
Replied by Robin123 on topic 7i97t Mesaflash Problem
I haven't wired them up yet, but the fuse issue also happened when the power amplifiers were connected.
Please Log in to join the conversation.
9 months 4 weeks ago #340885
by PCW
Replied by PCW on topic 7i97t Mesaflash Problem
What Mesa fuse? There are PTCs to protect the 5V encoder wiring, if these trip, you have a wiring error.
Please Log in to join the conversation.
9 months 4 weeks ago #340887
by Robin123
Replied by Robin123 on topic 7i97t Mesaflash Problem
I installed a 1A FF miniature fuse for the Mesa.
Please Log in to join the conversation.
9 months 4 weeks ago #340892
by PCW
Replied by PCW on topic 7i97t Mesaflash Problem
If a 1A fuse blows with no encoders connected and analog outputs open (or at least not shorted).
the 7I97T is damaged...
the 7I97T is damaged...
Please Log in to join the conversation.