Huanyang VFD and Mesa 7i76e stuck at 6000 rpm

More
6 years 3 months ago #175326 by Stran_ge
I edited the Spindle part of my hal as following:
Code:
loadrt timedelay count=1 loadrt lincurve personality=4 addf timedelay.0 servo-thread addf lincurve.0 servo-thread setp timedelay.0.on-delay 4 setp timedelay.0.off-delay 0 #******************* # SPINDLE #******************* setp pid.s.Pgain [SPINDLE_0]P setp pid.s.Igain [SPINDLE_0]I setp pid.s.Dgain [SPINDLE_0]D setp pid.s.bias [SPINDLE_0]BIAS setp pid.s.FF0 [SPINDLE_0]FF0 setp pid.s.FF1 [SPINDLE_0]FF1 setp pid.s.FF2 [SPINDLE_0]FF2 setp pid.s.deadband [SPINDLE_0]DEADBAND setp pid.s.maxoutput [SPINDLE_0]MAX_OUTPUT setp pid.s.error-previous-target true # ---auto rpm: 1-6000 = 6000 / 24000 max setp lincurve.0.x-val-00 0 setp lincurve.0.y-val-00 0 setp lincurve.0.x-val-01 1 setp lincurve.0.y-val-01 6000 setp lincurve.0.x-val-02 6000 setp lincurve.0.y-val-02 6000 setp lincurve.0.x-val-03 24000 setp lincurve.0.y-val-03 24000 net spindle-index-enable <=> pid.s.index-enable net spindle-enable => pid.s.enable net spindle-vel-cmd-rpm-abs => pid.s.command net spindle-vel-fb-rpm-abs => pid.s.feedback net spindle-output <= pid.s.output # ---digital potentionmeter output signals/setup--- setp hm2_7i76e.0.7i76.0.0.spinout-minlim [SPINDLE_0]OUTPUT_MIN_LIMIT setp hm2_7i76e.0.7i76.0.0.spinout-maxlim [SPINDLE_0]OUTPUT_MAX_LIMIT setp hm2_7i76e.0.7i76.0.0.spinout-scalemax [SPINDLE_0]OUTPUT_SCALE net spindle-output => hm2_7i76e.0.7i76.0.0.spinout net spindle-enable => hm2_7i76e.0.7i76.0.0.spinena net spindle-ccw => hm2_7i76e.0.7i76.0.0.spindir # ---setup spindle control signals--- net spindle-vel-cmd-rps <= spindle.0.speed-out-rps net spindle-vel-cmd-rps-abs <= spindle.0.speed-out-rps-abs net spindle-vel-cmd-rpm <= spindle.0.speed-out net spindle-pre <= spindle.0.speed-out-abs lincurve.0.in net spindle-vel-cmd-rpm-abs <= lincurve.0.out net spindle-enable <= spindle.0.on net spindle-cw <= spindle.0.forward net spindle-ccw <= spindle.0.reverse net spindle-brake <= spindle.0.brake net spindle-revs => spindle.0.revs net spindle-at-speed => spindle.0.at-speed timedelay.0.out net spindle-vel-fb-rps => spindle.0.speed-in net spindle-index-enable <=> spindle.0.index-enable # ---Setup spindle at speed signals--- #sets spindle-at-speed true

When i start my spindle it starts at 9xxx rpm instead of 6000 when i type M3 S24000 i only reach 22xxx rpm and for everything else the values are higher than what i typed in.


This is the Spindle part of my Ini:
Code:
[SPINDLE_0] P = 0.0 I = 0.0 D = 0.0 FF0 = 1.0 FF1 = 0.0 FF2 = 0.0 BIAS = 0.0 DEADBAND = 0.0 MAX_OUTPUT = 24000.0 OUTPUT_SCALE = 26000 OUTPUT_MIN_LIMIT = 0 OUTPUT_MAX_LIMIT = 24000


I will attach the full hal and ini aswell.

Attachment not found

Attachment not found

Please Log in to join the conversation.

More
6 years 3 months ago #175334 by Stran_ge
I cant be doing everything wrong here :( , is everyone else controlling their vfd via modbus ??

Please Log in to join the conversation.

More
6 years 3 months ago #175338 by PCW
It sounds like the drive runs at 6000 RPM for 0V input
if so the lincurve values are wrong since you want a
Y value (output) of 0 at a commanded RPM of 6000

Also if you have a output scale of 26000 and a maxoutput of 24000
you can never get full output (these should both be left at 24000)

Please Log in to join the conversation.

More
6 years 3 months ago #175340 by Stran_ge
the thing is at m3 s1 where it shouldnt be turning i measure 0.03v and get perfect 6000 rpm
at m3 s6000 i get 2.3 v and 10300 rpm and at m3 s7000 i get 2.7 volt and 11000 rpm

i already changed that output scale back to 24000 but it didnt change anything

Please Log in to join the conversation.

More
6 years 3 months ago #175341 by PCW
Right, so your linscale values are wrong,
Y should be 0 when X is 6000, you have that backwards

Please Log in to join the conversation.

More
6 years 3 months ago #175343 by Stran_ge
so it should be this way:

Code:
# ---auto rpm: 1-6000 = 6000 / 24000 max setp lincurve.0.x-val-00 0 setp lincurve.0.y-val-00 0 setp lincurve.0.x-val-01 6000 setp lincurve.0.y-val-01 0 setp lincurve.0.x-val-02 6000 setp lincurve.0.y-val-02 6000 setp lincurve.0.x-val-03 24000 setp lincurve.0.y-val-03 24000

Please Log in to join the conversation.

More
6 years 3 months ago #175344 by PCW
Point 02 is wrong and will cause you to get about 2.5V with a 6000 RPM command instead of 0V

Do you get 24000 RPM at 10V?

Please Log in to join the conversation.

More
6 years 3 months ago #175345 by Stran_ge
the maximum is 23xxx rpm at 9.1 volt

Please Log in to join the conversation.

More
6 years 3 months ago #175346 by PCW
So you really only need 3 points for lincurve (you could actually do the same thing with the scale component since you are just offsetting the analog output by 6000 )

setp lincurve.0.x-val-00 0
setp lincurve.0.y-val-00 0
setp lincurve.0.x-val-01 6000
setp lincurve.0.y-val-01 0
setp lincurve.0.x-val-02 24000
setp lincurve.0.y-val-02 24000

Please Log in to join the conversation.

More
6 years 3 months ago #175347 by Stran_ge
i changed the hal part and now when i start the spindle it starts at 6000 but i cant change the speed anymore.

I can start stop and change direction nothing else.

The Output voltage stays the same whatever i input via m3 sxxxxx


i appreciate the help so far, im trying to get this working correctly for the past 2 days