Mesa 5i25 + 7i77D can't cofig

More
5 years 6 months ago #207375 by tommylight
OK that seems good, for Z set it to 1 or 2 and try again.
Then set the jog velocity to very slow and try to jog very shortly in both directions for each axis. If any of them "jump" the direction for the output or the encoder has to be reversed in hal.

Please Log in to join the conversation.

More
5 years 6 months ago #207380 by PCW
Replied by PCW on topic Mesa 5i25 + 7i77D can't cofig
Jerks/overshoots when jogging can be caused by incorrect (too high) FF1

Please Log in to join the conversation.

More
5 years 6 months ago #207394 by Taichi
Can you explain me what means that all parameters in servo tune?

I read your instructions maybe hundred times.
In English can't fully understand what you mean. Google translate bad working with technical words. Excuse me if i make stupid question.

I understood what you said about different direction of encoder and motor. Motor drift to positive side and encoder counting to negative side. Linuxcnc think that need to compensate in analogoutN. Encoder counting faster to same direction, close loop and we have rise amplitude vibration.

jog.n.f-error its that parameter who show bad fluctuations when PID controller try to move servo?
Minimum fluctuations = maximum performance

Please Log in to join the conversation.

More
5 years 6 months ago #207401 by tommylight
I think wee need to do this step by step since a lot of info gets lost in translation.
Do the drives disable and enable with F2 ?
This is the first thing to have working.

Please Log in to join the conversation.

More
5 years 6 months ago #207403 by PCW
Replied by PCW on topic Mesa 5i25 + 7i77D can't cofig
To avoid jerks/oscillations set all P terms to say 2
and _all_ other PID terms to 0 to start

Then you need to look at one of the tuning tutorials,
open the calibrate menus and tune one parameter
on one axis at a time.

Please Log in to join the conversation.

More
5 years 6 months ago #207474 by Taichi
Today i worked with one axes X.
I set P value to 20 and FF1 to 0
Then stepped by instructions i got:
P value: 40
FF1:0.22
Motor on 60mm/m run smooth and silent.
But in stop position, DRO make little jumps and in f-error line was some little amplitude noise. I heard vibration.
I decided to grounded computer directly to ground line.
And know what, noise disappeared. I got nice horizontal line in f-error signal. Motor stand still, DRO not moved.

In calibration menu i corrected FF1 to 0.24 and line f-error stand at center. On start/stop ware splash line. So i changed FF2 value to 0.0008.

What i have:
P = 40
FF1 = 0.24
FF2 = 0.0008

From 1 to 240mm/m motor move without hits and f-error signal so little change. But in 250mm/m amplitude f-error rise over 20 times and motor start/stop with hits.

In manual written thar servo/joint can move with 10000/5000 mm/m (reduction ratio 2/1)

Need to tune more?
Photo after tune.

Attachment not found


Code:
# Generated by PNCconf at Wed Feb 17 18:23:45 2021 # Using LinuxCNC version: 2.8 # Все изменения в этом файле будут перезаписаны # overwritten when you run PNCconf again [EMC] MACHINE = Strausak DEBUG = 0 VERSION = 1.1 [DISPLAY] DISPLAY = gmoccapy POSITION_OFFSET = RELATIVE POSITION_FEEDBACK = ACTUAL MAX_FEED_OVERRIDE = 2.000000 MAX_SPINDLE_OVERRIDE = 1.000000 MIN_SPINDLE_OVERRIDE = 0.500000 INTRO_GRAPHIC = linuxcnc.gif INTRO_TIME = 5 PROGRAM_PREFIX = /home/taichi/linuxcnc/nc_files INCREMENTS = 5mm 1mm .5mm .1mm .05mm .01mm .005mm POSITION_FEEDBACK = ACTUAL DEFAULT_LINEAR_VELOCITY = 6.000000 MAX_LINEAR_VELOCITY = 25.000000 MIN_LINEAR_VELOCITY = 0.500000 DEFAULT_ANGULAR_VELOCITY = 12.000000 MAX_ANGULAR_VELOCITY = 180.000000 MIN_ANGULAR_VELOCITY = 1.666667 EDITOR = gedit GEOMETRY = xyzab #EMBED_TAB_NAME = left_side_panel #EMBED_TAB_LOCATION = box_left #EMBED_TAB_COMMAND = gladevcp -g 64x697+997+10 -H v_buttonlist.hal v_buttonlist.glade #EMBED_TAB_NAME = right_side_panel #EMBED_TAB_LOCATION = box_right #EMBED_TAB_COMMAND = gladevcp -g 995x64+0+805 -H h_buttonlist.hal h_buttonlist.glade [FILTER] PROGRAM_EXTENSION = .png,.gif,.jpg Greyscale Depth Image PROGRAM_EXTENSION = .py Python Script png = image-to-gcode gif = image-to-gcode jpg = image-to-gcode py = python [TASK] TASK = milltask CYCLE_TIME = 0.010 [RS274NGC] PARAMETER_FILE = linuxcnc.var [EMCMOT] EMCMOT = motmod COMM_TIMEOUT = 1.0 SERVO_PERIOD = 1000000 [HMOT] # **** This is for info only **** CARD0=hm2_5i25.0 [HAL] HALUI = halui HALFILE = Strausak.hal HALFILE = custom.hal POSTGUI_HALFILE = postgui_call_list.hal SHUTDOWN = shutdown.hal [HALUI] [KINS] JOINTS = 5 KINEMATICS = trivkins coordinates=XYZAB [TRAJ] COORDINATES = XYZAB MAX_ANGULAR_VELOCITY = 33.33 DEFAULT_ANGULAR_VELOCITY = 3.33 LINEAR_UNITS = mm ANGULAR_UNITS = degree DEFAULT_LINEAR_VELOCITY = 5.00 MAX_LINEAR_VELOCITY = 50.00 NO_FORCE_HOMING = 1 [EMCIO] EMCIO = io CYCLE_TIME = 0.100 TOOL_TABLE = tool.tbl #****************************************** [AXIS_X] MAX_VELOCITY = 50.0 MAX_ACCELERATION = 200.0 MIN_LIMIT = -0.01 MAX_LIMIT = 350.0 [JOINT_0] TYPE = LINEAR HOME = 0.0 FERROR = 10.0 MIN_FERROR = 1.0 MAX_VELOCITY = 50.0 MAX_ACCELERATION = 200.0 P = 40 I = 0 D = 0 FF0 = 0 FF1 = 0.238 FF2 = 0.0011 BIAS = 0 DEADBAND = 0 MAX_OUTPUT = 1 ENCODER_SCALE = -20000 OUTPUT_SCALE = -10 OUTPUT_MIN_LIMIT = -10 OUTPUT_MAX_LIMIT = 10 MIN_LIMIT = -0.01 MAX_LIMIT = 350.0 HOME_OFFSET = 0.0 #****************************************** #****************************************** [AXIS_Y] MAX_VELOCITY = 50.0 MAX_ACCELERATION = 200.0 MIN_LIMIT = -0.01 MAX_LIMIT = 2350000.0 [JOINT_1] TYPE = LINEAR HOME = 0.0 FERROR = 10.0 MIN_FERROR = 1.0 MAX_VELOCITY = 50.0 MAX_ACCELERATION = 200.0 P = 30 I = 0 D = 0 FF0 = 0 FF1 = 0 FF2 = 0 BIAS = 0 DEADBAND = 0 MAX_OUTPUT = 0 ENCODER_SCALE = 20000 OUTPUT_SCALE = 10 OUTPUT_MIN_LIMIT = -10 OUTPUT_MAX_LIMIT = 10 MIN_LIMIT = -0.01 MAX_LIMIT = 2350000.0 HOME_OFFSET = 0.0 #****************************************** #****************************************** [AXIS_Z] MAX_VELOCITY = 50.0 MAX_ACCELERATION = 200.0 MIN_LIMIT = -350.0 MAX_LIMIT = 0.01 [JOINT_2] TYPE = LINEAR HOME = 0.0 FERROR = 10.0 MIN_FERROR = 1.0 MAX_VELOCITY = 50.0 MAX_ACCELERATION = 200.0 P = 30 I = 0 D = 0 FF0 = 0 FF1 = 0 FF2 = 0 BIAS = 0 DEADBAND = 0 MAX_OUTPUT = 0 ENCODER_SCALE = -20000 OUTPUT_SCALE = -10 OUTPUT_MIN_LIMIT = -10 OUTPUT_MAX_LIMIT = 10 MIN_LIMIT = -350.0 MAX_LIMIT = 0.01 HOME_OFFSET = 0.0 #****************************************** #****************************************** [AXIS_A] MAX_VELOCITY = 33.3333333333 MAX_ACCELERATION = 100.0 MIN_LIMIT = -9999.0 MAX_LIMIT = 9999.0 [JOINT_3] TYPE = ANGULAR HOME = 0.0 FERROR = 0.5 MIN_FERROR = 0.05 MAX_VELOCITY = 33.3333333333 MAX_ACCELERATION = 100.0 P = 30 I = 0 D = 0 FF0 = 0 FF1 = 0 FF2 = 0 BIAS = 0 DEADBAND = 0 MAX_OUTPUT = 0 ENCODER_SCALE = 4166.667 OUTPUT_SCALE = 10 OUTPUT_MIN_LIMIT = -10 OUTPUT_MAX_LIMIT = 10 MIN_LIMIT = -9999.0 MAX_LIMIT = 9999.0 HOME_OFFSET = 0.0 #****************************************** #****************************************** [AXIS_B] MAX_VELOCITY = 33.3333333333 MAX_ACCELERATION = 100.0 MIN_LIMIT = -9999.0 MAX_LIMIT = 9999.0 [JOINT_4] TYPE = ANGULAR HOME = 0.0 FERROR = 0.5 MIN_FERROR = 0.05 MAX_VELOCITY = 33.3333333333 MAX_ACCELERATION = 100.0 P = 30 I = 0 D = 0 FF0 = 0 FF1 = 0 FF2 = 0 BIAS = 0 DEADBAND = 0 MAX_OUTPUT = 0 ENCODER_SCALE = 4166.667 OUTPUT_SCALE = 10 OUTPUT_MIN_LIMIT = -10 OUTPUT_MAX_LIMIT = 10 MIN_LIMIT = -9999.0 MAX_LIMIT = 9999.0 HOME_OFFSET = 0.0 #****************************************** [SPINDLE_0] P = 0 I = 0 D = 0 FF0 = 1 FF1 = 0 FF2 = 0 BIAS = 0 DEADBAND = 0 MAX_OUTPUT = 2000
Code:
# Generated by PNCconf at Wed Feb 17 18:23:45 2021 # Using LinuxCNC version: 2.8 # Все изменения в этом файле будут перезаписаны # overwritten when you run PNCconf again loadrt [KINS]KINEMATICS loadrt [EMCMOT]EMCMOT servo_period_nsec=[EMCMOT]SERVO_PERIOD num_joints=[KINS]JOINTS loadrt hostmot2 loadrt hm2_pci config=" num_encoders=6 num_pwmgens=0 num_stepgens=0 sserial_port_0=000xxx" setp hm2_5i25.0.watchdog.timeout_ns 5000000 loadrt pid names=pid.x,pid.y,pid.z,pid.a,pid.b,pid.s addf hm2_5i25.0.read servo-thread addf motion-command-handler servo-thread addf motion-controller servo-thread addf pid.x.do-pid-calcs servo-thread addf pid.y.do-pid-calcs servo-thread addf pid.z.do-pid-calcs servo-thread addf pid.a.do-pid-calcs servo-thread addf pid.b.do-pid-calcs servo-thread addf pid.s.do-pid-calcs servo-thread addf hm2_5i25.0.write servo-thread # external output signals # --- MACHINE-IS-ENABLED --- net machine-is-enabled => hm2_5i25.0.7i77.0.0.output-00 # external input signals #******************* # AXIS X JOINT 0 #******************* setp pid.x.Pgain [JOINT_0]P setp pid.x.Igain [JOINT_0]I setp pid.x.Dgain [JOINT_0]D setp pid.x.bias [JOINT_0]BIAS setp pid.x.FF0 [JOINT_0]FF0 setp pid.x.FF1 [JOINT_0]FF1 setp pid.x.FF2 [JOINT_0]FF2 setp pid.x.deadband [JOINT_0]DEADBAND setp pid.x.maxoutput [JOINT_0]MAX_OUTPUT setp pid.x.error-previous-target true net x-index-enable <=> pid.x.index-enable net x-enable => pid.x.enable net x-pos-cmd => pid.x.command net x-pos-fb => pid.x.feedback net x-output <= pid.x.output # ---PWM Generator signals/setup--- setp hm2_5i25.0.7i77.0.1.analogout0-scalemax [JOINT_0]OUTPUT_SCALE setp hm2_5i25.0.7i77.0.1.analogout0-minlim [JOINT_0]OUTPUT_MIN_LIMIT setp hm2_5i25.0.7i77.0.1.analogout0-maxlim [JOINT_0]OUTPUT_MAX_LIMIT net x-output => hm2_5i25.0.7i77.0.1.analogout0 net x-pos-cmd <= joint.0.motor-pos-cmd net x-enable <= joint.0.amp-enable-out # enable _all_ sserial pwmgens net x-enable => hm2_5i25.0.7i77.0.1.analogena # ---Encoder feedback signals/setup--- setp hm2_5i25.0.encoder.00.counter-mode 0 setp hm2_5i25.0.encoder.00.filter 1 setp hm2_5i25.0.encoder.00.index-invert 0 setp hm2_5i25.0.encoder.00.index-mask 0 setp hm2_5i25.0.encoder.00.index-mask-invert 0 setp hm2_5i25.0.encoder.00.scale [JOINT_0]ENCODER_SCALE net x-pos-fb <= hm2_5i25.0.encoder.00.position net x-vel-fb <= hm2_5i25.0.encoder.00.velocity net x-pos-fb => joint.0.motor-pos-fb net x-index-enable joint.0.index-enable <=> hm2_5i25.0.encoder.00.index-enable net x-pos-rawcounts <= hm2_5i25.0.encoder.00.rawcounts # ---setup home / limit switch signals--- net x-home-sw => joint.0.home-sw-in net x-neg-limit => joint.0.neg-lim-sw-in net x-pos-limit => joint.0.pos-lim-sw-in #******************* # AXIS Y JOINT 1 #******************* setp pid.y.Pgain [JOINT_1]P setp pid.y.Igain [JOINT_1]I setp pid.y.Dgain [JOINT_1]D setp pid.y.bias [JOINT_1]BIAS setp pid.y.FF0 [JOINT_1]FF0 setp pid.y.FF1 [JOINT_1]FF1 setp pid.y.FF2 [JOINT_1]FF2 setp pid.y.deadband [JOINT_1]DEADBAND setp pid.y.maxoutput [JOINT_1]MAX_OUTPUT setp pid.y.error-previous-target true net y-index-enable <=> pid.y.index-enable net y-enable => pid.y.enable net y-pos-cmd => pid.y.command net y-pos-fb => pid.y.feedback net y-output <= pid.y.output # ---PWM Generator signals/setup--- setp hm2_5i25.0.7i77.0.1.analogout1-scalemax [JOINT_1]OUTPUT_SCALE setp hm2_5i25.0.7i77.0.1.analogout1-minlim [JOINT_1]OUTPUT_MIN_LIMIT setp hm2_5i25.0.7i77.0.1.analogout1-maxlim [JOINT_1]OUTPUT_MAX_LIMIT net y-output => hm2_5i25.0.7i77.0.1.analogout1 net y-pos-cmd <= joint.1.motor-pos-cmd net y-enable <= joint.1.amp-enable-out # ---Encoder feedback signals/setup--- setp hm2_5i25.0.encoder.01.counter-mode 0 setp hm2_5i25.0.encoder.01.filter 1 setp hm2_5i25.0.encoder.01.index-invert 0 setp hm2_5i25.0.encoder.01.index-mask 0 setp hm2_5i25.0.encoder.01.index-mask-invert 0 setp hm2_5i25.0.encoder.01.scale [JOINT_1]ENCODER_SCALE net y-pos-fb <= hm2_5i25.0.encoder.01.position net y-vel-fb <= hm2_5i25.0.encoder.01.velocity net y-pos-fb => joint.1.motor-pos-fb net y-index-enable joint.1.index-enable <=> hm2_5i25.0.encoder.01.index-enable net y-pos-rawcounts <= hm2_5i25.0.encoder.01.rawcounts # ---setup home / limit switch signals--- net y-home-sw => joint.1.home-sw-in net y-neg-limit => joint.1.neg-lim-sw-in net y-pos-limit => joint.1.pos-lim-sw-in #******************* # AXIS Z JOINT 2 #******************* setp pid.z.Pgain [JOINT_2]P setp pid.z.Igain [JOINT_2]I setp pid.z.Dgain [JOINT_2]D setp pid.z.bias [JOINT_2]BIAS setp pid.z.FF0 [JOINT_2]FF0 setp pid.z.FF1 [JOINT_2]FF1 setp pid.z.FF2 [JOINT_2]FF2 setp pid.z.deadband [JOINT_2]DEADBAND setp pid.z.maxoutput [JOINT_2]MAX_OUTPUT setp pid.z.error-previous-target true net z-index-enable <=> pid.z.index-enable net z-enable => pid.z.enable net z-pos-cmd => pid.z.command net z-pos-fb => pid.z.feedback net z-output <= pid.z.output # ---PWM Generator signals/setup--- setp hm2_5i25.0.7i77.0.1.analogout2-scalemax [JOINT_2]OUTPUT_SCALE setp hm2_5i25.0.7i77.0.1.analogout2-minlim [JOINT_2]OUTPUT_MIN_LIMIT setp hm2_5i25.0.7i77.0.1.analogout2-maxlim [JOINT_2]OUTPUT_MAX_LIMIT net z-output => hm2_5i25.0.7i77.0.1.analogout2 net z-pos-cmd <= joint.2.motor-pos-cmd net z-enable <= joint.2.amp-enable-out # ---Encoder feedback signals/setup--- setp hm2_5i25.0.encoder.02.counter-mode 0 setp hm2_5i25.0.encoder.02.filter 1 setp hm2_5i25.0.encoder.02.index-invert 0 setp hm2_5i25.0.encoder.02.index-mask 0 setp hm2_5i25.0.encoder.02.index-mask-invert 0 setp hm2_5i25.0.encoder.02.scale [JOINT_2]ENCODER_SCALE net z-pos-fb <= hm2_5i25.0.encoder.02.position net z-vel-fb <= hm2_5i25.0.encoder.02.velocity net z-pos-fb => joint.2.motor-pos-fb net z-index-enable joint.2.index-enable <=> hm2_5i25.0.encoder.02.index-enable net z-pos-rawcounts <= hm2_5i25.0.encoder.02.rawcounts # ---setup home / limit switch signals--- net z-home-sw => joint.2.home-sw-in net z-neg-limit => joint.2.neg-lim-sw-in net z-pos-limit => joint.2.pos-lim-sw-in #******************* # AXIS A JOINT 3 #******************* setp pid.a.Pgain [JOINT_3]P setp pid.a.Igain [JOINT_3]I setp pid.a.Dgain [JOINT_3]D setp pid.a.bias [JOINT_3]BIAS setp pid.a.FF0 [JOINT_3]FF0 setp pid.a.FF1 [JOINT_3]FF1 setp pid.a.FF2 [JOINT_3]FF2 setp pid.a.deadband [JOINT_3]DEADBAND setp pid.a.maxoutput [JOINT_3]MAX_OUTPUT setp pid.a.error-previous-target true net a-index-enable <=> pid.a.index-enable net a-enable => pid.a.enable net a-pos-cmd => pid.a.command net a-pos-fb => pid.a.feedback net a-output <= pid.a.output # ---PWM Generator signals/setup--- setp hm2_5i25.0.7i77.0.1.analogout3-scalemax [JOINT_3]OUTPUT_SCALE setp hm2_5i25.0.7i77.0.1.analogout3-minlim [JOINT_3]OUTPUT_MIN_LIMIT setp hm2_5i25.0.7i77.0.1.analogout3-maxlim [JOINT_3]OUTPUT_MAX_LIMIT net a-output => hm2_5i25.0.7i77.0.1.analogout3 net a-pos-cmd <= joint.3.motor-pos-cmd net a-enable <= joint.3.amp-enable-out # ---Encoder feedback signals/setup--- setp hm2_5i25.0.encoder.03.counter-mode 0 setp hm2_5i25.0.encoder.03.filter 1 setp hm2_5i25.0.encoder.03.index-invert 0 setp hm2_5i25.0.encoder.03.index-mask 0 setp hm2_5i25.0.encoder.03.index-mask-invert 0 setp hm2_5i25.0.encoder.03.scale [JOINT_3]ENCODER_SCALE net a-pos-fb <= hm2_5i25.0.encoder.03.position net a-vel-fb <= hm2_5i25.0.encoder.03.velocity net a-pos-fb => joint.3.motor-pos-fb net a-index-enable joint.3.index-enable <=> hm2_5i25.0.encoder.03.index-enable net a-pos-rawcounts <= hm2_5i25.0.encoder.03.rawcounts # ---setup home / limit switch signals--- net a-home-sw => joint.3.home-sw-in net a-neg-limit => joint.3.neg-lim-sw-in net a-pos-limit => joint.3.pos-lim-sw-in #******************* # AXIS B JOINT 4 #******************* setp pid.b.Pgain [JOINT_4]P setp pid.b.Igain [JOINT_4]I setp pid.b.Dgain [JOINT_4]D setp pid.b.bias [JOINT_4]BIAS setp pid.b.FF0 [JOINT_4]FF0 setp pid.b.FF1 [JOINT_4]FF1 setp pid.b.FF2 [JOINT_4]FF2 setp pid.b.deadband [JOINT_4]DEADBAND setp pid.b.maxoutput [JOINT_4]MAX_OUTPUT setp pid.b.error-previous-target true net b-index-enable <=> pid.b.index-enable net b-enable => pid.b.enable net b-pos-cmd => pid.b.command net b-pos-fb => pid.b.feedback net b-output <= pid.b.output # ---PWM Generator signals/setup--- setp hm2_5i25.0.7i77.0.1.analogout4-scalemax [JOINT_4]OUTPUT_SCALE setp hm2_5i25.0.7i77.0.1.analogout4-minlim [JOINT_4]OUTPUT_MIN_LIMIT setp hm2_5i25.0.7i77.0.1.analogout4-maxlim [JOINT_4]OUTPUT_MAX_LIMIT net b-output => hm2_5i25.0.7i77.0.1.analogout4 net b-pos-cmd <= joint.4.motor-pos-cmd net b-enable <= joint.4.amp-enable-out # ---Encoder feedback signals/setup--- setp hm2_5i25.0.encoder.04.counter-mode 0 setp hm2_5i25.0.encoder.04.filter 1 setp hm2_5i25.0.encoder.04.index-invert 0 setp hm2_5i25.0.encoder.04.index-mask 0 setp hm2_5i25.0.encoder.04.index-mask-invert 0 setp hm2_5i25.0.encoder.04.scale [JOINT_4]ENCODER_SCALE net b-pos-fb <= hm2_5i25.0.encoder.04.position net b-vel-fb <= hm2_5i25.0.encoder.04.velocity net b-pos-fb => joint.4.motor-pos-fb net b-index-enable joint.4.index-enable <=> hm2_5i25.0.encoder.04.index-enable net b-pos-rawcounts <= hm2_5i25.0.encoder.04.rawcounts # ---setup home / limit switch signals--- net b-home-sw => joint.4.home-sw-in net b-neg-limit => joint.4.neg-lim-sw-in net b-pos-limit => joint.4.pos-lim-sw-in #******************* # SPINDLE #******************* setp pid.s.Pgain [SPINDLE_0]P setp pid.s.Igain [SPINDLE_0]I setp pid.s.Dgain [SPINDLE_0]D setp pid.s.bias [SPINDLE_0]BIAS setp pid.s.FF0 [SPINDLE_0]FF0 setp pid.s.FF1 [SPINDLE_0]FF1 setp pid.s.FF2 [SPINDLE_0]FF2 setp pid.s.deadband [SPINDLE_0]DEADBAND setp pid.s.maxoutput [SPINDLE_0]MAX_OUTPUT setp pid.s.error-previous-target true net spindle-index-enable <=> pid.s.index-enable net spindle-enable => pid.s.enable net spindle-vel-cmd-rpm => pid.s.command net spindle-vel-fb-rpm => pid.s.feedback net spindle-output <= pid.s.output # ---setup spindle control signals--- net spindle-vel-cmd-rps <= spindle.0.speed-out-rps net spindle-vel-cmd-rps-abs <= spindle.0.speed-out-rps-abs net spindle-vel-cmd-rpm <= spindle.0.speed-out net spindle-vel-cmd-rpm-abs <= spindle.0.speed-out-abs net spindle-enable <= spindle.0.on net spindle-cw <= spindle.0.forward net spindle-ccw <= spindle.0.reverse net spindle-brake <= spindle.0.brake net spindle-revs => spindle.0.revs net spindle-at-speed => spindle.0.at-speed net spindle-vel-fb-rps => spindle.0.speed-in net spindle-index-enable <=> spindle.0.index-enable # ---Setup spindle at speed signals--- sets spindle-at-speed true #****************************** # connect miscellaneous signals #****************************** # ---HALUI signals--- net axis-select-x halui.axis.x.select net jog-x-pos halui.axis.x.plus net jog-x-neg halui.axis.x.minus net jog-x-analog halui.axis.x.analog net x-is-homed halui.joint.0.is-homed net axis-select-y halui.axis.y.select net jog-y-pos halui.axis.y.plus net jog-y-neg halui.axis.y.minus net jog-y-analog halui.axis.y.analog net y-is-homed halui.joint.1.is-homed net axis-select-z halui.axis.z.select net jog-z-pos halui.axis.z.plus net jog-z-neg halui.axis.z.minus net jog-z-analog halui.axis.z.analog net z-is-homed halui.joint.2.is-homed net axis-select-a halui.axis.a.select net jog-a-pos halui.axis.a.plus net jog-a-neg halui.axis.a.minus net jog-a-analog halui.axis.a.analog net a-is-homed halui.joint.3.is-homed net jog-selected-pos halui.axis.selected.plus net jog-selected-neg halui.axis.selected.minus net spindle-manual-cw halui.spindle.0.forward net spindle-manual-ccw halui.spindle.0.reverse net spindle-manual-stop halui.spindle.0.stop net machine-is-on halui.machine.is-on net jog-speed halui.axis.jog-speed net MDI-mode halui.mode.is-mdi # ---coolant signals--- net coolant-mist <= iocontrol.0.coolant-mist net coolant-flood <= iocontrol.0.coolant-flood # ---probe signal--- net probe-in => motion.probe-input # ---motion control signals--- net in-position <= motion.in-position net machine-is-enabled <= motion.motion-enabled # ---digital in / out signals--- # ---estop signals--- net estop-out <= iocontrol.0.user-enable-out net estop-out => iocontrol.0.emc-enable-in # ---toolchange signals for custom tool changer--- net tool-number <= iocontrol.0.tool-prep-number net tool-change-request <= iocontrol.0.tool-change net tool-change-confirmed => iocontrol.0.tool-changed net tool-prepare-request <= iocontrol.0.tool-prepare net tool-prepare-confirmed => iocontrol.0.tool-prepared

Please Log in to join the conversation.

More
5 years 6 months ago #207475 by PCW
Replied by PCW on topic Mesa 5i25 + 7i77D can't cofig
1. Can you post your current hal and ini files?

Edit I see you added these, I don't see anything wrong at first glance

2. A screen shot of the halscope plot would be a lot more legible

3. Plotting the following error versus velocity rather than position is easier to interpret

Please Log in to join the conversation.

More
5 years 6 months ago #207476 by PCW
Replied by PCW on topic Mesa 5i25 + 7i77D can't cofig

[JOINT_0]
TYPE = LINEAR
HOME = 0.0
FERROR = 10.0
MIN_FERROR = 1.0
.................................
MAX_OUTPUT = 1
^^^^^^^^^^^^^^^^^^^^^


This statement will limit the maximum output voltage to +-1V
or 1/10th of full velocity. This is likely the reason you get a following error
when attempting to move at higher speeds. it should be set to 0 or 10

Please Log in to join the conversation.

More
5 years 6 months ago #207481 by Taichi
I set max_output = 1 on first start pncconfig.
And successfully forgot about it.

Ok, weekend will end, i will try to make graphics f-error vs velocity.

You know, I don't know what the end result should look like. I have no experience in this.
Do I have to achieve a perfectly smooth graph or should the graph not go beyond of max_error in all operating modes?

Also, the time zone prevents us from communicating normally. Anyway, thanks you for the help.

Please Log in to join the conversation.

More
5 years 6 months ago #207488 by PCW
Replied by PCW on topic Mesa 5i25 + 7i77D can't cofig
The errors will always be there depending on how much you magnify them...

Your plot currently shows a peak error of 5 microns
and a error during (slow) motion of less than 1 micron.
I would say that is quite good for a standard mill,
If you can maintain that accuracy up to higher speeds.

Your current following error limits are huge (1 to 10 MM!)
If you have errors of this size it means a setup error or
hardware fault. These large following error limits are good
for tuning but should be reduced once tuning is complete

Please Log in to join the conversation.