2 years 6 months ago #298088
by jtrantow
G540 Timings (defaults too slow) was created by jtrantow
After years of using the default stepgen timings I've noticed they are much larger than needs be. Using PnCConf Wizard and selecting G540 generates:
DIRSETUP = 5000
DIRHOLD = 5000
STEPLEN = 10000
STEPSPACE = 10000
www.geckodrive.com/support/g540-manual-rev8
Step Pulse “0” Time2 uSStep Pulse “1” Time1 uSDirection Setup (Before step rising edge)200 nSDirection Setup (Hold after pulse rising edge)200 nS
PNCConf G540 timing will require 20usec per step when it only requires 3usec. I believe the PnCConf Wizard should be generating:
DIRSETUP = 200
DIRHOLD = 200
STEPLEN = 1000
STEPSPACE = 2000
I realize these timings are not the limitation in most cases. I think stepgen has similarly loose timing but I'm no longer using that. I have not tested mesact to see if this problem is across the board.
DIRSETUP = 5000
DIRHOLD = 5000
STEPLEN = 10000
STEPSPACE = 10000
www.geckodrive.com/support/g540-manual-rev8
Step Pulse “0” Time2 uSStep Pulse “1” Time1 uSDirection Setup (Before step rising edge)200 nSDirection Setup (Hold after pulse rising edge)200 nS
PNCConf G540 timing will require 20usec per step when it only requires 3usec. I believe the PnCConf Wizard should be generating:
DIRSETUP = 200
DIRHOLD = 200
STEPLEN = 1000
STEPSPACE = 2000
I realize these timings are not the limitation in most cases. I think stepgen has similarly loose timing but I'm no longer using that. I have not tested mesact to see if this problem is across the board.
Please Log in to join the conversation.
2 years 6 months ago #298097
by Aciera
Replied by Aciera on topic G540 Timings (defaults too slow)
In my opinion the PnCConf Wizard should produce a working config for a beginner.
While the default timings do seem rather conservative it would certainly not be wise to set them to the minimum values stated in the manual.
While the default timings do seem rather conservative it would certainly not be wise to set them to the minimum values stated in the manual.
Please Log in to join the conversation.
2 years 6 months ago #298396
by zz912
Replied by zz912 on topic G540 Timings (defaults too slow)
I agree with Aciera. I have bad experience with short timing. If the hardware is not ideal, a step may be lost. Longer timing has already solved my hardware problem several times.
Please Log in to join the conversation.
2 years 6 months ago #298450
by jtrantow
Replied by jtrantow on topic G540 Timings (defaults too slow)
Were these bad experiences with short timing on systems with a Mesa fpga board and G540?
I too have helped friends debug systems with PP and chinesium drivers where increasing the timing solved stepping problems.
I'm not asking for changing the timing for all boards. I do think specifically selecting the G540 driver should use values in the right ballpark. 25X DIR, 7X STEP aren't even in the same zipcode.
I've had good experience with Gecko drivers and tend to believe their specifications. I'd have less confidence in parallel port stepping. It might be reasonable to apply a 10%, 20%, or even 100% safety factor.
I emailed Gecko support to get their take on this matter and will report back when I hear more.
I too have helped friends debug systems with PP and chinesium drivers where increasing the timing solved stepping problems.
I'm not asking for changing the timing for all boards. I do think specifically selecting the G540 driver should use values in the right ballpark. 25X DIR, 7X STEP aren't even in the same zipcode.
I've had good experience with Gecko drivers and tend to believe their specifications. I'd have less confidence in parallel port stepping. It might be reasonable to apply a 10%, 20%, or even 100% safety factor.
I emailed Gecko support to get their take on this matter and will report back when I hear more.
Please Log in to join the conversation.
2 years 6 months ago #298455
by PCW
Replied by PCW on topic G540 Timings (defaults too slow)
I would probably double minimum timings for step time and step space
for adequate margins.
The setup and hold times have basically 0 effect on performance so
it's not harmful to give them larger margins.
for adequate margins.
The setup and hold times have basically 0 effect on performance so
it's not harmful to give them larger margins.
Please Log in to join the conversation.
2 years 6 months ago #299036
by jtrantow
Replied by jtrantow on topic G540 Timings (defaults too slow)
I received the following reply from Marcus Freimanis. I believe he's the designer. Based on this information I believe the following 110% values should be the g540 defaults.
DIRSETUP = 220
DIRHOLD = 220
STEPLEN = 1100
STEPSPACE = 2200
Thank you for contacting Geckodrive technical support. I apologize for missing your email when it first came in. There is zero advantage to a much longer signal being sent; the G540 will only pay attention to the minimum timing (e.g.: the first 2uS of a 10mS signal, essentially wasting 9.998mS). If it is six-in-one and half-dozen in the other it is always wise to err on the side of a longer signal as there is no explicit downside as long as you can output the frequency you need with that pulse timing. The only reason you would NEED a very specific and very short signal would be if you were driving the motor to run at a high step pulse frequency, which would result in what would likely be a speed beyond the stall speed of the motor. A safety margin of 10% will take into account component tolerances across multiple devices. The timing on all revisions is identical and they all use the same circuit, with an HCPL2531 optoisolator. Again, my apologies for missing your email! Marcus Freimanis Geckodrive, Inc.1540 S Grand AveSanta Ana, CA 92705 P: (714) 832-8874F: (714) 832-8082 www.geckodrive.com
DIRSETUP = 220
DIRHOLD = 220
STEPLEN = 1100
STEPSPACE = 2200
Thank you for contacting Geckodrive technical support. I apologize for missing your email when it first came in. There is zero advantage to a much longer signal being sent; the G540 will only pay attention to the minimum timing (e.g.: the first 2uS of a 10mS signal, essentially wasting 9.998mS). If it is six-in-one and half-dozen in the other it is always wise to err on the side of a longer signal as there is no explicit downside as long as you can output the frequency you need with that pulse timing. The only reason you would NEED a very specific and very short signal would be if you were driving the motor to run at a high step pulse frequency, which would result in what would likely be a speed beyond the stall speed of the motor. A safety margin of 10% will take into account component tolerances across multiple devices. The timing on all revisions is identical and they all use the same circuit, with an HCPL2531 optoisolator. Again, my apologies for missing your email! Marcus Freimanis Geckodrive, Inc.1540 S Grand AveSanta Ana, CA 92705 P: (714) 832-8874F: (714) 832-8082 www.geckodrive.com
Please Log in to join the conversation.
1 year 10 months ago #317010
by jasont64
Replied by jasont64 on topic G540 Timings (defaults too slow)
I'd like to report an experience I had with too-short timings.
All of my software/hardware is circa 2012 but mostly not used until now. I am using a g540 and 5i25 running hostmot2 from LinuxCNC.
I was using:
DIRSETUP = 2000
DIRHOLD = 2000
STEPLEN = 1500
STEPSPACE = 2500
With these settings, at very low velocities I was losing steps. I actually thought I had a backlash problem for some time. However, I eventually accidentally tried jogging at extremely low speed and noticed nothing happened at all, and after some time my position was significantly off from what LinuxCNC displayed.
Based on another thread here, I tried some more conservative timings:
DIRSETUP = 2000
DIRHOLD = 2000
STEPLEN = 5000
STEPSPACE = 5000
With these settings, my problems are gone. So if you are running at very tight settings, I recommend you try jogging at extremely low velocity and see if you get into a mode where the axis does not move, just in case you encounter the same problem.
All of my software/hardware is circa 2012 but mostly not used until now. I am using a g540 and 5i25 running hostmot2 from LinuxCNC.
I was using:
DIRSETUP = 2000
DIRHOLD = 2000
STEPLEN = 1500
STEPSPACE = 2500
With these settings, at very low velocities I was losing steps. I actually thought I had a backlash problem for some time. However, I eventually accidentally tried jogging at extremely low speed and noticed nothing happened at all, and after some time my position was significantly off from what LinuxCNC displayed.
Based on another thread here, I tried some more conservative timings:
DIRSETUP = 2000
DIRHOLD = 2000
STEPLEN = 5000
STEPSPACE = 5000
With these settings, my problems are gone. So if you are running at very tight settings, I recommend you try jogging at extremely low velocity and see if you get into a mode where the axis does not move, just in case you encounter the same problem.