Waiting for VFD to spin up the spindle.
However, the spindle takes a few seconds to get up to speed and if the mill is close to the starting point it's possible to engage the work before the spindle is moving fast enough. I have a broken end mill to prove it. :blush:
I'd like to read in the voltage output from the vfd (VO) and compare them to set the spindle-at-speed. When I read the VO from a multimeter, it reads 0-10V as expected. I connect it to analogin1 and read it through halmeter and it jumps back and forth between 0 and 10.1, never coming to rest anywhere.
That's as far as I've gotten but I'm sure I'll need to use near to compare them.
I'm kinda feeling my way blindly here so if someone could fill in the fuzzy areas I'd be grateful.
Please Log in to join the conversation.
- Todd Zuercher
- Offline
- Platinum Member
-
- Posts: 4739
- Thank you received: 2
Please Log in to join the conversation.
Please Log in to join the conversation.
Please Log in to join the conversation.
Please Log in to join the conversation.
Can you check that the 7I77 input is OK?
Connecting one of the analog inputs to field power would be a good check
Please Log in to join the conversation.
I found that reading through the manual for the vfd a few time's enlightens onesliptonic wrote: I'm using a huanyang vfd to drive my spindle motor. I'm controlling it from a 5i25/7i77 by sending a 0-10v signal on analogout5 to the VI on the VFD. That's all working fine.
However, the spindle takes a few seconds to get up to speed and if the mill is close to the starting point it's possible to engage the work before the spindle is moving fast enough. I have a broken end mill to prove it. :blush:
I'd like to read in the voltage output from the vfd (VO) and compare them to set the spindle-at-speed. When I read the VO from a multimeter, it reads 0-10V as expected. I connect it to analogin1 and read it through halmeter and it jumps back and forth between 0 and 10.1, never coming to rest anywhere.
That's as far as I've gotten but I'm sure I'll need to use near to compare them.
I'm kinda feeling my way blindly here so if someone could fill in the fuzzy areas I'd be grateful.
pd119 (default is 150) change it to 180 for near instant speed up at start of machine it can be set between 1 - 200
Please Log in to join the conversation.