Setting up USB -> Modbus (CH340) for VFD control

More
9 years 8 months ago #88041 by Victor
Hi!

Ok, i got awesome help in my previous thread on how i would tackle my journey into LinuxCNC, so off i went and got a ASRock card with db25 connector, a BOB etc.

And i was expecting a rough entry but, i got the Live CD, followed the installation guide, got it working, did the StepConf Wizard, plugged in the BOB and amazingly it worked, i can detect Estop, limit switches etc. so i'm impressed!

However my next task on my to-do list got me pulling my hair a little bit so i would need some guidance :silly:

i was recommended to go for a USB -> Modbus dongle for VFD control and i thought it sounded great, so i got a CH340 dongle, and i thought i would need to tick a box in the configuration "Use Modbus" but to my great surprise it is much more complicated and out of my existing knowledge zone.

I have searched the forum, wiki, docs, google but it is still not clear for me. should i use HAL? or Classic Ladder?
i have read wiki.linuxcnc.org/cgi-bin/wiki.pl?VFD_Modbus and wiki.linuxcnc.org/cgi-bin/wiki.pl?ModbusToHal

this chapter got me stucked:

Create a directory under "/home/my_home/emc2" such as "/home/my_home/emc2/my_vfd" (this line i understnad :P )
Copy into "my_vfd" a sample vfd.c, modbus.c, modbus.h, and Makefile
Edit my_vfd-x.c and Makefile
Run "cp my_vfd-x my_vfd.c", "make", "sudo make install"
Copy sample linuxcnc config files in "/home/my_home/emc2/configs/myCNC/"
Edit the .hal file in "...myCNC/myCNC.hal" to "loadusr my_vfd ..." and connect HAL pins
Invoke emc2 and enjoy

sample vfd.c, modbus.c modbus.h are these empty documents i create? what is Makerfile?

So if somebody could help me get thru this it would be very appreciated!

The below link is a couple pages on the modbus section from my ENC EN600 VFD.
VFD Modbus manual

Thanks!

// Victor

Please Log in to join the conversation.

More
9 years 8 months ago #88057 by Todd Zuercher
The wiki page on ModbusToHal is a bit (alot) out of date. It was written before the release of Linuxcnc 2.6 and before MB2HAL was added to Master (then 2.6pre). MB2HAL is now part of mainline Linuxcnc so you don't have to go through the steps to compile and install it (if you are using 2.6 or later). All you need to do is configure it by adding its ini config file to your config dir and adding the right lines to your hal file.
linuxcnc.org/docs/html/drivers/mb2hal.html

I'm sure there are some sample MB2HAL configs floating around in the forum that you could look up. (I know I've posted a couple of them). If you can't find anything let me know and I'll see if I can dig up a simple example. (What I have running on the machine would not be considered a simple example as it is controlling 8 VFDs.)

If you still have questions please ask.

Please Log in to join the conversation.

More
9 years 8 months ago #88058 by Victor
Sounds like good news for me! (i run 2.7.8)

i will check some examples out and see if i can make any sense from it ;D

Thanks!

Victor

Please Log in to join the conversation.

More
9 years 8 months ago #88070 by Victor
Ok i have done some more reading and if get this correctly i need the following "files"

a .ini file for the MB2hal component?

i have named my .ini file to "mb2hal.ini" and posted the below code frome the linuxcnc.org/docs/html/drivers/mb2hal.html page
Code:
#This .INI file is also the HELP, MANUAL and HOW-TO file for mb2hal. #Load the modbus HAL userspace module as the examples below, #change to match your own HAL_MODULE_NAME and .ini file name #Using HAL_MODULE_NAME=mb2hal or nothing (default): loadusr -W mb2hal config=config_file.ini #Using HAL_MODULE_NAME=mymodule: loadusr -Wn mymodule mb2hal config=config_file.ini #Common section [MB2HAL_INIT] #OPTIONAL: Debug level of init and INI file parsing. # 0 = silent. # 1 = error messages (default). # 2 = OK confirmation messages. # 3 = debugging messages. INIT_DEBUG=3 #OPTIONAL: HAL module (component) name. Defaults to "mb2hal". HAL_MODULE_NAME=mb2hal #OPTIONAL: Insert a delay of "FLOAT seconds" between transactions in order #to not to have a lot of logging and facilitate the debugging. #Usefull when using DEBUG=3 (NOT INIT_DEBUG=3) #It affects ALL transactions. #Use "0.0" for normal activity. SLOWDOWN=0.0 #REQUIRED: The number of total Modbus transactions. There is no maximum. TOTAL_TRANSACTIONS=9 #One transaction section is required per transaction, starting at 00 and counting up sequentially. #If there is a new link (not transaction), you must provide the REQUIRED parameters 1st time. #Warning: Any OPTIONAL parameter not specified are copied from the previous transaction. [TRANSACTION_00] #REQUIRED: You must specify either a "serial" or "tcp" link for the first transaction. #Later transaction will use the previous transaction link if not specified. LINK_TYPE=tcp #if LINK_TYPE=tcp then REQUIRED (only 1st time): The Modbus slave device ip address. #if LINK_TYPE=serial then IGNORED TCP_IP=192.168.2.10 #if LINK_TYPE=tcp then OPTIONAL. #if LINK_TYPE=serial then IGNORED #The Modbus slave device tcp port. Defaults to 502. TCP_PORT=502 #if LINK_TYPE=serial then REQUIRED (only 1st time). #if LINK_TYPE=tcp then IGNORED #The serial port. SERIAL_PORT=/dev/ttyS0 #if LINK_TYPE=serial then REQUIRED (only 1st time). #if LINK_TYPE=tcp then IGNORED #The baud rate. SERIAL_BAUD=115200 #if LINK_TYPE=serial then REQUIRED (only 1st time). #if LINK_TYPE=tcp then IGNORED #Data bits. One of 5,6,7,8. SERIAL_BITS=8 #if LINK_TYPE=serial then REQUIRED (only 1st time). #if LINK_TYPE=tcp then IGNORED #Data parity. One of: even, odd, none. SERIAL_PARITY=none #if LINK_TYPE=serial then REQUIRED (only 1st time). #if LINK_TYPE=tcp then IGNORED #Stop bits. One of 1, 2. SERIAL_STOP=2 #if LINK_TYPE=serial then OPTIONAL: #if LINK_TYPE=tcp then IGNORED #Serial port delay between for this transaction only. #In ms. Defaults to 0. SERIAL_DELAY_MS=10 #REQUIRED (only 1st time). #Modbus slave number. MB_SLAVE_ID=1 #REQUIRED: The first element address. FIRST_ELEMENT=0 #REQUIRED: The number of elements. NELEMENTS=16 #REQUIRED: Modbus transaction function code (see www.modbus.org specifications). # fnct_02_read_discrete_inputs (02 = 0x02) # fnct_03_read_holding_registers (03 = 0x03) # fnct_04_read_input_registers (04 = 0x04) # fnct_15_write_multiple_coils (15 = 0x0F) # fnct_16_write_multiple_registers (16 = 0x10) #fnct_02_read_discrete_inputs: creates boolean output HAL pins. #fnct_03_read_holding_registers: creates a floating point output HAL pins. # also creates a u32 output HAL pins. #fnct_04_read_input_registers: creates a floating point output HAL pins. # also creates a u32 output HAL pins. #fnct_15_write_multiple_coils: creates boolean input HAL pins. #fnct_16_write_multiple_registers: creates a floating point input HAL pins. #The pins are named based on component name, transaction number and order number. #Example: mb2hal.00.01 (transaction=00, second register=01 (00 is the first one)) MB_TX_CODE=fnct_03_read_holding_registers #OPTIONAL: Response timeout for this transaction. In INTEGER ms. Defaults to 500 ms. #This is how much to wait for 1st byte before raise an error. MB_RESPONSE_TIMEOUT_MS=500 #OPTIONAL: Byte timeout for this transaction. In INTEGER ms. Defaults to 500 ms. #This is how much to wait from byte to byte before raise an error. MB_BYTE_TIMEOUT_MS=500 #OPTIONAL: Instead of giving the transaction number, use a name. #Example: mb2hal.00.01 could become mb2hal.plcin.01 #The name must not exceed 32 characters. #NOTE: when using names be careful that you dont end up with two transactions #usign the same name. HAL_TX_NAME=remoteIOcfg #OPTIONAL: Maximum update rate in HZ. Defaults to 0.0 (0.0 = as soon as available = infinit). #NOTE: This is a maximum rate and the actual rate may be lower. #If you want to calculate it in ms use (1000 / required_ms). #Example: 100 ms = MAX_UPDATE_RATE=10.0, because 1000.0 ms / 100.0 ms = 10.0 Hz MAX_UPDATE_RATE=0.0 #OPTIONAL: Debug level for this transaction only. #See INIT_DEBUG parameter above. DEBUG=1 #While DEBUGGING transactions note the returned "ret[]" value correspond to: #/* Modbus protocol exceptions */ #ILLEGAL_FUNCTION -0x01 the FUNCTION code received in the query is not allowed or invalid. #ILLEGAL_DATA_ADDRESS -0x02 the DATA ADDRESS received in the query is not an allowable address for the slave or is invalid. #ILLEGAL_DATA_VALUE -0x03 a VALUE contained in the data query field is not an allowable value or is invalid. #SLAVE_DEVICE_FAILURE -0x04 SLAVE (or MASTER) device unrecoverable FAILUER while attemping to perform the requested action. #SERVER_FAILURE -0x04 (see above). #ACKNOWLEDGE -0x05 This response is returned to PREVENT A TIMEOUT in the master. # A long duration of time is required to process the request in the slave. #SLAVE_DEVICE_BUSY -0x06 The slave (or server) is BUSY. Retrasmit the request later. #SERVER_BUSY -0x06 (see above). #NEGATIVE_ACKNOWLEDGE -0x07 Unsuccessful programming request using function code 13 or 14. #MEMORY_PARITY_ERROR -0x08 SLAVE parity error in MEMORY. #GATEWAY_PROBLEM_PATH -0x0A (-10) Gateway path(s) not available. #GATEWAY_PROBLEM_TARGET -0x0B (-11) The target device failed to repond (generated by master, not slave). #/* Program or connection */ #COMM_TIME_OUT -0x0C (-12) #PORT_SOCKET_FAILURE -0x0D (-13) #SELECT_FAILURE -0x0E (-14) #TOO_MANY_DATAS -0x0F (-15) #INVALID_CRC -0x10 (-16) #INVALID_EXCEPTION_CODE -0x11 (-17) [TRANSACTION_01] MB_TX_CODE=fnct_02_read_discrete_inputs FIRST_ELEMENT=1024 NELEMENTS=24 HAL_TX_NAME=remoteIOin MAX_UPDATE_RATE=0.0 DEBUG=1 [TRANSACTION_02] MB_TX_CODE=fnct_15_write_multiple_coils FIRST_ELEMENT=1280 NELEMENTS=8 HAL_TX_NAME=remoteIOout MAX_UPDATE_RATE=0.0 [TRANSACTION_03] LINK_TYPE=serial SERIAL_PORT=/dev/ttyS0 SERIAL_BAUD=115200 SERIAL_BITS=8 SERIAL_PARITY=none SERIAL_STOP=2 SERIAL_DELAY_MS=50 MB_SLAVE_ID=1 MB_TX_CODE=fnct_03_read_holding_registers FIRST_ELEMENT=1 NELEMENTS=2 HAL_TX_NAME=XDrive01 MAX_UPDATE_RATE=0.0 DEBUG=1 [TRANSACTION_04] MB_TX_CODE=fnct_03_read_holding_registers FIRST_ELEMENT=4 NELEMENTS=3 HAL_TX_NAME=XDrive02 MAX_UPDATE_RATE=0.0 DEBUG=1 [TRANSACTION_05] MB_TX_CODE=fnct_03_read_holding_registers FIRST_ELEMENT=9 NELEMENTS=1 HAL_TX_NAME=XDrive03 MAX_UPDATE_RATE=0.0 [TRANSACTION_06] MB_TX_CODE=fnct_03_read_holding_registers FIRST_ELEMENT=1024 NELEMENTS=1 HAL_TX_NAME=XDrive04 MAX_UPDATE_RATE=0.0 [TRANSACTION_07] MB_TX_CODE=fnct_03_read_holding_registers FIRST_ELEMENT=1030 NELEMENTS=2 HAL_TX_NAME=XDrive05 MAX_UPDATE_RATE=0.0 [TRANSACTION_08] MB_TX_CODE=fnct_03_read_holding_registers FIRST_ELEMENT=1033 NELEMENTS=1 HAL_TX_NAME=XDrive06 MAX_UPDATE_RATE=0.0

and then i need to put the following lines in my custom.hal file:

loadusr -W mb2hal config=mb2hal.ini
loadusr -Wn mymodule mb2hal config=config_file.ini <- i guess i should make a .ini file for my vfd like "enc_vfd.ini" ?

so the second line should perhaps be: loadusr -Wn enc_vfd mb2hal config=enc_vfd.ini ?

and in this "enc_vfd.ini" file i need to put the modbus translation code?

i looked for some examples and i found one on a X200 Hitachi inverter,

some of it makes sense to me but i'm uncertain what i need to change for my application?

below is the X200 .ini file
Code:
[MB2HAL_INIT] INIT_DEBUG=0 . HAL_MODULE_NAME=x200-vfd SLOWDOWN=0.0 TOTAL_TRANSACTIONS=10 # Set Run Status [TRANSACTION_00] LINK_TYPE=serial SERIAL_PORT=/dev/ttyS0 SERIAL_BAUD=9600 SERIAL_BITS=8 SERIAL_PARITY=none SERIAL_STOP=1 SERIAL_DELAY_MS=3 MB_SLAVE_ID=1 FIRST_ELEMENT=0 NELEMENTS=1 MB_TX_CODE=fnct_15_write_multiple_coils HAL_TX_NAME=run MAX_UPDATE_RATE=0.0 DEBUG=3 # Set Direction [TRANSACTION_01] MB_TX_CODE=fnct_15_write_multiple_coils FIRST_ELEMENT=1 NELEMENTS=1 HAL_TX_NAME=direction MAX_UPDATE_RATE=0.0 DEBUG=3 # Set Frequency [TRANSACTION_02] MB_TX_CODE=fnct_16_write_multiple_registers FIRST_ELEMENT=0 NELEMENTS=1 HAL_TX_NAME=set-frequency MAX_UPDATE_RATE=0.0 DEBUG=3 # Spindle Running? [TRANSACTION_03] MB_TX_CODE=fnct_15_write_multiple_coils FIRST_ELEMENT=13 NELEMENTS=1 HAL_TX_NAME=is-running MAX_UPDATE_RATE=0.0 DEBUG=3 # Running Clockwise? [TRANSACTION_04] MB_TX_CODE=fnct_15_write_multiple_coils FIRST_ELEMENT=14 NELEMENTS=1 HAL_TX_NAME=is-reverse MAX_UPDATE_RATE=0.0 DEBUG=3 # Is at Speed? [TRANSACTION_05] MB_TX_CODE=fnct_15_write_multiple_coils FIRST_ELEMENT=24 NELEMENTS=1 HAL_TX_NAME=is-at-speed MAX_UPDATE_RATE=0.0 DEBUG=3 # Is Alarm? [TRANSACTION_06] MB_TX_CODE=fnct_15_write_multiple_coils FIRST_ELEMENT=19 NELEMENTS=1 HAL_TX_NAME=is-alarm MAX_UPDATE_RATE=0.0 DEBUG=3 # Is Ready? [TRANSACTION_07] MB_TX_CODE=fnct_15_write_multiple_coils FIRST_ELEMENT=16 NELEMENTS=1 HAL_TX_NAME=is-ready MAX_UPDATE_RATE=0.0 DEBUG=3 # Is External Trip active? [TRANSACTION_08] MB_TX_CODE=fnct_15_write_multiple_coils FIRST_ELEMENT=5 NELEMENTS=1 HAL_TX_NAME=is-tripped MAX_UPDATE_RATE=0.0 DEBUG=3 # Reset VFD [TRANSACTION_09] MB_TX_CODE=fnct_15_write_multiple_coils FIRST_ELEMENT=6 NELEMENTS=1 HAL_TX_NAME=reset MAX_UPDATE_RATE=0.0 DEBUG=3 #REQUIRED: Modbus transaction function code (see www.modbus.org specifications). # fnct_02_read_discrete_inputs (02 = 0x02) # fnct_03_read_holding_registers (03 = 0x03) # fnct_04_read_input_registers (04 = 0x04) # fnct_15_write_multiple_coils (15 = 0x0F) # fnct_16_write_multiple_registers (16 = 0x10) #fnct_02_read_discrete_inputs: creates boolean output HAL pins. #fnct_03_read_holding_registers: creates a floating point output HAL pins. # also creates a u32 output HAL pins. #fnct_04_read_input_registers: creates a floating point output HAL pins. # also creates a u32 output HAL pins. #fnct_15_write_multiple_coils: creates boolean input HAL pins. #fnct_16_write_multiple_registers: creates a floating point input HAL pins. #The pins are named based on component name, transaction number and order number. #Example: mb2hal.00.01 (transaction=00, second register=01 (00 is the first one))

Thanks!

Victor

Please Log in to join the conversation.

More
9 years 8 months ago #88071 by Todd Zuercher

and then i need to put the following lines in my custom.hal file:

loadusr -W mb2hal config=mb2hal.ini
loadusr -Wn mymodule mb2hal config=config_file.ini <- i guess i should make a .ini file for my vfd like "enc_vfd.ini" ?


No, those are 2 possible options for the line of code you need in your hal file.
Keep it simple and only use the top line.

You only need one modbus ini file, so you only need to keep your mb2hal.ini or your enc_vfd.ini (not both).
If you use enc_vfd.ini for the config file name you will need to change the line in your hal file to" loadusr -W mb2hal config=enc_vfd.ini"

Just remember the mb2hal.ini file has a lot of unnecessary info, lots of comments, optional settings, and commented out examples included. It can be difficult to sort through it all to see just what you need and don't need. That is where other examples like the X200 one you posted come in handy. You are going to have to carefully read through the manuals for your drive to determine what all the settings are going to be both in mb2hal and in the drive its self. Every drive manufacturer uses different protocols so you can't just copy what works for a different drive.

It took me a couple of weeks to sort it all out for the drives I was using, even with decent manuals. If you can't get the modbus manuals for your drives you might be out of luck.

Please Log in to join the conversation.

More
9 years 8 months ago #88073 by Victor
Ok,

So i should go

loadusr -W mb2hal config=enc_vfd.ini

do i need antything else in the .hal file?

this was a chapter in the X200 thread (code from the .hal file) that catched my eye:

net x200-run x200.run.00 <= motion.spindle-on
net x200-dir x200.direction.00 <= motion.spindle-forward
net x200-RPM x200.frequency.00 <= motion.spindle-speed-out
net x200-at-speed x200.at-speed.00 <= motion.spindle-at-speed

setp x200.direction.00 0


Well the manual is really good for my vfd, i separated the modbus part that can be located here: 1drv.ms/b/s!AnY9CcWCLBtalGev69rQ1UOUzZXn

i just don't understand how i should apply the information from the manual, if we look at this chapter from the X200 code for example:
Code:
# Running Clockwise? [TRANSACTION_04] MB_TX_CODE=fnct_15_write_multiple_coils FIRST_ELEMENT=14 NELEMENTS=1 HAL_TX_NAME=is-reverse MAX_UPDATE_RATE=0.0 DEBUG=3

i have this table in the manual:

Attachment not found




Victor

Please Log in to join the conversation.

More
9 years 8 months ago #88077 by Todd Zuercher
Looks enough simpler than the ones I had to use, to wonder if your are missing something.

Such as my drives need to have a certain register written to to unlock the drive. Then another had to be read periodically to prevent a communications shut down... I'm a little jealous if you only need to write to one register and read 2 contiguous ones. (Did i mention the drives I had to work with were a complicated mess.)

Please Log in to join the conversation.

More
9 years 8 months ago #88078 by Victor
Well simple for you perhaps for me it's a diffrent story ;p

Would be super if you could explain how i would need to code for one function like running clockwise

Victor

Please Log in to join the conversation.

More
9 years 8 months ago #88084 by Todd Zuercher
You'll have to bear with me a bit, as it was more than 3 years ago since I have last looked at this stuff. (and it wasn't all fond memories, so I have not dwelt on it.)

The first thing you need to do is figure out what the drives current modbus parameter settings are, and what you need to set them to.

You need to figure out what the address of your little USB dongle is. (It should be something like SERIAL_PORT=/dev/ttyUSB0 (or 1,2 3...) Mine was 0 as it it the only USB device on that computer.

Please Log in to join the conversation.

More
9 years 8 months ago #88085 by Victor
Ok. The usb address is ttyUSB0

I have the following pages with diffrent protocols if that is what you mean?

Attachment not found

Attachment not found

Attachment not found

Please Log in to join the conversation.

Time to create page: 0.074 seconds