7i76 limits question..

More
7 years 7 months ago #129926 by B_Casey
when the signal is not inverted the switches show joint 0 and joint one on limit switch error.
so i inverted the signals.. now the switches to not register at all.
have tested the switches with a meter, the switches are working
the e-stop is doing the same thing...

not sure what could be causing this issue, (the same switches and e-stops where functioning fine on the 5i25-g540 before i put the 7i76

12v field power
5v other power
both leds are on
field pwr ->switch -> input on 7i76

Brian

Please Log in to join the conversation.

More
7 years 7 months ago #129971 by B_Casey
Replied by B_Casey on topic 7i76 limits question..
figured this out, it was a typo in the server period thing, was causing the sserial to shut down due to errors, (left off one of the zeros)

Please Log in to join the conversation.

More
7 years 7 months ago #130000 by tommylight
Replied by tommylight on topic 7i76 limits question..
Thank you for reporting back.
Glad you got it working.

Please Log in to join the conversation.

More
7 years 7 months ago #130010 by PCW
Replied by PCW on topic 7i76 limits question..
You should have gotten a cascade of error messages if you lost contact with the 7I76

If you want to generate a fault if you lose contact with a sserial remote, you can use the

hm2_(card).0.sserial.port-0.run

pin to monitor the health of sserial connections

Please Log in to join the conversation.

More
7 years 7 months ago #130011 by B_Casey
Replied by B_Casey on topic 7i76 limits question..
there was and your response to someone else some other when clued me into what the problem was !