- Posts: 17524
- Thank you received: 0
Servo Oscillation Issue at ±6.6V 5i25 + 7i77, Analog Control
1 year 8 months ago #321656
by PCW
Replied by PCW on topic Servo Oscillation Issue at ±6.6V 5i25 + 7i77, Analog Control
That looks like maybe an electrical/wiring issue with the encoder.
Is differential signaling used?
Is differential signaling used?
Please Log in to join the conversation.
1 year 8 months ago #321846
by Traken
Replied by Traken on topic Servo Oscillation Issue at ±6.6V 5i25 + 7i77, Analog Control
Yes, it is a differential signal.
I am attaching a screen manual from the servopack.
Two servos are Delta asda-b2 750w and one on the z axis is the Chinese a1-svd 750w and in total there are such symptoms on each axis.
The encoder cable is shielded and a separate analog cable is also shielded, the shield is only connected to the servopack.
Maybe I need to use resistors?
I am attaching a screen manual from the servopack.
Attachment not found
Two servos are Delta asda-b2 750w and one on the z axis is the Chinese a1-svd 750w and in total there are such symptoms on each axis.
The encoder cable is shielded and a separate analog cable is also shielded, the shield is only connected to the servopack.
Maybe I need to use resistors?
Please Log in to join the conversation.
1 year 8 months ago #321856
by PCW
Replied by PCW on topic Servo Oscillation Issue at ±6.6V 5i25 + 7i77, Analog Control
Is the 7I77 jumpered for differential inputs?
It may be a noise issue. One way to check if it's a common mode noise issue
(noise that exceeds the common mode range of the RS-422 receivers)
is to enable encoder error reporting:
setp hm2_5i25.0.encoder.00.quad-error-enable true
Once this has been done, inputs that violate the quadrature sequence
(often noise will do this) will set the quadrature error flag:
hm2_5i25.0.encoder.00.quad-error
It may be a noise issue. One way to check if it's a common mode noise issue
(noise that exceeds the common mode range of the RS-422 receivers)
is to enable encoder error reporting:
setp hm2_5i25.0.encoder.00.quad-error-enable true
Once this has been done, inputs that violate the quadrature sequence
(often noise will do this) will set the quadrature error flag:
hm2_5i25.0.encoder.00.quad-error
Please Log in to join the conversation.
1 year 8 months ago #322049
by Traken
Replied by Traken on topic Servo Oscillation Issue at ±6.6V 5i25 + 7i77, Analog Control
It checks your method and shows no error. I will try to turn on linuxcnc and control from the servopack to read a higher speed and exclude the encoder reading.
Because it still seems to me that it is not related to the encoder reading but to the analog power supply.
What still surprises me is that if I drive the axle in the positive direction, I can achieve 10 m/min, and if I drive the axle in the negative direction, 8.3 m/min.
Because it still seems to me that it is not related to the encoder reading but to the analog power supply.
What still surprises me is that if I drive the axle in the positive direction, I can achieve 10 m/min, and if I drive the axle in the negative direction, 8.3 m/min.
Please Log in to join the conversation.
1 year 8 months ago #322074
by PCW
Replied by PCW on topic Servo Oscillation Issue at ±6.6V 5i25 + 7i77, Analog Control
It sure looks like an encoder issue, especially the speed limit
(in one plot the encoder velocity dropped to 0 in basically an instant)
Did you set the encoder filter to 0 on all encoder channels?
(in one plot the encoder velocity dropped to 0 in basically an instant)
Did you set the encoder filter to 0 on all encoder channels?
Please Log in to join the conversation.
1 year 8 months ago #322169
by Traken
Replied by Traken on topic Servo Oscillation Issue at ±6.6V 5i25 + 7i77, Analog Control
No, I set it on one axis I was testing. Should I set it on all axes?
Please Log in to join the conversation.
1 year 8 months ago #322517
by Traken
Replied by Traken on topic Servo Oscillation Issue at ±6.6V 5i25 + 7i77, Analog Control
I changed the encoder filter to 0 on each axis, it had no effect. I wonder if I can somehow drive the servo without a closed loop and see if it works.
Please Log in to join the conversation.
1 year 8 months ago #322523
by PCW
Replied by PCW on topic Servo Oscillation Issue at ±6.6V 5i25 + 7i77, Analog Control
Yes, if you decouple the linear axis (and comment out the net statement that connects
the PID output to the 7I77 analog output pin, you can simply setp the output voltage
with halcmd.
the PID output to the 7I77 analog output pin, you can simply setp the output voltage
with halcmd.
Please Log in to join the conversation.
1 year 4 months ago #329586
by Traken
Replied by Traken on topic Servo Oscillation Issue at ±6.6V 5i25 + 7i77, Analog Control
After a long break I'm back to the topic. I did some research, tried to swap the wires between the mesa and the servopack, but no changes. It's not a problem with the analog voltage as in the topic because if I set P=0 I can normally drive at high speed without a closed loop.
What should the encoder accuracy be set to?
Maybe I have set the scale too large or too small?
But I tried changing it to less and it didn't have any effect.
I'm still wondering if the analog wire can go parallel to the encoder wire, maybe it creates some interference.
What should the encoder accuracy be set to?
Maybe I have set the scale too large or too small?
But I tried changing it to less and it didn't have any effect.
I'm still wondering if the analog wire can go parallel to the encoder wire, maybe it creates some interference.
Please Log in to join the conversation.
1 year 4 months ago #329607
by PCW
Replied by PCW on topic Servo Oscillation Issue at ±6.6V 5i25 + 7i77, Analog Control
Yes, looks like an encoder issue of some kind (especially the sudden drop to 0 velocity)
I would try lowering the emulated encoder output scale, as
maybe the drive has an issue with quadrature generation at high
speeds and high resolutions.
I would try lowering the emulated encoder output scale, as
maybe the drive has an issue with quadrature generation at high
speeds and high resolutions.
Please Log in to join the conversation.
Time to create page: 0.125 seconds