Indraworks and Twincat is running on the same PC? The ethercat par file has been created after you connected twincat to the drive?
your steps at the moment are:
-power up the drive
-connect to twincat, start twincat
-conncet to the linux PC
-start linuxcnc , drives goes op?
-without the twincat step, the drive stays safeop or preop ?
please post your (linuxcnc) ethercat_conf.xml
Please Log in to join the conversation.
db1981 wrote: ok, i understand.
Indraworks and Twincat is running on the same PC? The ethercat par file has been created after you connected twincat to the drive?
your steps at the moment are:
-power up the drive
-connect to twincat, start twincat
-conncet to the linux PC
-start linuxcnc , drives goes op?
-without the twincat step, the drive stays safeop or preop ?
please post your (linuxcnc) ethercat_conf.xml
Indraworks and Twincat is running on the same PC?
Yes Indraworks and TwinCAT are running on the same PC/Windows installation LinuxCNC on the same Machine on a Stand alone installation.
The ethercat par file has been created after you connected twincat to the drive?
The HCS01.1E_W0009_mpb20v26_ethercat.par was created after the TwinCAT connection to the drive.
The HCS01.1E_W0009_mpb20v26_eth.par was created after the the initial Setup to the drive, but before TwinCAT interference.
My steps at the moment are:
-Setup the drive, do the Scaling and Initial Setup in Indraworks over Ethernet. (only once)
-Change the MasterCommunication to EtherCAT COE (only once)
-Restart the Drive start TwinCAT --> Scan for boxes --> Configure PDO´s --> activate Configuration (only once)
-Restart PC load LinuxCNC --> Start LinuxCNC Clear E-Stop & Enable the Machine --> Drive goes from INIT-->SafeOP-->PO-->OP
-Jog the Drive with false Scaling (Changing the Scaling in HAL file leads to F2037 Excessive position command difference
Without TwinCAT step the Drive stays in INIT-State
Attachment not found
Please Log in to join the conversation.
-Change the MasterCommunication to EtherCAT COE ,-Drive restart ?
If yes, please post an parameter file after this, before the use of twincat.
at the moment its not 100% clear for me, why twincat is necessary for PDO config.
Please Log in to join the conversation.
db1981 wrote: are you able to use indraworks after the step
-Change the MasterCommunication to EtherCAT COE ,-Drive restart ?
If yes, please post an parameter file after this, before the use of twincat.
at the moment its not 100% clear for me, why twincat is necessary for PDO config.
Yes i can use IndraworksDS after Change but i only if TwinCAT is in run state, only then i can Connect to the drive.
I will try tomorrow if i get somehow the connection to the drive without TwinCAT running, maybe it is somehow possible.
Please Log in to join the conversation.
Please explain your step -Configure PDOs , are there no pdo's listet after the box scan?
Please Log in to join the conversation.
db1981 wrote: ok, don't try this will not work. Twincat sets an EoE Gateway for the ethernet communication through ethercat.
Please explain your step -Configure PDOs , are there no pdo's listet after the box scan?
After Changing the MasterCommunication to Ethercat there are 2 pairs of PDO´s preconfigured, this is preconfigured from IndraworksDS.
see Attachments
Attachment not found
Attachment not found
I reconfigured the PDO´s to get more options like this:
Attachment not found
Attachment not found
Please Log in to join the conversation.
try to start your config without the twincat workaround.
this are the init cmds for your drive, for your desired PDO configuration. You can put them manually in your ethercat config with
an "sdo_config" line or as an external .xml file.
These commands are sent in the transition between preop and safeop state, before the master configs the pdos, goes to realtime and in op mode.
with beckhoff or sercos drives this list is very long, because it contains the whole drive configuration. These drives configurations are empty after power loose. I hope this is not so with the indradrives.
At CIA Can Profile the scaling and weigthing is handled with other units, as descriped in the indradrive manual for this firmware. but first get the drive to op without twincat, then we can get an aim at the scaling.
Attachment not found
Attachment not found
Please Log in to join the conversation.
db1981 wrote: i have added an line to your ethercat_conf.xml, please put the additional file in your machine config folder.
try to start your config without the twincat workaround.
this are the init cmds for your drive, for your desired PDO configuration. You can put them manually in your ethercat config with
an "sdo_config" line or as an external .xml file.
These commands are sent in the transition between preop and safeop state, before the master configs the pdos, goes to realtime and in op mode.
with beckhoff or sercos drives this list is very long, because it contains the whole drive configuration. These drives configurations are empty after power loose. I hope this is not so with the indradrives.
At CIA Can Profile the scaling and weigthing is handled with other units, as descriped in the indradrive manual for this firmware. but first get the drive to op without twincat, then we can get an aim at the scaling.
Attachment not found
Attachment not found
I know these Commands, they are listed in the startup tab from TwinCAT, i think they are stored in the drive, because i only had to use TwinCAT once to configure them.
But i did not know how to use them without TwinCAT.
Thanks i do a reset of the drive tomorrow and set it up with your additional XML and then get it hopefully to work.
Greets Sven
Please Log in to join the conversation.
if you once did start the drive with Twincat, you can start it again direct with linuxcnc after an power cycle?
Please Log in to join the conversation.
regards
bkt