- Posts: 12160
- Thank you received: 0
Beckhoff ethercat 64 with bit linuxcnc, How to install.
3 years 10 months ago #259143
by rodw
Replied by rodw on topic Beckhoff ethercat 64 with bit linuxcnc, How to install.
What IO module?
If its not beckhof, you need to make a custom xml file.
With just the io module connected type
ethercat slaves -v
ethercat pdos
You will have all the info to build a xml file similar to slave1 here
github.com/rodw-au/linuxcnc-cia402/blob/...ercat-conf-diewu.xml
If its not beckhof, you need to make a custom xml file.
With just the io module connected type
ethercat slaves -v
ethercat pdos
You will have all the info to build a xml file similar to slave1 here
github.com/rodw-au/linuxcnc-cia402/blob/...ercat-conf-diewu.xml
Please Log in to join the conversation.
3 years 10 months ago #259249
by akg1904
Replied by akg1904 on topic Beckhoff ethercat 64 with bit linuxcnc, How to install.
So I am trying to get a Weidmuller UR20-FBC-EC IO module integrated.
I tried my best to make the xml file.
I had a few doubts though...
On line 6 what are these responsible for:
appTimePeriod="1000000"
refClockSyncCycles="1"
On line 7 what are these responsible for:
type="generic"
configPdos="false"
On line 8 what are these responsible for:
assignActivate="300"
sync0Cycle="*1"
sync0Shift="0"
I have also attached the xml file with this post.
At the end of the file there are 3 commented out sections that have the response to:
ethercat slaves -v
ethercat pdos
ethercat sdos
Not sure if that is any help or not but just thought maybe the extra information may be useful. Please ignore it if it's useless.
Now I do have another question. After this custom xml file is generated, how do I go about integrating it with linuxcnc?
Thanks again for you help
I tried my best to make the xml file.
I had a few doubts though...
On line 6 what are these responsible for:
appTimePeriod="1000000"
refClockSyncCycles="1"
On line 7 what are these responsible for:
type="generic"
configPdos="false"
On line 8 what are these responsible for:
assignActivate="300"
sync0Cycle="*1"
sync0Shift="0"
I have also attached the xml file with this post.
At the end of the file there are 3 commented out sections that have the response to:
ethercat slaves -v
ethercat pdos
ethercat sdos
Not sure if that is any help or not but just thought maybe the extra information may be useful. Please ignore it if it's useless.
Attachment not found
Now I do have another question. After this custom xml file is generated, how do I go about integrating it with linuxcnc?
Thanks again for you help
Please Log in to join the conversation.
3 years 10 months ago #259250
by rodw
Replied by rodw on topic Beckhoff ethercat 64 with bit linuxcnc, How to install.
LINE 6 = servo thread length. must agree
LINE 7 generic. because it does not have built in support so you are creating a generic slave
LINE 8 I just accepted.
halpin = the name you wil call this as a pin in linuxcnc so it cannot have spaces
vid and pid are as in your slaves -v
vid = Vendor Id: 0x00000230
pid = Product code: 0x4f911c30
Probably other errors that i am not familiar with but a good start.
LINE 7 generic. because it does not have built in support so you are creating a generic slave
LINE 8 I just accepted.
halpin = the name you wil call this as a pin in linuxcnc so it cannot have spaces
vid and pid are as in your slaves -v
vid = Vendor Id: 0x00000230
pid = Product code: 0x4f911c30
Probably other errors that i am not familiar with but a good start.
Please Log in to join the conversation.
3 years 10 months ago #259255
by akg1904
Replied by akg1904 on topic Beckhoff ethercat 64 with bit linuxcnc, How to install.
Thanks you for that prompt response, I appreciate your effort.
I've attached the xml rectifying the hal pin spaces and updated the PID and VID.
Can you point me to any resource on how to integrate this xml file into Linuxcnc so that it reflects in the HAL configuration window?
Right now its just kinda sitting in my config folder...
I've attached the xml rectifying the hal pin spaces and updated the PID and VID.
Attachment not found
Can you point me to any resource on how to integrate this xml file into Linuxcnc so that it reflects in the HAL configuration window?
Right now its just kinda sitting in my config folder...
Please Log in to join the conversation.
3 years 10 months ago #259260
by rodw
Replied by rodw on topic Beckhoff ethercat 64 with bit linuxcnc, How to install.
I can't help any further except to say configpdos should be true (I think)
If you ignore the cia402 stuff, this example shows how to load from your halfile
github.com/rodw-au/linuxcnc-cia402/blob/main/cia402.hal
The sticky at the end shows how to use halcmd to do basic testing.
Expect errors so do at the command line so yo see them..
If you ignore the cia402 stuff, this example shows how to load from your halfile
github.com/rodw-au/linuxcnc-cia402/blob/main/cia402.hal
The sticky at the end shows how to use halcmd to do basic testing.
Expect errors so do at the command line so yo see them..
Please Log in to join the conversation.
3 years 10 months ago #259432
by akg1904
Replied by akg1904 on topic Beckhoff ethercat 64 with bit linuxcnc, How to install.
Hi Rodw,
Thank you for your input, it helped me a lot in figuring out the problems, I followed the link you shared and then circled back to an old post of yours and realised linuxcnc-uspace-dev hadn't been installed as well. Super embarassing but I finally managed to get lcec to show in the hal configuration.
So, once again thanks for the help.
Thank you for your input, it helped me a lot in figuring out the problems, I followed the link you shared and then circled back to an old post of yours and realised linuxcnc-uspace-dev hadn't been installed as well. Super embarassing but I finally managed to get lcec to show in the hal configuration.
So, once again thanks for the help.
Please Log in to join the conversation.
- johntrevick
- Offline
- New Member
-
Less
More
- Posts: 15
- Thank you received: 0
2 years 8 months ago #294011
by johntrevick
Replied by johntrevick on topic Beckhoff ethercat 64 with bit linuxcnc, How to install.
Hi,
I'm trying to get a module working that is not already supported and I hope someone can help me. I followed the instructions on the first page of this thread as best I could.
First I was trying to get an EL3068 8 port analog card working and it was successful. I'm using it to read some potentiometers.
Now I'm trying to get an EL5102 module working and I thought this would be the easier one since the EL5101 is already supported. After following the process linuxcnc doesn't complain about it being in my hal file but the module doesn't leave preop stage.
I copied the EL5101.h and EL5101.c files to lcec_El5102.h and .c
modified them to substitute 5101 to 5102 and changed the ProductCode field (from ethercat xml -p7)
I didn't try adding the second channel in the .c file. I looked but how to do it wasn't obvious.
did make clean and then make
cp lcec.so ../../linuxcnc-dev/rtlib/
sudo cp lcec_conf /usr/bin/
cp lcec_conf ../../linuxcnc/configs/wedm/
ethercat slaves gives: (with linuxcnc started)
0 0:0 OP + EK1100 EtherCAT-Koppler (2A E-Bus)
1 0:1 OP + EL1809 16K. Dig. Eingang 24V, 3ms
2 0:2 OP + EL2008 8K. Dig. Ausgang 24V, 0.5A
3 0:3 OP + EL3068 8K. Ana. Eingang 0-10V
4 0:4 OP + EK1100 EtherCAT-Koppler (2A E-Bus)
5 0:5 OP + EL1008 8K. Dig. Eingang 24V, 3ms
6 0:6 OP + EL2008 8K. Dig. Ausgang 24V, 0.5A
7 0:7 PREOP + EL5102 2Ch. Inc. Encoder 5V (RS422,TTL)
8 0:8 OP + EL7342 2K. DC-Motor-Endstufe (50V, 3.5A)
9 0:9 OP + DVS_ETHCAT_v1.004
10 0:10 OP + DVS_ETHCAT_v1.004
if I set ethercat debug 1 and look at dmesg I see it checking the time offset when starting up but later it just skips over it when going through each device.
[...]
[186186.355310] EtherCAT DEBUG 0-4: Checking system time offset.
[186186.375331] EtherCAT DEBUG 0-4: DC 64 bit system time offset calculation: system_time=761845177497583898 (corrected with 20000000), app_time=761845177496618367, diff=-965531
[186186.375339] EtherCAT DEBUG 0-4: Not touching time offset.
[186186.395306] EtherCAT DEBUG 0-7: Checking system time offset.
[186186.415328] EtherCAT DEBUG 0-7: DC 64 bit system time offset calculation: system_time=761845177537569111 (corrected with 20000000), app_time=761845177536577318, diff=-991793
[186186.415336] EtherCAT DEBUG 0-7: Not touching time offset.
[186186.435301] EtherCAT DEBUG 0-8: Checking system time offset.
[186186.455318] EtherCAT DEBUG 0-8: DC 64 bit system time offset calculation: system_time=761845177577586331 (corrected with 20000000), app_time=761845177576580029, diff=-1006302
[186186.455327] EtherCAT DEBUG 0-8: Setting time offset to 761658983053803698 (was 761658983054810000)
[...]
[186186.860091] EtherCAT DEBUG 0-6: Now in SAFEOP.
[186186.862084] EtherCAT DEBUG 0-6: Now in OP. Finished configuration.
[186186.895348] EtherCAT DEBUG 0-8: Changing state from PREOP to OP.
[186186.895356] EtherCAT DEBUG 0-8: Configuring...
[186186.898094] EtherCAT DEBUG 0-8: Now in INIT.
ethercat slaves -v gives:
=== Master 0, Slave 7 ===
Device: Main
State: PREOP
Flag: +
Identity:
Vendor Id: 0x00000002
Product code: 0x13ee3052
Revision number: 0x00100000
Serial number: 0x00000000
DL information:
FMMU bit operation: no
Distributed clocks: yes, 64 bit
DC system time transmission delay: 1880 ns
Port Type Link Loop Signal NextSlave RxTime [ns] Diff [ns] NextDc [ns]
0 EBUS up open yes 6 3045771182 0 145
1 EBUS up open yes 8 3045771492 310 155
2 N/A down closed no - - - -
3 N/A down closed no - - - -
Mailboxes:
Bootstrap RX: 0x1000/244, TX: 0x10f4/244
Standard RX: 0x1000/128, TX: 0x1100/128
Supported protocols: CoE, FoE
General:
Group: Measuring
Image name:
Order number: EL5102
Device name: EL5102 2Ch. Inc. Encoder 5V (RS422,TTL)
CoE details:
Enable SDO: yes
Enable SDO Info: yes
Enable PDO Assign: yes
Enable PDO Configuration: no
Enable Upload at startup: no
Enable SDO complete access: yes
Flags:
Enable SafeOp: no
Enable notLRW: no
Current consumption: 210 mA
uname -a
Linux Charmilles 4.19.71-rt24-v7l+ #1 SMP PREEMPT RT Fri Jan 1 21:15:16 GMT 2021 armv7l GNU/Linux
LINUXCNC - 2.8.4
This is a raspberry PI and built following instructions from MetalMusings
forum.linuxcnc.org/ethercat/42048-notes-...at-on-raspberry-pi-4
I'm sure I did a bunch of other stuff after following his instructions but I didn't document exactly what I was doing and don't quite remember. However, apart from this card it is mostly working. I/O is working and my ethercat drives are moving are moving the servo motors. I have a separate issue related to a belt reduction but that should probably be in another thread.
I'm trying to get a module working that is not already supported and I hope someone can help me. I followed the instructions on the first page of this thread as best I could.
First I was trying to get an EL3068 8 port analog card working and it was successful. I'm using it to read some potentiometers.
Now I'm trying to get an EL5102 module working and I thought this would be the easier one since the EL5101 is already supported. After following the process linuxcnc doesn't complain about it being in my hal file but the module doesn't leave preop stage.
I copied the EL5101.h and EL5101.c files to lcec_El5102.h and .c
modified them to substitute 5101 to 5102 and changed the ProductCode field (from ethercat xml -p7)
I didn't try adding the second channel in the .c file. I looked but how to do it wasn't obvious.
did make clean and then make
cp lcec.so ../../linuxcnc-dev/rtlib/
sudo cp lcec_conf /usr/bin/
cp lcec_conf ../../linuxcnc/configs/wedm/
ethercat slaves gives: (with linuxcnc started)
0 0:0 OP + EK1100 EtherCAT-Koppler (2A E-Bus)
1 0:1 OP + EL1809 16K. Dig. Eingang 24V, 3ms
2 0:2 OP + EL2008 8K. Dig. Ausgang 24V, 0.5A
3 0:3 OP + EL3068 8K. Ana. Eingang 0-10V
4 0:4 OP + EK1100 EtherCAT-Koppler (2A E-Bus)
5 0:5 OP + EL1008 8K. Dig. Eingang 24V, 3ms
6 0:6 OP + EL2008 8K. Dig. Ausgang 24V, 0.5A
7 0:7 PREOP + EL5102 2Ch. Inc. Encoder 5V (RS422,TTL)
8 0:8 OP + EL7342 2K. DC-Motor-Endstufe (50V, 3.5A)
9 0:9 OP + DVS_ETHCAT_v1.004
10 0:10 OP + DVS_ETHCAT_v1.004
if I set ethercat debug 1 and look at dmesg I see it checking the time offset when starting up but later it just skips over it when going through each device.
[...]
[186186.355310] EtherCAT DEBUG 0-4: Checking system time offset.
[186186.375331] EtherCAT DEBUG 0-4: DC 64 bit system time offset calculation: system_time=761845177497583898 (corrected with 20000000), app_time=761845177496618367, diff=-965531
[186186.375339] EtherCAT DEBUG 0-4: Not touching time offset.
[186186.395306] EtherCAT DEBUG 0-7: Checking system time offset.
[186186.415328] EtherCAT DEBUG 0-7: DC 64 bit system time offset calculation: system_time=761845177537569111 (corrected with 20000000), app_time=761845177536577318, diff=-991793
[186186.415336] EtherCAT DEBUG 0-7: Not touching time offset.
[186186.435301] EtherCAT DEBUG 0-8: Checking system time offset.
[186186.455318] EtherCAT DEBUG 0-8: DC 64 bit system time offset calculation: system_time=761845177577586331 (corrected with 20000000), app_time=761845177576580029, diff=-1006302
[186186.455327] EtherCAT DEBUG 0-8: Setting time offset to 761658983053803698 (was 761658983054810000)
[...]
[186186.860091] EtherCAT DEBUG 0-6: Now in SAFEOP.
[186186.862084] EtherCAT DEBUG 0-6: Now in OP. Finished configuration.
[186186.895348] EtherCAT DEBUG 0-8: Changing state from PREOP to OP.
[186186.895356] EtherCAT DEBUG 0-8: Configuring...
[186186.898094] EtherCAT DEBUG 0-8: Now in INIT.
ethercat slaves -v gives:
=== Master 0, Slave 7 ===
Device: Main
State: PREOP
Flag: +
Identity:
Vendor Id: 0x00000002
Product code: 0x13ee3052
Revision number: 0x00100000
Serial number: 0x00000000
DL information:
FMMU bit operation: no
Distributed clocks: yes, 64 bit
DC system time transmission delay: 1880 ns
Port Type Link Loop Signal NextSlave RxTime [ns] Diff [ns] NextDc [ns]
0 EBUS up open yes 6 3045771182 0 145
1 EBUS up open yes 8 3045771492 310 155
2 N/A down closed no - - - -
3 N/A down closed no - - - -
Mailboxes:
Bootstrap RX: 0x1000/244, TX: 0x10f4/244
Standard RX: 0x1000/128, TX: 0x1100/128
Supported protocols: CoE, FoE
General:
Group: Measuring
Image name:
Order number: EL5102
Device name: EL5102 2Ch. Inc. Encoder 5V (RS422,TTL)
CoE details:
Enable SDO: yes
Enable SDO Info: yes
Enable PDO Assign: yes
Enable PDO Configuration: no
Enable Upload at startup: no
Enable SDO complete access: yes
Flags:
Enable SafeOp: no
Enable notLRW: no
Current consumption: 210 mA
uname -a
Linux Charmilles 4.19.71-rt24-v7l+ #1 SMP PREEMPT RT Fri Jan 1 21:15:16 GMT 2021 armv7l GNU/Linux
LINUXCNC - 2.8.4
This is a raspberry PI and built following instructions from MetalMusings
forum.linuxcnc.org/ethercat/42048-notes-...at-on-raspberry-pi-4
I'm sure I did a bunch of other stuff after following his instructions but I didn't document exactly what I was doing and don't quite remember. However, apart from this card it is mostly working. I/O is working and my ethercat drives are moving are moving the servo motors. I have a separate issue related to a belt reduction but that should probably be in another thread.
Please Log in to join the conversation.
2 years 8 months ago #294026
by rodw
Replied by rodw on topic Beckhoff ethercat 64 with bit linuxcnc, How to install.
I think you are out of date here
The Pi4 is supported on the LInuxcnc Downloads page.
The image includes the current repository for ethercat
Follow these steps forum.linuxcnc.org/ethercat/45336-etherc...-how-to-step-by-step
There has been a lot of work in recent months. You hardware could be supported now. If not ask, it might get supported.
forum.linuxcnc.org/ethercat/51187-new-li...cat-git-tree?start=0
The Pi4 is supported on the LInuxcnc Downloads page.
The image includes the current repository for ethercat
Follow these steps forum.linuxcnc.org/ethercat/45336-etherc...-how-to-step-by-step
There has been a lot of work in recent months. You hardware could be supported now. If not ask, it might get supported.
forum.linuxcnc.org/ethercat/51187-new-li...cat-git-tree?start=0
Please Log in to join the conversation.
- johntrevick
- Offline
- New Member
-
Less
More
- Posts: 15
- Thank you received: 0
2 years 8 months ago #294042
by johntrevick
Replied by johntrevick on topic Beckhoff ethercat 64 with bit linuxcnc, How to install.
yes I'm not at the most recent version, thank you for your quick reply.
I have upgraded to the more recent ethercat library as mentioned in New LinuxCNC-Ethercat git tree .
My devices folder is under linuxcnc-ethercat/src/devices and I didn't have to do the part where I added the device to lcec.config.c & lcec.config.h files
I guess I will try rebuilding from scratch but overall it is working with just this one module EL5102 not supported. The other unsupported module EL3068 I was able to get working and my other common i/o modules work so the ethercat part is working.
I have upgraded to the more recent ethercat library as mentioned in New LinuxCNC-Ethercat git tree .
My devices folder is under linuxcnc-ethercat/src/devices and I didn't have to do the part where I added the device to lcec.config.c & lcec.config.h files
I guess I will try rebuilding from scratch but overall it is working with just this one module EL5102 not supported. The other unsupported module EL3068 I was able to get working and my other common i/o modules work so the ethercat part is working.
Please Log in to join the conversation.
2 years 8 months ago #294043
by rodw
Replied by rodw on topic Beckhoff ethercat 64 with bit linuxcnc, How to install.
If possible, it would be good if you could do a pull request to Scotts repo to add your drivers. MAybe ask on the other thread
Please Log in to join the conversation.
Time to create page: 0.201 seconds